    240 V electrical

    I had no issue running my 10-3 and 12-2 romex in the 3/4 conduit. It was only a 5.5' length and straight. If there were any bends, I'm sure that would make things far more difficult. The lift instructions say to use a thermal disconnect if required by local code. I did search a bit to see if...
  2. M

    240 V electrical

    Yea, I'm the only one using the lift. I ain't gonna worry about it. Got it all hooked up and tested today. Works fine!
  3. M

    240 V electrical

    I did post a photo of the motor name plate in my previous post. It clearly says 'not thermally protected'. I found these, but would have to use 2 of them to protect both legs. https://www.amazon.com/Circuit-Breaker-125-250V-Overload-Protector/dp/B0DHVG1BFD/?tag=atomicindus08-20
  4. M

    240 V electrical

    I haven't been able to find a single one rated for 30 amps with 4 terminals. I wonder if I could use a 2 terminal on each leg?
  5. M

    240 V electrical

    Thanks, guys. I think I'm going to run my 10-3 and 12-2 romex through the same 3/4 (straight conduit) to the power disconnect switch box. I have plenty of (sub) panel space, so running a separate 12-2 line to a 20 amp breaker in the panel seems easiest to me. I'll just cap off the white wire...
  6. M

    240 V electrical

    I was thinking you could buy BX armor and run your own wires in it (like conduit). It doesn't appears it sells like that. I guess I could use conduit. It's a straight shot from ceiling to post. Just saw your post, Stuart. Thanks, that would be easier.
  7. M

    240 V electrical

    The walls and ceiling will be insulated, so I plan to run the 10-3 romex to a box directly above the power unit post (the motor/fluid reservoir mounts on the post). Then I'm thinking BX type armored cable from ceiling box to emergency disconnect switch. I know you shouldn't run romex inside...
  8. M

    240 V electrical

    Yes, single phase. I will forego the outlet. A short extension cord will do.
  9. M

    240 V electrical

    I have to provide the power disconnect switch. I did buy a double pole, 30 amp rated switch for that. Here's a related question; since I'm running 10-3 anyway and will have a power disconnect switch mounted on the lift column, is there any reason I can't/shouldn't put a GFI outlet in that same...
  10. M

    240 V electrical

    I'll get a photo of the motor tomorrow, but here's the wiring diagram in manual. I expect the motor will show 208-230 VAC. I guess I've always been wiring dryers and ovens, etc. and not motors. I guess I spent a little more on copper than I needed to. Thanks, guys.
  11. M

    240 V electrical

    I'm getting ready to start wiring install for my new lift. It needs 240 V / 25 amp and I've got my 10-3 romex and 25 amp double breaker. However, I just discovered that the hydraulic pump motor has only a black, white and bare (ground) wires. Does this mean it does not require a neutral wire...
  12. M

    How do I insulate an existing, finished garage?

    Unless you have a pretty steeply pitched roof, and/or large rafters (2 x 12, etc.), drilling holes in the wall header may be pretty difficult, especially if the ceiling is already in place. Access will be a real pain. I'd much rather drill holes in wall and deal with a little drywall patching.
  13. M

    Source for metal ceiling panels?

    I've had some delays in the schedule and haven't purchased yet.
  14. M

    New Bay Window: U-factor not met, Inspector says need new glass, will argon maybe meet new code?

    Agreed. I believe there are situations where stealth remodeling is worth the risk.
  15. M

    New Bay Window: U-factor not met, Inspector says need new glass, will argon maybe meet new code?

    I understand, if it is made to order, even if to some standard dimensions, it's still considered a 'custom' order. They're not simply stacked up in a warehouse waiting for a buyer. So far as the inserts, it would seems he needs to verify that his local building department will accept the...
  16. M

    New Bay Window: U-factor not met, Inspector says need new glass, will argon maybe meet new code?

    When you say it was a custom order, was it actually built to fit dimensions you specified or was it something they didn't have in stock and had to order it from a warehouse somewhere? If the latter case, I would expect HD to allow a return. If it truly is a special order per your dimensions...
  17. M

    Do I need a temp supporting wall?

    New OHD and windows installed. Things went pretty smoothly.
  18. M

    Source for metal ceiling panels?

    I do have a trailer. If price is good, it might be worth the drive.
  19. M

    Source for metal ceiling panels?

    Thanks, guys. I was searching on 'metal ceiling panels'. I'll try the alternates. I'm between Danbury and Norwalk and will check with a local lumber yard (Rings End). I'm not sure who does metal buildings / pole barns in this area. I think 22/24 gage is a little heavier than for my needs.
  20. M

    Source for metal ceiling panels?

    Hey guys, those of you who have used metal panels for garage ceiling, where did you buy them? I'm not having much luck finding basic interior panels in CT/Tri-State area. Did you buy them locally or have them shipped? I did search this site and didn't find too many leads.
Top Bottom