To avoid these ads, REGISTER NOW!

Wiring a 100amp outlet/connection- typical practice?

tarbellb

Well-known member
Joined
Apr 17, 2011
Messages
5,766
Location
Oregon
Im in the middle of a service line upgrade for my property and shop.

I will need a few high amp connections in the shop for certain tools (large 20hp VFD screw compressor, laser machine, welders, etc..)

What is considered best practice or typical for a 100amp and 60amp 1ph 240v connection
_ hardwired?
_ do i need or want a shutoff
_ anything else to consider


My setup will be using surface mount conduit, the run from box to panel is under 10ft
 
To avoid these ads, REGISTER NOW!

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,609
Location
BC
Pin/sleeve is often used for these higher amp connections. I would hardwire though, as those get really pricey.

At 10' I'm content to use the breaker as the disconnect.
 

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,737
Location
SE Michigan
Hardwired is cheapest but gives minimum flexibility in the layout as times change. 3 pole non-fused disconnects are still pretty cheap, in good-used condition, if you want to go that route.

A screw compressor or machine tool (etc) may have its own 3 pole disconnect native to the machine...
 
OP
T

tarbellb

Well-known member
Joined
Apr 17, 2011
Messages
5,766
Location
Oregon
If all the equipment will be line of sight to a spot in the shop, a sub panel would likely be easiest.

How are you hooking up the 20hp vfd? That's not single phase, right?

Yes it's a single phase compressor

Sub panel could be the move. I'm pulling 100amp feeder to the original sub panel. My thought was running a couple surface mount boxes would be easier but now a the shut offs requires it could be cheaper.
 
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,587
Location
Fullerton, CA
Any switching device between the VFD and the motor will, when under load, will do damage to the VFD's output transistors. This will greatly decrease the life of the VFD.
Make sure the equipment isn't running when you throw the switch (except in an emergency)
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,776
Location
Richmond, VA
Had to look it up - 1ø 230 V, a 20 HP motor pulls 88 amps. If you got the service and the $$ for electricity, why not? Cheaper in the long run to go 3ø...
Because power companies will have limits as motors draw far more current at startup than running.

A normal residential transformer will not support a 20hp motor starting as it could be a few hundred amps

Limits are usually 5, 7.5 or 10hp on the high end for residential service
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,054
Location
Modesto, CA
Had to look it up - 1ø 230 V, a 20 HP motor pulls 88 amps.

where did you come up with 88a? the NEC FLC chart for single phase doesnt go past 10HP, which is 50a

regardless, the in-rush current would be 4-8x and a residential service would not support that kind of load starting on the line.

most PoCos also have HP limits for residential services and small commercial.... you will probably trip the main breaker starting that motor
 

jar944

Well-known member
Joined
Jul 26, 2010
Messages
5,948
Location
Northern VA
regardless, the in-rush current would be 4-8x and a residential service would not support that kind of load starting on the line.

most PoCos also have HP limits for residential services and small commercial.... you will probably trip the main breaker starting that motor

Ideally op needs a 3ph motor and a soft start (vfd or otherwise) if they want 20hp on single phase power. Now that does assume the compressor would function with a soft start.
 

jblnut

ALLIANCE MEMBER
Joined
Jan 17, 2015
Messages
7,104
Location
In the Middle of MN
As mentioned I’d absolutely check with the PoCo before wiring up a 20hp single phase motor. We asked about a 15hp single phase motor for a grain bin and they said “sure, as long as you sign this paper that says you’re responsible for any issues on the line up to the substation that we think you caused”. WTF yeah nope lol. So anything larger than 10hp here is 3ph and is either on a rotary phase converter or a VFD.
 

jblnut

ALLIANCE MEMBER
Joined
Jan 17, 2015
Messages
7,104
Location
In the Middle of MN
Ideally op needs a 3ph motor and a soft start (vfd or otherwise) if they want 20hp on single phase power. Now that does assume the compressor would function with a soft start.
I have a 40hp well pump behind a rotary converter with no soft start that I know of unless the rotary converter has one built in but I don’t think it does. But the same dudes wouldn’t let me start a 15hp single phase motor for some reason lol.

Why wouldn’t a compressor work with a soft start ? The unloading valve should have the head at 0psi so it should fire up just fine even if it isn’t getting max amps/hz right away. My larger grain bin fan motors on VFD’s are using the VFD exclusively to ramp up to max speed. They start under a larger load right away than a compressor would I’d think.

It’s a distinct possibility I don’t understand how a soft start works and if so please disregard 🫣
 

Lassen Forge

Well-known member
Joined
Apr 26, 2014
Messages
15,336
Location
The romantic hills of central Umbria, Italy,
where did you come up with 88a? the NEC FLC chart for single phase doesnt go past 10HP, which is 50a

regardless, the in-rush current would be 4-8x and a residential service would not support that kind of load starting on the line.

most PoCos also have HP limits for residential services and small commercial.... you will probably trip the main breaker starting that motor

It was some chart on an electrical supply site's catalog - contactor section....

https://www.sprecherschuh.com/content/dam/sprecher-schuh/ecatalog/hp-volts-fla_charts.pdf

Probably read it wrong - in a pinch I defer to those who actually KNOW this stuff.
 
To avoid these ads, REGISTER NOW!
Top Bottom