5hp 240 Volt Air compressor Install
Bert_
NW Iowa
#10 thhn is fine. No need to change that part. Romex is limited to lower ampacity than thhn.
Agree with sberry that 40 is about the right size breaker. I would really consider a 30 to be to small. You are actually allowed up to a 70A breaker according to the NEC.
sberry
Brethren, Michigan
I believe if it was 70 might have to be 8 wire ???? I have ran them from 30, my bud had a 28A one ran 30 for 30 yrs. I have a 24A that runs 30,,, I had the breaker in hand, it never caused a problem. But there isn't a problem putting a little headroom in.
Bert_
NW Iowa
No restriction on wire size vs breaker size. If you had an application were the motor wouldn't reliably start on a 70A (250% of FLC). You are actually allowed to go up to a 100A breaker (max 400% of FLC). All this is allowed on #10 thhn or #8 Romex.
I agree that many will run fine on a 30. But if you're wiring it from scratch I can't think of a single reason to use less than a 40. A 30A leaves the possibility of nuisance trips in my book.
sberry
Brethren, Michigan
I can be wrong here,, so,, fwiw,, if a guy was to use 100 would need 8 wire. Seems I did this in study somewhere along the way but some other part of code applies, 10 to 60, 8 to 100. 12 on 50,, like the welder, it may run on 14 but has to have the breaker reduced to 30
A
AllThingsOld
My house
They didn’t have the wire I went to buy, the guy working was zero help, but they had the 6 THHN, so I just bought it and will use it in place of the romex. I didn’t want to make 2 trips.
Bert_
NW Iowa
There is absolutely no need for #6 anywhere on this project.
The sizes you need are,
#8 for any Romex
#10 for any thhn
Anything else is a waste of money.
sberry
Brethren, Michigan
It isn't in motors, it's some other part that escapes me at the moment. It's been so long since I really read it I have troube with 250, 310 and 630,,,, ha
Kaizen
New England
Overkill but will work fine. Make sure you use insulator bushings or screw in ones on that flex. Also easier to push wire through before connecting to both sides.
A
AllThingsOld
My house
I am half way there, I just need to wire the compressor in now
A
AllThingsOld
My house
And it doesn’t work. Everything is wired properly, not tripping the breaker, it’s definitely getting 120 on each side of the switch. I can hear the motor trying to start, but it doesn’t. Now when I flip the pressure switch on, I get nothing, no sound.. I want to pull my hair out
wyliesdiesels
Modesto, CA
Are you using a double pole breaker?
Did you test line to line at the switch?
Bad capacitor?
A
AllThingsOld
My house
Yes, first thing I checked was power at the switch, I have 120 per side. The motor is making some strange sound, like an electric humm. I hope it isn’t the kiss of death for the motor.
Bert_
NW Iowa
Motor doesn't care about 120 to ground. It needs 240 volts line to line. That is where you need to connect your meter, line to line. Testing to ground tells you nothing.
A
AllThingsOld
My house
I didn’t do anything with this wiring, I probably should have checked it.. who am I kidding, I would not even know what to check.
A
AllThingsOld
My house
230 yes... I just turned the switch on, motor started making that hmmm sound, I hit the reset button and it tripped the breaker
A
AllThingsOld
My house
No, it’s not a new compressor, used. It’s the Harbor Freight 93274 2 stage... I have spent so much money at this point, that I let the “good deal” cloud my decision making and I cannot believe I bought it without hearing it run. Long story short. I bought a blast cabinet, didn’t realize how much air I actually needed.This is the 3rd compressor I have bought in a short amount of time, the others just undersized. Bought this used and the guy delivered it.. I’m a complete idiot and took him at his word that it ran great, no issues etc.. This blast cabinet adventure has cost me a fortune and I’m not up and running yet.
Bert_
NW Iowa
I agree it could be a capacitor. It would be under a round cover on the side of the motor. It's worth checking.
A
AllThingsOld
My house
Motor has 2 round covers, should I just check both of them ? Should I just check the part # and order 2 or ?
Bert_
NW Iowa
You can kind of test them with an ohm meter. Won't be able to tell you and exact value but can usually tell you good / bad.
Pull the covers and just look at them visually first. Oftentimes the problem is obvious.
Terry D
St. Louis, MO.
I would still isolate the motor from the compressor, to make sure its not a compressor problem. make sure the compressor spins freely, make sure it wasn't ran without oil. If you bought it from some one that you don't know, make sure its even the right capacitors for that motor. If it doesn't say on the motor, google it.
A
AllThingsOld
My house
Compressor spins freely, which is sort of a relief, I guess. I have called the seller and sent him a text, no reply of course. Which it’s my fault, I should have made the time to insure it ran, instead of taking his word and him delivering it, such a stupid move by me. I’m about to look at the capacitors now.
A
AllThingsOld
My house
Not sure if this is right or wrong, but it doesn’t seem right. 2 different capacitors and wired differently. I am hoping this is the issue, so that I can just replace one or both. I can see the the top of the second one appears to be leaking. I believe the one in the first photo has been replaced already, possibly, but it only has 2 wires, while the second capacitor has 3... Also they are much different in size, is this correct ?
wyliesdiesels
Modesto, CA
The cap with 3 wires is most likely a dual cap- typically start and run, built into one canister.
If one is leaking, then its going bad and should be replaced.
pattenp
Virginia - USA
Neither of those caps are dual. There would be three separate insulated connectors. The metal one is a run, the plastic one is the start.
A
AllThingsOld
My house
I m trying to figure out if both capacitors are the stock units or if they have been replaced. I found this one on amazon, I believe this is what I need