Wiring a 100amp outlet/connection- typical practice?
tarbellb
Oregon
Im in the middle of a service line upgrade for my property and shop.
I will need a few high amp connections in the shop for certain tools (large 20hp VFD screw compressor, laser machine, welders, etc..)
What is considered best practice or typical for a 100amp and 60amp 1ph 240v connection
_ hardwired?
_ do i need or want a shutoff
_ anything else to consider
My setup will be using surface mount conduit, the run from box to panel is under 10ft
u2slow
BC
Pin/sleeve is often used for these higher amp connections. I would hardwire though, as those get really pricey.
At 10' I'm content to use the breaker as the disconnect.
compressor and I assume laser, are not portable, so i would hardwire those to a disco.
the welders, I assume, are portable and thus a plug and receptacle would be best
what is the make and model on the welder?
matt_i
Hardwired is cheapest but gives minimum flexibility in the layout as times change. 3 pole non-fused disconnects are still pretty cheap, in good-used condition, if you want to go that route.
A screw compressor or machine tool (etc) may have its own 3 pole disconnect native to the machine...
mike93lx
Richmond, VA
If all the equipment will be line of sight to a spot in the shop, a sub panel would likely be easiest.
How are you hooking up the 20hp vfd? That's not single phase, right?