  1. W

    In use outlet covers that don't let wasps in?

    have you tried the expandable in use cover? https://www.homedepot.com/p/Commercial-Electric-1-Gang-Expandable-Extra-Duty-Horizontal-Vertical-Non-Metallic-Weatherproof-In-Use-Cover-24-in-1-Configurations-Gray-WCWR1PG/304669863
  2. W

    In use outlet covers that don't let wasps in?

    if your area was not on 2002 code when the house was built, then it is code complaint to not have them.
  3. W

    Discrete device generator lockout/disconnect.

    take pics of the panel and post them here dragging extension cords around is not only a pain, but it is against code to run them thru doors and windows and they create trip hazards. PIB and an interlock along with color coding of breakers would be the best route for multi-day outages what is...
  4. W

    What the heck is this thing?

    sprinkler timer, doorbell or BA/IA power supply
  5. W

    Always a 'fun' day when you get to put on the extra layers

    ok so what does this machine do or what is it for?
  6. W

    Square D special breaker?

    the breaker style is "cable-in cable-out" that whole can needs to be redone. new breakers, new terminals bar, new neutral bar replace the NM-b and put duct seal on the conduits after you replace the lock rings the sewer gases are corroding everything
  7. W

    Plug wired to compressor

    shop. 3Ø 208Y/120 panel
  8. W

    Plug wired to compressor

    Ive got red tape on the floor in front of my panel because my techs kept stacking ladders in front of the panel
  9. W

    Plug wired to compressor

    that is for 3Ø not 1Ø
  10. W

    Plug wired to compressor

    for a 4-wire 120/240v plug yes. but you dont need that for a 240v motor. 6-50p would be the correct one
  11. W

    Plug wired to compressor

    the issue comes from unplugging them while running. say you have an emergency and need to shut the motor off right away and dont have time to run to the breaker panel. pulling that plug can expose you to a nasty arc flash.... also the 10-50p is non-grounded 120/240v rated so of course its the...
  12. W

    Plug wired to compressor

    as said above, the issue is the plug and recept ratings..... if you can find a plug and recept rated for the HP of the motor, then you are good to go.... they do exist up to certain ratings, but they are expensive... cheaper to hardwire especially for equipment you dont need to move on a regular...
  13. W

    Utilities easement?

    wow what a mess definitely tell sparky to stop and wait til the plans are figured out
  14. W

    Wiring a 100amp outlet/connection- typical practice?

    that in-rush rating is awfully low my 3-ton AC condenser pulls almost 100a on startup and its not even 5hp
  15. W

    Plug wired to compressor

    30a breaker will probably hold but could also nuissance rip since it will be hardwired, breaker can be max 2.5x of FLC, 70a for 5HP
  16. W

    Plug wired to compressor

    I have serious doubts about that. most handymen would do a better job than that. I hope you didnt pay much for that mess.
  17. W

    Wiring a 100amp outlet/connection- typical practice?

    yeah those numbers are from the NEC FLC chart in 430.248.... they are NOT full load amp ratings which would come from the motor nameplate.... they are max ratings for motors with those HP ratings and it is what you size your wire off of.... and standard NEMA size motors stop at 10hp 1Ø.... farm...
  18. W

    Plug wired to compressor

    it can be but i wouldnt use it for a whip to a compressor. use stranded THWN instead
  19. W

    Wiring a 100amp outlet/connection- typical practice?

    where did you come up with 88a? the NEC FLC chart for single phase doesnt go past 10HP, which is 50a regardless, the in-rush current would be 4-8x and a residential service would not support that kind of load starting on the line. most PoCos also have HP limits for residential services and...