what type of wire?

diesel06

Well-known member
Joined
Nov 3, 2014
Messages
50
Location
pennsylvania
running all new wire in my pole barn, new service has already been ran, want to run new wirings for lights and electrical outletss, not sure what type of wire i need to use
 
To avoid these ads, REGISTER NOW!

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,031
Location
Modesto, CA
Depends on the framing. If u have wood studs u can bore through them and run 12/2 NM-b aka Romex. If metal, i would use EMT or PVC(if u cant bend conduit) conduit. Conduit is more versatile...can u post some pics...also any 240v equipment?
 
OP
D

diesel06

Well-known member
Joined
Nov 3, 2014
Messages
50
Location
pennsylvania
its a wood post frame, two 240 plugs one for air compressor one for welder
 

Attachments

  • 179.jpg
    179.jpg
    141.2 KB · Views: 68
  • 184.jpg
    184.jpg
    146.9 KB · Views: 63
  • 182.jpg
    182.jpg
    147.8 KB · Views: 57

Slowgsr

Well-known member
Joined
Nov 14, 2014
Messages
610
Location
Southern ontario
If you don't have the needed skills for Emt, I would run bx (ac90) if you want things on the surface like that or plan to leave it exposed
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,581
Location
Fullerton, CA
If you don't have the needed skills for Emt, I would run bx (ac90) if you want things on the surface like that or plan to leave it exposed

AC and MC cables both have exactly the same rules for protection against physical damage as Romex.

If you don't have the skills needed for EMT..... Flexible Metal Conduit isn't subject to the same restrictions, and can be run exposed or concealed
 
To avoid these ads, REGISTER NOW!
OP
D

diesel06

Well-known member
Joined
Nov 3, 2014
Messages
50
Location
pennsylvania
5hp 80 gallon, i know ill have to run a bigger wire size for the 240 plugs from the subpanel just not sure what it needs to be, i plan on insulating all the walls and finishing them in white metal so no wires will be exposed
 

wingfootedgodhead

Active member
Joined
Feb 5, 2009
Messages
41
Location
Oregon (dry side)
For what it's worth, years of experience wiring then rewiring my 80 x 40 x 16 pole barn

Start with a plan, consider that you will initially WAY OVERSIZE your initial requirements. Consider future high output lighting, compressor, post lift and welder as well as general electrical requirements.

Consider future addition of generator and battery inverter / solar backup.

Don't forget multiple sub panels and junction boxes up along every top of the posts.

Accommodate both 240V and 120V circuits.

Use EMT. Romex is ****. DIY EMT is a long process, but ultimately rewarding.

Don't use anything less than 3/4 EMT and a minimum of 1 inch is better.

Buy a scissors lift on EBay. You are going to be up on the ceiling for a while...
 
Last edited:

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,031
Location
Modesto, CA
5hp 80 gallon, i know ill have to run a bigger wire size for the 240 plugs from the subpanel just not sure what it needs to be, i plan on insulating all the walls and finishing them in white metal so no wires will be exposed

Since its 5HP, it needs to be hardwired.
 
OP
D

diesel06

Well-known member
Joined
Nov 3, 2014
Messages
50
Location
pennsylvania
right, it will have its own through switch box correct? yes i do plan on adding a lift thanks for reminding of that option, if i used emt what wire would i use, if u opted not to use emt what would be the next best thing
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,031
Location
Modesto, CA
right, it will have its own through switch box correct? yes i do plan on adding a lift thanks for reminding of that option, if i used emt what wire would i use, if u opted not to use emt what would be the next best thing

U said u were going to put in a receptacle for the compressor. U cant do that as the compressor is rated for 5HP. Standard NEMA plugs are rated at 3HP...

For wire u need either #10 THHN in EMT or #8 NM-b....and u need a disconnect at the compressor if its more than 50' from and out of sight of the electrical panel...
 