#10 thhn is fine. No need to change that part. Romex is limited to lower ampacity than thhn.
Agree with sberry that 40 is about the right size breaker. I would really consider a 30 to be to small. You are actually allowed up to a 70A breaker according to the NEC.
Agree with sberry that 40 is about the right size breaker. I would really consider a 30 to be to small. You are actually allowed up to a 70A breaker according to the NEC.