Wiring a 100amp outlet/connection- typical practice?

tarbellb

Well-known member
Joined
Apr 17, 2011
Messages
5,765
Location
Oregon
Im in the middle of a service line upgrade for my property and shop.

I will need a few high amp connections in the shop for certain tools (large 20hp VFD screw compressor, laser machine, welders, etc..)

What is considered best practice or typical for a 100amp and 60amp 1ph 240v connection
_ hardwired?
_ do i need or want a shutoff
_ anything else to consider


My setup will be using surface mount conduit, the run from box to panel is under 10ft
 
To avoid these ads, REGISTER NOW!

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,605
Location
BC
Pin/sleeve is often used for these higher amp connections. I would hardwire though, as those get really pricey.

At 10' I'm content to use the breaker as the disconnect.
 
To avoid these ads, REGISTER NOW!

matt_i

Well-known member
Joined
Mar 14, 2008
Messages
10,734
Location
SE Michigan
Hardwired is cheapest but gives minimum flexibility in the layout as times change. 3 pole non-fused disconnects are still pretty cheap, in good-used condition, if you want to go that route.

A screw compressor or machine tool (etc) may have its own 3 pole disconnect native to the machine...
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,748
Location
Richmond, VA
If all the equipment will be line of sight to a spot in the shop, a sub panel would likely be easiest.

How are you hooking up the 20hp vfd? That's not single phase, right?
 