what type of wire?
diesel06
pennsylvania
running all new wire in my pole barn, new service has already been ran, want to run new wirings for lights and electrical outletss, not sure what type of wire i need to use
wyliesdiesels
Modesto, CA
Depends on the framing. If u have wood studs u can bore through them and run 12/2 NM-b aka Romex. If metal, i would use EMT or PVC(if u cant bend conduit) conduit. Conduit is more versatile...can u post some pics...also any 240v equipment?
D
diesel06
pennsylvania
its a wood post frame, two 240 plugs one for air compressor one for welder
Slowgsr
Southern ontario
If you don't have the needed skills for Emt, I would run bx (ac90) if you want things on the surface like that or plan to leave it exposed
alfredeneuman
Fullerton, CA
AC and MC cables both have exactly the same rules for protection against physical damage as Romex.
If you don't have the skills needed for EMT..... Flexible Metal Conduit isn't subject to the same restrictions, and can be run exposed or concealed
D
diesel06
pennsylvania
5hp 80 gallon, i know ill have to run a bigger wire size for the 240 plugs from the subpanel just not sure what it needs to be, i plan on insulating all the walls and finishing them in white metal so no wires will be exposed
wingfootedgodhead
Oregon (dry side)
For what it's worth, years of experience wiring then rewiring my 80 x 40 x 16 pole barn
Start with a plan, consider that you will initially WAY OVERSIZE your initial requirements. Consider future high output lighting, compressor, post lift and welder as well as general electrical requirements.
Consider future addition of generator and battery inverter / solar backup.
Don't forget multiple sub panels and junction boxes up along every top of the posts.
Accommodate both 240V and 120V circuits.
Use EMT. Romex is ****. DIY EMT is a long process, but ultimately rewarding.
Don't use anything less than 3/4 EMT and a minimum of 1 inch is better.
Buy a scissors lift on EBay. You are going to be up on the ceiling for a while...
wyliesdiesels
Modesto, CA
Since its 5HP, it needs to be hardwired.
D
diesel06
pennsylvania
right, it will have its own through switch box correct? yes i do plan on adding a lift thanks for reminding of that option, if i used emt what wire would i use, if u opted not to use emt what would be the next best thing
wyliesdiesels
Modesto, CA
U said u were going to put in a receptacle for the compressor. U cant do that as the compressor is rated for 5HP. Standard NEMA plugs are rated at 3HP...
For wire u need either #10 THHN in EMT or #8 NM-b....and u need a disconnect at the compressor if its more than 50' from and out of sight of the electrical panel...