2 hots and 1 neutral?

tipsy

Well-known member
Joined
Jul 16, 2014
Messages
337
Location
Speedwell, Tennessee
Existing 220 circuit for an a/c unit in the breezeway. Want to take out the 220 breaker and replace with two 20 amp breakers and then replace the 220 receptacle with a 110 outlet. Split it by removing the hot tab but my question is can I use the one neutral for both sides?


Sent from my iPhone using Garage Journal
 
To avoid these ads, REGISTER NOW!

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
Just leave the breaker as is. In fact it's a Code requirement.
Just wire the receptacle, break out the tab on the hot side, and you're good to go.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
Hold up.

Does this existing circuit have 3 or 4-wires?

Assuming 3 since its a 240v circuit, then you cant do what you want as you have no neutral.

A 240v circuit does not have a neutral. It has 2 hots and a ground wire/EGC.

For a MWBC/multi-wire branch circuit, you need 2 hots, neutral AND ground.
 

alfredeneuman

Well-known member
Joined
Mar 3, 2011
Messages
4,580
Location
Fullerton, CA
The NEC doesn't see it that way:
Branch Circuit, Multiwire. A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system.

The grounding wire isn't even mentioned, but of course it should be there.
They must have figured that was a given
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
The NEC doesn't see it that way:
Branch Circuit, Multiwire. A branch circuit that consists of two or more ungrounded conductors that have a voltage between them, and a grounded conductor that has equal voltage between it and each ungrounded conductor of the circuit and that is connected to the neutral or grounded conductor of the system.

The grounding wire isn't even mentioned, but of course it should be there.
They must have figured that was a given

Sure and how many people interchange neutral and ground?

This circuit feeding the A/C unit could have a bare wire for the EGC and he is just calling it a neutral. That obviously cant be used as a neutral.

In these types of situations with little info and the knowledge of the OP being unknown, best to ask questions.
 
OP
T

tipsy

Well-known member
Joined
Jul 16, 2014
Messages
337
Location
Speedwell, Tennessee
Ok all good input. I’ll be looking at this setup this week and will report back for further info.


Sent from my iPhone using Garage Journal
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
Why do you need 2 circuits to that one outlet? Trace one of the black hots and wrap it white, call it your neutral and make the existing white (if it is) a green and use that as your EGC. Then you have a spare breaker for a circuit for somewhere else (assuming you can pull wire to where you'd like).
 

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
^ My thought as well.

Also....can OP install a 15A receptacle on the end of a dedicated 20A circuit? Even a 15A/20A 'dual rated outlet' might not be code, since it is a single outlet. (and not a string of receptacles).

Not that Id be overly worried, but from a code perspective....
 

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
^ My thought as well.

Also....can OP install a 15A receptacle on the end of a dedicated 20A circuit? Even a 15A/20A 'dual rated outlet' might not be code, since it is a single outlet. (and not a string of receptacles).

Not that Id be overly worried, but from a code perspective....
Not if it's the only outlet on the circuit,unless something has changed.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,716
Location
NW Iowa
There is a lot of assumptions in this thread...

We need to know how many insulated wires are at this 240V outlet.

I would guess this has a 2 wire w/ground NM, again assuming.

^ My thought as well.

Also....can OP install a 15A receptacle on the end of a dedicated 20A circuit? Even a 15A/20A 'dual rated outlet' might not be code, since it is a single outlet. (and not a string of receptacles).

Not that Id be overly worried, but from a code perspective....

A 20A single outlet would be fine at the end of a 20A circuit. Not sure why you think it wouldn't?

Also one 15A duplex receptacle is actually (2) receptacles and is also fine as the only thing on a 20A circuit.

The only thing not allowed would be (1) 15A single receptacle. Any other receptacle or combination is fine.
 

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
There is a lot of assumptions in this thread...

Agree

A 20A single outlet would be fine at the end of a 20A circuit. Not sure why you think it wouldn't?

Sure would. never said it wasnt. A 15 wouldnt.

Also one 15A duplex receptacle is actually (2) receptacles and is also fine as the only thing on a 20A circuit.

OP is talking about dividing a duplex into two singles, correct? Or are you responding to something else?

The only thing not allowed would be (1) 15A single receptacle. Any other receptacle or combination is fine.

So a duplex with a 15/20A dual amperage plug config but divided into two circuits is...OK?
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,716
Location
NW Iowa
OP is talking about dividing a duplex into two singles, correct? Or are you responding to something else?
Just a general reminder. Many people think of a duplex as one outlet when it is really two.


So a duplex with a 15/20A dual amperage plug config but divided into two circuits is...OK?

I guess I'm not following you 100%. All 20a receptacles will also accept 15a plugs. It's still a 20 rated receptacle.
 

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
The OP was here yesterday, and could have cleared the whole "assumptions" thing up once and for all....but didn't.

He said he was going to take another look at the wiring "this week" and will give an update. :dunno: It's extremely possible and likely he doesn't remember the colors of all of the wires at the outlet, and also extremely likely he doesn't have time to check it out immediately. Just chill out until he gets a chance to have another look.
 
To avoid these ads, REGISTER NOW!
OP
T

tipsy

Well-known member
Joined
Jul 16, 2014
Messages
337
Location
Speedwell, Tennessee
Sorry guys. Had the flu for several days too.
Anyway, I have not seen this yet. My customer described it to me. I will see it sometime this week.
I need two “dedicated 20 amp circuits” for a treadmill and some other piece of sports equipment like a stepper or bike or something. I don’t remember exactly what.
Anyway, I’ll get back to you when I know more.
Thanks


Sent from my iPhone using Garage Journal
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
I don't think your supposed to re-identify 12 ga. wires.

Where'd you hear that? It's been done with switch legs for ages. Maybe re-identifying a conductor to an EGC but I think you could strip that back to where it entered the box and make sure that everyone understands what that wire does.

IDK, experts?
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
Where'd you hear that? It's been done with switch legs for ages. Maybe re-identifying a conductor to an EGC but I think you could strip that back to where it entered the box and make sure that everyone understands what that wire does.

IDK, experts?

If it’s part of a cable assembly then in most cases it can be re identified but individual conductors cannot.
 

PWC Repair

Well-known member
Joined
Dec 27, 2012
Messages
3,173
Location
Arkansas
Well, i can tell you for a fact with 2 hots and a true ground as out in my well house, you can not get 110 volts no matter where you try to hook up. MUST have a neutral for 110v.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,716
Location
NW Iowa
I have heard this before. It assumes there is a license requirement in whatever jurisdiction he is in. I never had one as I never worked where one was required.

Ok maybe I should ask if the OP is competent in electrical work? Asking for what seems like simple advise on a diy forum makes me wonder.

Asking about a license was the wrong question.
I know a few people with no electrical license who can do good work. I also know a few guy who do have a license but aren't competent at anything other than bending pipe.
 

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
Ok maybe I should ask if the OP is competent in electrical work? Asking for what seems like simple advise on a diy forum makes me wonder.

Asking about a license was the wrong question.
I know a few people with no electrical license who can do good work. I also know a few guy who do have a license but aren't competent at anything other than bending pipe.
:beer::beer::beer::beer::spit:
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
Ok maybe I should ask if the OP is competent in electrical work? Asking for what seems like simple advise on a diy forum makes me wonder.

Asking about a license was the wrong question.
I know a few people with no electrical license who can do good work. I also know a few guy who do have a license but aren't competent at anything other than bending pipe.

yeah a license doesnt mean sh*t.

i used to work for a licensed C10 electrical contractor who didnt know the difference between neutral and ground/EGC and why "both were ran because they both go to the same bar." :headscrat :wtf: :wtf: :shocking:

*facepalm*

had to educate him... smh :spit:
 
Last edited:

Jim greengo

Well-known member
Joined
Sep 3, 2018
Messages
7,415
Location
Behind my house
yeah a license doesnt mean sh*t.

i used to work for a licensed C10 electrical contractor who didnt know the difference between neutral and ground/EGC and why "both were ran because they both go to the same bar."

*facepalm*

had to educate him... smh
I met a city electrical inspector in Carter lake Iowa around 20 years ago that didnt know what a gfi was,hes been gone a while fortunately.
Yes,they're out there among us.:spit:
 
OP
T

tipsy

Well-known member
Joined
Jul 16, 2014
Messages
337
Location
Speedwell, Tennessee
I thought this was a simple question, maybe not. Can two hots from two separate circuits, share a neutral wire? Or does each hot require its own neutral wire back to the panel?


Sent from my iPhone using Garage Journal
 
OP
T

tipsy

Well-known member
Joined
Jul 16, 2014
Messages
337
Location
Speedwell, Tennessee
So I’ve been to the house and seen the situation. 10-3 w/o ground is in use. Just wondering as I mentioned above. Can each of those hots share the one neutral. Each hot would be on its own dedicated circuit breaker.


Sent from my iPhone using Garage Journal
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
19,998
Location
Modesto, CA
I thought this was a simple question, maybe not. Can two hots from two separate circuits, share a neutral wire? Or does each hot require its own neutral wire back to the panel?


Sent from my iPhone using Garage Journal

yes they can as long as the 2 hots are from opposite phases. this is to prevent overloading of the neutral.

You will need to use handle tied breakers.

however, read below....

So I’ve been to the house and seen the situation. 10-3 w/o ground is in use. Just wondering as I mentioned above. Can each of those hots share the one neutral. Each hot would be on its own dedicated circuit breaker.


Sent from my iPhone using Garage Journal

since you do not have a 4th wire for ground, this wire/circuit is not usable for what you want to do. You cannot put a grounded outlet on a non grounded circuit.

And since this is for grounded equipment(assuming), it most definitely should be on a grounded circuit.

The only saving grace would be if the wire is ran in conduit which is doubtful since its old NM cable....
 

nsula_country

Well-known member
Joined
May 23, 2013
Messages
1,534
Location
Northwestern Louisiana
But... Can't a GFCI be used in this situation? Well, 2 GFCI's.

Can GFCI's use a shared neutral?

Can you MWBC w/o a ground/EGC if each phase has a GFCI?

My understanding is that if existing wiring is L-N (2 blade receptacle) that a GFCI can be used to add ground fault capability. Though, not to downstream receptacles...

I may be WAY off base. Majority of my experience is all Industrial electrical...

CT
 