I’m in need of some assistance, I bought a new Champion VRV7F with a 7.5 hp motor. It’s 220v single phase. I haven’t had to deal with much a/c wiring before. I’m mostly wondering what to do with the white neutral wire. Does that just get hooked to the ground with the motor? I’ve attached an image of what I’m dealing with.
Untitled by just a noob, on Flickr
 
Last edited:
To avoid these ads, REGISTER NOW!

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,715
Location
NW Iowa
Pull it out or cap it. You don't need a neutral.

2 hots and ground is what it takes.
 

Terry D

Well-known member
Joined
Mar 25, 2015
Messages
2,202
Location
St. Louis, MO.
It doesn't look like you ran a equipment ground on your line side. Assuming this goes to a disconnect or J-box on the wall. You must replace that white with a green conductor of the correct size. Code only allows you to re identify a conductor #4 and larger. You are not allowed to use FMC for the equipment ground when it is installed for flexibility to prevent transmission of vibration. 348.60 of the NEC. Just add another lug or change the existing lug to a two barrel to land the equipment ground.


Sent from my SM-G960U using The Garage Journal mobile app
 
Last edited:
OP
J

just a noob

Well-known member
Joined
Oct 24, 2013
Messages
261
It doesn't look like you ran a equipment ground on your line side. Assuming this goes to a disconnect or J-box on the wall. You must replace that white with a green conductor of the correct size. Code only allows you to re identify a conductor #4 and larger. You are not allowed to use FMC for the equipment ground when it is installed for flexibility to prevent transmission of vibration. 348.60 of the NEC. Just add another lug or change the existing lug to a two barrel to land the equipment ground.


Sent from my SM-G960U using The Garage Journal mobile app

Exactly what I did. I didn’t want to be that ******* that burned down his own shop :thumbup:
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,933
Location
Coronado, CA
I can’t argue with the letter of the law, in this case the code book.

If it was my compressor you might find a green paint on a conductor that lands on the same buss bar as the green wires.

I will admit to knowing just enough to be dangerous.
 
To avoid these ads, REGISTER NOW!
OP
J

just a noob

Well-known member
Joined
Oct 24, 2013
Messages
261
Why are you using all three starter contacts with single phase?

I only put wires in l1 and l2, l3 was installed when I got it.

what size breaker did you use?

how far away is the panel and is it within site of the compressor?

I put a 60 amp breaker in the main box and used 6 awg cable.

The panel is probably 3 feet away from the main breaker box, the compressor is about 2 feet away from the disconnect.
 