Small slab on grade buildings can make it very difficult to cram all the mechanical and electrical stuff in that you need to make the house work....a lot easier with a full basement.I haven't been involved with one in at least 8 years
 

Higgins

Well-known member
Joined
Dec 25, 2009
Messages
1,939
Location
Shepheardsville, KY
It's 36" in front and 6'6" high. 30" total width, including the panel
Thanks !!! Couldn't remember. However, the inspectors in IL do check for that on inspections! It seams the only ones they seamed to leave alone were the ones built by Levitt?? back in the early 50's and were more or less prefab with the panel in a kitchen closet!
 

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
Curious why you think this. My house was built with homeline panels in '03. Still working fine and they are certainly not junk
At what point in my post did I say anything bad about homeline panels?
They've been my go to panel for residential work since the early 90s.
I said service panels in coat/clothes closets are generally frowned upon unless it's an origional install to the house when built.
I said the homeline panel was probably a change out at some point,and probably wouldnt be allowed if it was inspected.
Unfortunately, electrical Codes have little control what homeowners and other trades do after the fact.

Homeline in '03? I was still installing FPE panels... Homeline (that replaced it) hadn't come out yet. :unsure:
I was at an open house at our local "sq d" supply house at the time(the old electric fixture and supply in omaha)
A rep from sq d was talking to me about their newer residential line,"home line".
That would of been around 95 maybe I'm thinking at the latest.
So they've been in our area for close to 30 years atleast that I've used them.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,981
Location
Central Iowa
Code requires 30" Left, Right, and in front of the panel!
It's 30" wide total, not left and right. It's also 36" in front (depth). What does that have to do with closets? I've seen bedroom closets bigger than my living room, but that doesn't mean a panel can be there.
 

Steve.S

Well-known member
Joined
Sep 25, 2011
Messages
1,660
Location
Cincinnati, Ohio
Unfortunately, electrical Codes have little control what homeowners and other trades do after the fact.

Homeline in '03? I was still installing FPE panels... Homeline (that replaced it) hadn't come out yet. :unsure:
I replaced our fusebox with a 200a Homeline panel in 2000.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,981
Location
Central Iowa
Guys...my house was built in 2009...inspected and everything passed with flying colors.Wired by a friend who was a master electrician for over 35 years. Its a utility closet that happens to have a few coats hanging there presently.
If the intended use is as a utility closet and you have the clearances, you should be ok. Just get rid of the coats and any clothes rods for a few minutes.
 

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
I am not sure about this and others will likely chime in. My only thought on this is that the breaker panel label/nameplate is usually on the inside of the can and after swapping the guts you will still have the old label which could be an issue.

Doing it is not an issue I think, but when times comes with UL and warranty it's probably out the door... do it right and replace it with a similar panel size is my IMHO.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,981
Location
Central Iowa
I promise I am not trying to be snarky. Is that definition universally or near-univerally agreed upon by inspectors? Or is it defined as such in the NEC?
Here is the definition, right out of the 2020 NEC. There is no definition of any other type of closet, so if it's not a clothes closet, and the clearances are there, a panel can be in a closet.
 

Attachments

  • clothes closet.jpg
    clothes closet.jpg
    306.1 KB · Views: 36

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,038
Location
Modesto, CA
Guys...my house was built in 2009...inspected and everything passed with flying colors. Wired by a friend who was a master electrician for over 35 years. Its a utility closet that happens to have a few coats hanging there presently.
It wasnt permitted to store clothes even in 2009 which means the inspector missed it....
I guarantee they won't be there when the inspector shows up.😁
doesnt matter. its a violation whether the inspector sees it or not.
What is the definition of "closet" I have been on several jobs the last year and every one had the panel in a "closet". Slab on grade construction...owners don't want to see that ugly panel.

Article 100, chapter 1
Clothes Closet: a nonhabitable room or space intended primarily for storage of garments and apparel.

Code requires 30" Left, Right, and in front of the panel!
not quite. its 30" side to side (doesnt have to be centered), 36" in front of panel, and 6.5' floor to ceiling

b106a0b5f236f8966b138803d0552d70.jpg
 
Last edited:

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,981
Location
Central Iowa
It wasnt permitted to store close even in 2009 which means the inspector missed it....

doesnt matter. its a violation whether the inspector sees it or not.
It doesn't sound to me like the intended use for the closet was for storing clothes. He said it's a utility closet that has a few coats hanging in it. What I refer to as a residential utility closet has the furnace and water heater in it also. I don't know if this is the case, but he did say it's a slab house so the mechanical has to go somewhere. That somewhere could be the attic, but that's a real ***** for the next guy.
 

walta

Well-known member
Joined
Jan 13, 2017
Messages
2,313
Location
Dutzow Missouri
What is the point of this post? Before you posted you had made up your mind exactly what and how you are going to do.

With master electrician friend that stuck you with an antiquated undersized panel installed in a location so tight replacement is impossible who need enemies.

Installing a panel 13 short years ago that cannot accept tandem breaker is some very poor judgment for a master.

20 slots is barely enough for a kitchen today no less the full house more poor judgment for a master in my opinion.

Installing a panel in a way that makes it impossible to replace equals more poor judgment for a master.

Is there a bed or exterior door within 15 feet of this closet?

Where is the master now?

Walta
 
OP
M

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,010
Location
Coastal Maine
mmmm....the closet in question is going to contain all the cat6 stuff I am adding to the house as it makes the most sense, so the coats and shoes are actually going to go into the addition space.The panels both in the garage and house have been more than adequate until adding 2 circuits for heat pumps and adding the surge breaker.Those panels were sold by our local electrical wholesaler at the time.Homeline tandem breakers were available in 2009. I don't know why we didn't buy different panels.Sq D made these exact panels until Jan 23,2021....why if they are so antiquated?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,722
Location
Richmond, VA
Hold on. Your friend didn't future proof the install? How dare he! Complete hack scumbag.

I am am sure there was no budget that he was keeping to, either. He just wanted to screw you and he won.

At least rehashing the past is helpful.
 
To avoid these ads, REGISTER NOW!
OP
M

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,010
Location
Coastal Maine
20 spaces just for the kitchen :scared: As I think back Sq D had a deal going and I got 2 panels and a bunch of breakers as a value pak for like $50. My friend is now retired and is one of the most honest and nice guys you could ever meet. Until the heat pumps everything has been just fine.
 

mark-NJ

Well-known member
Joined
Apr 1, 2019
Messages
773
Location
new jersey
I'll toss this in just for grins: Closet or not, why would anyone use a Homeline panel in their house (likely their largest investment) when a QO panel is only a few bucks more?

QO: 22K AIC vs. 10K on a Homeline
QO: silver-plated copper bus, vs. aluminum on a Homeline

It's your house, I suppose. As my friend likes to say, "Got a $20 brain? Buy a $20 helmet..."
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,722
Location
Richmond, VA
I'll toss this in just for grins: Closet or not, why would anyone use a Homeline panel in their house (likely their largest investment) when a QO panel is only a few bucks more?

QO: 22K AIC vs. 10K on a Homeline
QO: silver-plated copper bus, vs. aluminum on a Homeline

It's your house, I suppose. As my friend likes to say, "Got a $20 brain? Buy a $20 helmet..."
You are implying that homeline is bad, which is incorrect. You can always spend more money on a project.

This is also crixizing decisions made 20 years ago...super productive
 

mark-NJ

Well-known member
Joined
Apr 1, 2019
Messages
773
Location
new jersey
I'm implying no such thing. I'm simply stating that, as a comparison, Sq.D (Schneider) offers a far superior product for not a lot more. In my opinion, the Homeline serves one purpose only: cheapening a BOM's total cost. Again, my opinion: is the electrical infrastructure of one's house the place to make shortcuts?
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,722
Location
Richmond, VA
I'm implying no such thing. I'm simply stating that, as a comparison, Sq.D (Schneider) offers a far superior product for not a lot more. In my opinion, the Homeline serves one purpose only: cheapening a BOM's total cost. Again, my opinion: is the electrical infrastructure of one's house the place to make shortcuts?
What problems have been encountered with homeline? Sure, in theory, qo is better. But what is the practical impact?

House fires? Higher power bills? Earlier failures?

Legitimately curious. I have never bought Homeline, but have two 200a panels in my house without issue for almost 20 years
 

mark-NJ

Well-known member
Joined
Apr 1, 2019
Messages
773
Location
new jersey
Aluminum. It simply doesn't play nicely with other conductor materials without special treatments. Snapping on a (dissimilar metal) QO breaker isn't, in my view, a great idea when an alternative exists.

And I have, indeed, removed QO breakers from Homeline panels and seen signs of electrolysis.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,765
I'm implying no such thing. I'm simply stating that, as a comparison, Sq.D (Schneider) offers a far superior product for not a lot more. In my opinion, the Homeline serves one purpose only: cheapening a BOM's total cost. Again, my opinion: is the electrical infrastructure of one's house the place to make shortcuts?
Not really impressed with Homeline but ANYTHING is better then Eaton BR, even GE, if you see a BR panel, you have a **** electrical job in front of you, besides the difference between QO & HOM breakers, Homeline panels have a aluminum bus, until Eaton cheapened up the CH panels they were my preferred panel, now either Eaton CH, SQ D QO, or Siemens copper bussed panels. But back to Homeline, they were introduced to be more competitive in the residential market which is why they are only single phase, no 3 phase, and no QO all in ones, meter mains anymore, Eaton, & Siemens, responded by introducing UL classified breakers for QO panels.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,765
Aluminum. It simply doesn't play nicely with other conductor materials without special treatments. Snapping on a (dissimilar metal) QO breaker isn't, in my view, a great idea when an alternative exists.

And I have, indeed, removed QO breakers from Homeline panels and seen signs of electrolysis.
That I would like to see, QO breakers are 3/4" wide, Homeline is 1" wide and they clip to the bus quite differently.
 

mark-NJ

Well-known member
Joined
Apr 1, 2019
Messages
773
Location
new jersey
^^^

Correct. I was trying to type while cooking dinner, and....woops. "QO" came out of my brain & down to my fingers.

That said, I have seen such corrosion when Homeline breakers (with clips that are a dissimilar metal) are removed from Homeline panels. I've seen it with my own eyes..
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,722
Location
Richmond, VA
^^^

Correct. I was trying to type while cooking dinner, and....woops. "QO" came out of my brain & down to my fingers.

That said, I have seen such corrosion when Homeline breakers (with clips that are a dissimilar metal) are removed from Homeline panels. I've seen it with my own eyes..
I haven't pulled every breaker ,but I have moved a bunch and they all look clean to me. I guess anything is possible. Thankfully we can all spend out money how we want. I'll gladly take a donation for an upgrade, though
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,722
Location
Richmond, VA
Sure you are. "why would anyone use a Homeline panel in their house" is pretty clear. You keep dancing around and changing what you are saying. "I was busy cooking..." What a bunch of bs. Homeline is a decent panel. It's not top of the line, I'll give you that.
It's just back pedaling.

Sorry for the sidetrack, @Mr onetwo
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,981
Location
Central Iowa
I've yet to see a failure on a Homeline panel other than a bad main out of the box. The bus in a Homeline is aluminum, but it has the same tin coating (not silver) as a QO. I put a 200 amp Homeline in my own house. Sure, a QO or copper Siemens would have been better, but it was the summer of the 'Rona and some things were next to impossible to find. When it's all said and done, I'm not going to lose a bit of sleep over it.
 

grounded-b

Well-known member
Joined
Oct 23, 2012
Messages
285
Location
Milwaukee, WI
Code requires 30" Left, Right, and in front of the panel!
No, the NEC requires a 30" wide clear space in front of the panel. It does not have to be centered on the panel, a 16" wide panel could have it's working space in front of it and 14" to the right ( or left ). The working space in front of a panel is 36" for up to 150V to ground conditions. NEC 110.26(A)(1) and (2)
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,722
Location
Richmond, VA
No, the NEC requires a 30" wide clear space in front of the panel. It does not have to be centered on the panel, a 16" wide panel could have it's working space in front of it and 14" to the right ( or left ). The working space in front of a panel is 36" for up to 150V to ground conditions. NEC 110.26(A)(1) and (2)
I wonder how many times a post needs to be refuted/corrected
 
OP
M

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,010
Location
Coastal Maine
If I abandon the old panel in the closet and install a new panel on the other side of the wall and connect the 2 boxes with conduit, could I move the power wires with breakers to the new location and leave the grounds and neutrals in the old can? They would be connected with full size conductors. Essentially using the old panel as a junction box. This would move the panel to a much better location. I would like to avoid moving the grounds and neutrals if it is permitted.
 

Attachments

  • Capture.JPG
    Capture.JPG
    42 KB · Views: 10

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,722
Location
Richmond, VA
If I abandon the old panel in the closet and install a new panel on the other side of the wall and connect the 2 boxes with conduit, could I move the power wires with breakers to the new location and leave the grounds and neutrals in the old can? They would be connected with full size conductors. Essentially using the old panel as a junction box. This would move the panel to a much better location. I would like to avoid moving the grounds and neutrals if it is permitted.
How can you move all of the branch circuit hots but not the neutrals and grounds?

If it was my house, I would definitely not want it split like that, regardless of what code allowed
 
OP
M

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,010
Location
Coastal Maine
I would have to extend them all...just hoping to avoid doing the same with all the neutrals and grounds.They are really packed together, but I can extend them also if I must.
 