The electrician is doing some of the wiring on the shop. I had the idea of running a 120v wire to the a switch by the man door (next to the light switches) which I would use to trigger a solenoid that switches power to the 5hp compressor. When I leave for the day I would flip that switch off along with the light switches.

The electrician suggested a countdown timer switch like the spring loaded ones that turn on the heat lamp in a motel room but I kinda don't like that as they tend to go off when I'm in the middle of something.

Any other ideas?
 
To avoid these ads, REGISTER NOW!

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,605
Location
BC
If the compressor uses a starter/contactor, it's very easy to switch the control power at the light switch.

If it's just a line-start pressure switch on the machine, then you may as well train yourself to switch it locally, or kick off the breaker when you close up the shop.
 

Citation

Well-known member
Joined
Jan 20, 2016
Messages
3,222
Location
Indy
If the compressor uses a starter/contactor, it's very easy to switch the control power at the light switch.

If it's just a line-start pressure switch on the machine, then you may as well train yourself to switch it locally, or kick off the breaker when you close up the shop.
I agree with this.

A number of threads have covered this topic. With a starter contactor it's relatively easy as you just need to wire a low current (but 240V) relay inline with the pressure switch. You flip the switch, the relay turns off then the pressure switch can't turn on the motor. You could even make it a simple switched outlet by the compressor then get a simple 12 control (240V double pole) relay and power it off a simple 12V wall wart. Plug a lamp into the other plug in the switched outlet. If the lamp is on, so is the compressor.


If your compressor doesn't use a starter then it may be worth it to add one. A 5ho motor rated relay is basically a starter.
 
OP
E

ericm

Well-known member
Joined
Apr 17, 2016
Messages
1,963
Location
Southern Oregon
A lot of the more affordable 5hp compressors use pressure switches. I was planning on converting to a contactor.

My present setup has a 2hp compressor with the usual pressure switch, in a cabinet. For whatever reason, I sometimes forget to shut it off.

I'm also considering plumbing in an electric valve to close off the piping when the compressor is turned off.
 

ArcReactorKC

Well-known member
Joined
Jun 1, 2019
Messages
2,237
Location
Out in the county NE of KCMO
If we are going to "automated" solutions like your electrician is suggesting you could put an aqara presence sensor and a smart relay in that would only allow the compressor to run when it senses a living human in the shop.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,041
Location
Modesto, CA
A lot of the more affordable 5hp compressors use pressure switches. I was planning on converting to a contactor.

My present setup has a 2hp compressor with the usual pressure switch, in a cabinet. For whatever reason, I sometimes forget to shut it off.

I'm also considering plumbing in an electric valve to close off the piping when the compressor is turned off.
if no contactor on the current setup, you would need a motor rated switch such as the leviton model below

 

kabinenroller

Well-known member
Joined
Sep 14, 2013
Messages
906
Location
S.E. Wisconsin USA
I wired a 110volt light fixture with a red LED bulb to one leg of the 220v on the disconnect box for my compressor. When the power is turned on by flipping the disconnect box lever the compressor gets 220 and the fixture gets 110. My compressor is in a separate room of my shop and the fixture is in the main work area within clear sight from anywhere in the work area. I also have a ball valve on the outlet port of the compressor so that there will be no bleed down of pressure when the compressor is not powered.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,759
Location
NW Iowa
Just install a contactor with the coil tied to the lights. Lights off = compressor off

I wired a church kitchen last year. Plumber installed a circulating pump for hot water. They were talking about a timer or a dedicated switch. I told them I'll just put it on with the lights. Simple and they have been happy.
 

SouthernIllinois

Well-known member
Joined
Jan 14, 2024
Messages
1,679
If the green light is on, the compressor is energized. If it’s not, the disconnect is open (off)

If the red light is on, the Milwaukee, Dewalt and Stihl chargers are energized. If it’s not, the power to them is secured.

The lights are port & starboard running lights off an old Great Lakes Freighter.

IMG_6911.jpegIMG_6912.jpeg

The compressor disconnect switch (pic was before wiring was in place)

IMG_6844.jpeg

The tool battery charging station (panel cover is off because we are still wiring the shed)

IMG_6910.jpeg
 

niget2002

Well-known member
Joined
Oct 2, 2012
Messages
11,171
Location
Josephine, TX
My plan is to install a pool pump timer on mine. I'm going to set an "off" time at 10pm. I'll manually flip the switch to turn it on. If I forget to turn it off, it will turn itself off.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,008
Location
NJ
My plan is to install a pool pump timer on mine. I'm going to set an "off" time at 10pm. I'll manually flip the switch to turn it on. If I forget to turn it off, it will turn itself off.
Check the hp rating of the time clock.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,748
Location
Richmond, VA
The one I'm looking at supports a 40A load.
That's not the same as a HP rating.

For example, a 50a 6-50 plug is only rated for 3hp.

This thread has some info on why there is a difference

 

rust in the eye

Well-known member
Joined
Oct 2, 2017
Messages
2,802
Location
Chicagoland
If the compressor uses a starter/contactor, it's very easy to switch the control power at the light switch.

If it's just a line-start pressure switch on the machine, then you may as well train yourself to switch it locally, or kick off the breaker when you close up the shop.
I've been told that breakers should not be used as a switch. They certainly aren't designed as such.
 
To avoid these ads, REGISTER NOW!

dchawk81

Well-known member
Joined
Jul 31, 2014
Messages
14,408
If the green light is on, the compressor is energized. If it’s not, the disconnect is open (off)

If the red light is on, the Milwaukee, Dewalt and Stihl chargers are energized. If it’s not, the power to them is secured.

The lights are port & starboard running lights off an old Great Lakes Freighter.

IMG_6911.jpegIMG_6912.jpeg

The compressor disconnect switch (pic was before wiring was in place)

IMG_6844.jpeg

The tool battery charging station (panel cover is off because we are still wiring the shed)

IMG_6910.jpeg
The Edmund Fitzgerald? 🤔
 

MFortie

Well-known member
Joined
Aug 9, 2010
Messages
902
Location
San Diego County
I did what you suggested (relay off a light switch), except I sourced the 120v off one of my banks of lights. I always shut off my lights when I close up the shop, so the comp is definitely off.

In my shop I have three bays. Each bay has a bank of 4 lamp fixtures. Each fixture is controlled by two switches - two lamps per switch (multiple fixtures per switch). I rarely light up all the lamps, so I tied the comp relay to the least used bank.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,767
That is more about opening them under load.

Some breakers are marked/designed for switching duty.

Like anything, if it wears out, replace it.
The SWD rating on 15 & 20A single pole breakers is intended for fluorescent lighting, there is also a HID rating available but both those types of lighting are pretty much obsolete.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,982
Location
Central Iowa
I put switches for both of my compressors near the light switch. The 60 gallon switch is right under the light and the 30 gallon is about 5' away because I am too lazy to get out a bender and piece of EMT.
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,671
Location
Fargo, ND
My compressor controls are wired to the shop lights. Works great for me. A count down time would be my second choice. A switch by the door is just one more thing to remember. Do some sort of control that you don't have to think about.
 

jblnut

ALLIANCE MEMBER
Joined
Jan 17, 2015
Messages
7,094
Location
In the Middle of MN
I have a bathroom fan timer wired in to control a contactor that controls the entire circuit the compressor is on. It’s rare that I run the compressor longer than 60min but if I need to I’ll go push the button again. I have a 120v light wired to the contactor that lights up when it’s pulled in. If I’m doing air things and see the light is out I go push the button again. No big deal.
IMG_3198.jpeg
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,759
Location
NW Iowa
I've been told that breakers should not be used as a switch. They certainly aren't designed as such.
Breakers under 60 amp are cheap and easy to replace. You can buy several breakers for the price of a contactor or knife switch.

I use the breaker to control the auger motor all the time on farm bins. Up to 10hp 1 ph motors.
 

rust in the eye

Well-known member
Joined
Oct 2, 2017
Messages
2,802
Location
Chicagoland
Breakers under 60 amp are cheap and easy to replace. You can buy several breakers for the price of a contactor or knife switch.

I use the breaker to control the auger motor all the time on farm bins. Up to 10hp 1 ph motors.
I have to wonder if all the cycling when being used as a switch compomises its intended function. Like most things it works until it doesn't. Consequences of a failed breaker?
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,759
Location
NW Iowa
The
I have to wonder if all the cycling when being used as a switch compomises its intended function. Like most things it works until it doesn't. Consequences of a failed breaker?

Yes it wears them out. The catch inside gets weak. It will trip before it's supposed to and often you won't be able to reset it.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,041
Location
Modesto, CA
I have a bathroom fan timer wired in to control a contactor that controls the entire circuit the compressor is on. It’s rare that I run the compressor longer than 60min but if I need to I’ll go push the button again. I have a 120v light wired to the contactor that lights up when it’s pulled in. If I’m doing air things and see the light is out I go push the button again. No big deal.
IMG_3198.jpeg
no overloads on the contactor for the compressor? does the motor have built-in OL protection?

Is that cordage going into the panel? (white cable top of panel)?
 
Last edited:

jblnut

ALLIANCE MEMBER
Joined
Jan 17, 2015
Messages
7,094
Location
In the Middle of MN
no overloads on the contactor for the compressor? does the motor have built-in OL protection?

Is that cordage going into the panel? (white cable top of panel)?
The contactor/timer is on a 50a breaker inside the panel if that’s what you mean by overloads ? The compressor motor also has that annoying little red button on the side that’ll pop if something gets pissy out by the compressor.

Looks like ancient UF to me. That might have been installed by Abe Lincoln during in apprenticeship.
Yes it’s older UF running a 1hp dust collector.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,041
Location
Modesto, CA
The contactor/timer is on a 50a breaker inside the panel if that’s what you mean by overloads ? The compressor motor also has that annoying little red button on the side that’ll pop if something gets pissy out by the compressor.
nope. a breaker is not the overload protection for a motor of this size. notice the FLA on the motor nameplate is a lot lower than 50a? the red button on the back of the motor is part of the overload assembly in the motor however some motors do not have this integral overload protection so it needs to be provided with the contactor aka starter. it would go below the contactor then the motor connections are terminated on the load side lugs of the overload

the breaker is solely for short circuit and ground fault protection. it will not protect the motor or wiring.
 