Wiring question 240v to my jointer
gygeneral
Ontario, Canada
In my garage I have a 30 amp 220v breaker in my subpanel, wired with #10 wire, going to 3 -30 amp welder type receptacles.
I just bought a jointer motor 220v, 15 amp motor with a smaller 220v plug on the end. I believe its a 6-20 plug
I would like to simply change out one of the three existing receptacles with the appropriate smaller 220v to match the plug on the jointer.
Is this something I can do? or do I have to either swap out the 30 amp breakers to 20 amp , then the existing receptacles I would have to remove so I don't accidentally plug a tool with a higher than 20 amp load. I don't think the no 10 wire will be an issue.
Thanks
mike93lx
Richmond, VA
I guess I'm asking if this can cause a situation where the motor for some reason draws more amps due to a malfunction and causes a fire.
A fire isn't going to start from it pulling an extra few amps.
I'd likely change the jointer plug as well
Firebrick43
West central Indiana
If you have 6-30r receptacles they are only HP rated to 2 hp.
15 FLA at 240v is almost 3 hp.
Doe your new motor have an overload built in or the machine it’s installed in per 430.32?
G
gygeneral
Ontario, Canada
I read the manual , no mention of overload protection, all it says it must be on a circuit 240 with minimum 20amp.
G
gygeneral
Ontario, Canada
Found the wiring diagram, I see Thermal Overload there in the mag switch, I'm not an electrian but is this what i think it is.
Firebrick43
That is it and therefore your good. (y)
Many are built into the motor itself and people will not be aware of that when they replace it which is why I asked.
G
gygeneral
Ontario, Canada
Thanks for confirming, so to recap , I can either change the plug on the jointer to a 6-30p or change out one of the 6-30r receptacles to the one that matches the plug on my jointer which is a 6-20p. I guess there are also adapters I can get, altough more expensive, it would allow me to plug my jointer in any of the 3 plugs I already have.
Firebrick43
Your manual says no adapters and at that horsepower I would agree. Most of the adapters are not UL listed anyways, only a few lower amp ones are.
I would switch out the plug to 6-30p
mikedodge
I'd rather change the plug on the one machine then one outlet. Then someone comes along in the future and thinks that outlet is protected at the lower amperage, or you can't plug something else there if it's the more convenient location.
G
gygeneral
Ontario, Canada
Many thanks for the advice, Changing out the plug makes most sense and it accomplishes leaving my receptacles alone and then I can plug my jointer in any of the three receptacles.
mm08822
6-30p is good enough. Don't open under load. Starter has o/l protection.
Maybe 6-30P's are your go to as you get more equipment......no adapters, multiple locations to plug in.
If you ever need an extension cord....6-30's on both ends are the answer. It's a home shop and you are there when equipment is running.
micromind
Fernley, Nevada, about 30 miles east of Reno.
With motors, the circuit breaker is there for short-circuit and ground-fault protection, the overload will protect the motor and wire.
The largest breaker allowed for a 3HP single-phase motor operating at 230 volts is 45 amps. There is no minimum.
G
gygeneral
Ontario, Canada
Can someone explain to me why some 3hp motors have an amp rating of 15 amps and I've seen some as low as 9 amp. I noticed when I was shopping for a new jointer, eventually buying this used one. Just curious, is there some kind of efficiency factors involved here, like a good motor uses less amps as opposed to a crappy motor.
mike93lx
Richmond, VA
The ones saying 9a are lying about the HP
Many motors use the ********® scale of rating
u2slow
BC
It's the HP # that is fiction on lots of shop tools. Amps is amps. Capacitors may be employed, and that can reduce the running amps a little.
Efficiency difference is almost nothing these days.
jar944
Northern VA
FLA = (hp * 746) / (1.73 * V * pf * efficiency)
Pf and efficiency will be the variable between different motors.
micromind
They have charts that assign Horsepower by the Full Load Amps (FLA) listed on the data plate. Just make sure you are looking at a single phase section or table and not a 3 phase table
Typical online chart........partly accurate, partly way off.........
Note how it states that 'IN ALL CASES the current shown on the motor nameplate is the correct value for that particular motor and takes precedence over any value shown in this table'.
NEC 430.6(A)(1) states that the table values shall be used to determine the ampacity of conductors or amp rating of switches, short-circuit and ground-fault protection instead of the actual current rating marked on the motor nameplate.
Which one would you use? The code or some idiotic internet chart?
P.S. The values listed in the chart are the same as listed in the code.
Firebrick43
Its a general chart. All its stating that the current(FLA) might not match up exactly with the chart due to efficiency and power factor.
Some motors are made with higher (or lower) quality materials and methods giving them higher (or lower) efficiency. There is no way for all of them to match up exactly with a chart.
The chart is simply to corollate FLA to HP , and the chart works well for that. The OP saw some at 15 amps which is a little under the 17 amps on the chart for 3 hp but not too far off. We have no idea if its an efficiency thing or its really a 2.5 hp motor without more info.
But we can see that the 9 amp motor by the chart is in no way close to 3 hp, its half of that. Unless some new tech has been invented that none of know about, there is no possible way its a 3 hp motor
There was no implied notion to use the chart to size conductors and other current sized components?
mm08822
Why read the small print? Whose got time for that?? It's more useful to take things out of context. :lol_hitti
u2slow
BC
FWIW, using nameplate values is Code in Canada. Table values are for when motor/equipment is not available.
G
gygeneral
Ontario, Canada
Just change the plug on the jointer. I have all my shop equipment on 6-50 plugs.
Today I changed out the jointer plug with a 6-30 plug. I had some issues to tighen up the terminals I'm guessing because the wire from the machine is 12/3 and this 6-30 plug is made for 10/3 I could not get them tight enough. I had to bend the terminal a little to make the opening a little smaller then I was ok. Here where I live I could only find those combo plugs that can do 30 or 50 amps, I don't if there is such a thing as a 6-30 made for 12/3. Anyhow seems to work and everything was nice and tight
thats a full load current chart and it doesnt correspond to FLAs on nameplates as the values in these charts are much higher. also the codes have been updated to 430.248 & .250.
Bert_
NW Iowa
For smaller wire I will strip extra and fold the wire. Ends up 2x as thick.
Firebrick43
Did you read the context on what I was replying to that the OP asked? Did you read post 29? It was in reference to a motor that claimed it was 3hp but only pulled 9 amps.
I wasn't suggested to size anything based off the chart.
You can read the chart but not the rest of the thread? And the values for 240v single phase motors on 430.248 are the same from the version I posted?
youre not really paying attention here
what i was alluding to is that FLA and FLC are not one in the same.
you claimed there are charts that assign HP based on FLA and that chart you posted claimed to be typical FLA ratings but clearly its an FLC chart from the NEC, which are NOT typical FLA ratings at all. The FLC ratings are MAX amp ratings for a motor of a given HP. so the chart is misleading and what you claimed is misleading as well.
You cant use an FLA rating off a motor nameplate and then use an FLC chart from the NEC to guess the HP rating. you will get it wrong because FLAs and FLCs from the NEC table do not coincide. you are to use the amp rating in the FLC chart based on the HP rating from the motor nameplate.
The reason i brought up 430.248 and .250 is because at the bottom of the chart it claims the data was from 430-148 and 430-150 which is really old.