Connecting SER cable to MHF
75gmck25
Alexandria, VA
I have 2-2-2-4 aluminum SER cable running from my main electrical panel over to the exterior wall closest to the garage. At the wall I need to transition to 2-2-2-4 MHF so that I can make the buried wire run over to my detached garage and connect to a sub-panel. I will be using a 60 amp breaker at the main panel, so the wire size is well within the specs for amps and distance.
What do I buy to make the interconnection between SER and MHF inside the junction box? Do I buy an empty plastic or metal junction box and then use approved wire splices (barrel splice?) inside the box? Anyone have a suggested brand/type of wire splice that will be code compliant for #2 aluminum wire?
Thanks,
Bruce
theoldwizard1
SE MI
Polaris connectors are very common for splicing large wire such as 2 AWG. Not sure if Home Depot has them, but they are common. They are not a true "**** splice" but the should work well for your application.
I am not sure if it is approved for aluminum wire, but the old split bolts work well also. You MUST do at least a double wrap of GOOD (3M 88) electrical tape.
Some one else will have to recommend what size box you need for your splices.
Bert_
NW Iowa
Polaris connectors, Many split bolts are rated for aluminum, You could also use a terminal box
Midwest and I'm sure other manufacturers make them. Available in 60A, 100A and up. About $100, probably not much more expensive by the time you purchase a box + individual connectors and they are very installer friendly.
75gmck25
Alexandria, VA
Those terminal boxes are probably overkill, but would be really convenient. It looks like the size I need would cost about $110.
I found a few wire splice supplies at Home Depot, but the stock was limited. However, I could get the splices for about $2.50 each, and then add heat shrink or tape for insulation.
Bruce
Radix2
the thumb!, MI
Bruce
Splicer/reducer if you want inline, split bolts if you want side by side.
The Polaris are for the trust fund guys or those who take them from work...nice tho.:eek: