2 pole breakers

Roostzilla

Member
Joined
Jun 7, 2022
Messages
16
I'm trying to add 220 for a neighbor who just got an electric Mustang (pretty cool car!) It's a mobile home supply pedestal with 4 bus tabs from I guess 2 phases, there's a 2 pole 50 in the middle, so when I move it over to add a 2 pole 30 for the car I lose 220. My question is would it be better to add another bus bar, if I can, and ill need to call an electrician, or get a quad 2pole 30 2 pole 50? Added twist...can't have rejection clips! I've been trying to find one with zero luck. Thanks.
 
To avoid these ads, REGISTER NOW!

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
18,002
another bus bar? man this is a bad idea to be messing with.

also i believe you need a GFCI for outdoor ev outlets like you're doing.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
Its not 2 phases. Its single phase and you cant add a bus bar.

If its a 2 space 4-circuit panel you would need a quad 30-50 breaker to do what you want.
 
Last edited:
OP
R

Roostzilla

Member
Joined
Jun 7, 2022
Messages
16
Its not 2 phases. Its single phase and you cant add a bus bar.

If its a 2 space 4-circuit panel you would need a quad 30-50 breaker to do what you want.
I'm trying to add 220 for a neighbor who just got an electric Mustang (pretty cool car!) It's a mobile home supply pedestal with 4 bus tabs from I guess 2 phases, there's a 2 pole 50 in the middle, so when I move it over to add a 2 pole 30 for the car I lose 220. My question is would it be better to add another bus bar, if I can, and ill need to call an electrician, or get a quad 2pole 30 2 pole 50? Added twist...can't have rejection clips! I've been trying to find one with zero luck. Thanks.
Thanks guys for being so helpful, I thought this might be the place to go for answers. I made it clear that I don't know terminology and that if necessary I'd call an electrician, but I'm perfectly capable on changing a breaker! Geez, tough crowd. I've worked in remodeling for years, and moved to a mobile home park working under an electrical engineer. He died and now it's me....so if someone has something to say that is productive then I would appreciate it. Thanks to the guy who at least tried to help, but , again, I thought it was pretty clear that I an looking for a quad 2 pole 30 2 pole 50 with NO rejection clips. I'll send a picture and maybe someone can tell me the proper thing to ask. Thanks.
 

mark-NJ

Well-known member
Joined
Apr 1, 2019
Messages
775
Location
new jersey
moved to a mobile home park working under an electrical engineer. He died and now it's me....so if someone has something to say that is productive then I would appreciate it.

I thought I was productive in my previous post, but now that you've provided this info, I'm CERTAIN that I provided productive info. Here it is again: The liability is enormous...why bring that on yourself?
 
OP
R

Roostzilla

Member
Joined
Jun 7, 2022
Messages
16
As you can see, there's room for more in there, so I thought that might be an option....for an electrician!
 

Attachments

  • 20220504_163541.jpg
    20220504_163541.jpg
    186.3 KB · Views: 72

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
The quad is probably not gonna work in that panel as my guess is its a 4 space 4 circuit max panel.

What brand of panel is that? Can you take a picture of the overall outside of the panel?

It would’ve been good to put these pics in the OP

What’s with the PVC pipe inside the panel?
 
Last edited:
OP
R

Roostzilla

Member
Joined
Jun 7, 2022
Messages
16
I thought I was productive in my previous post, but now that you've provided this info, I'm CERTAIN that I provided productive info. Here it is again: The liability is enormous...why bring that on yourself?
Mark, not sure if you saw the picture as your responded as I was sending it, but I'm asking 2 questions....can you answer either of them? Can something be added, or where can I get that breaker?
 
OP
R

Roostzilla

Member
Joined
Jun 7, 2022
Messages
16
The quad is not gonna work in that panel.

What brand of panel is that? Can you take a picture of the overall outside of the panel?

It would’ve been good to put these pics in the OP

What’s with the PVC pipe inside the panel?
Well now we're gettin somewhere, thanks. My fault for not sending pictures first, I just found this site and got all excited. I'll go take some and post them.
 

Skooterj

Well-known member
Joined
Mar 11, 2021
Messages
759
Location
Indiana
The quad is not gonna work in that panel.

What brand of panel is that? Can you take a picture of the overall outside of the panel?

It would’ve been good to put these pics in the OP

What’s with the PVC pipe inside the panel?
Maybe I'm missing something, why wouldn't a Quad work if you kept it in the middle?
 

Skooterj

Well-known member
Joined
Mar 11, 2021
Messages
759
Location
Indiana
Whats the max # of circuits that panel can have as listed on the panel label? Im guessing its 4.
I can't make out any of the writing in the panel. But you are probably right. Personally, I would want to replace the panel anyway, something with at least 8 slots. But it may be fine for a mobile home, and if allowed by the panel, the 30/50 quad would solve the EV charger issue.
 
To avoid these ads, REGISTER NOW!
OP
R

Roostzilla

Member
Joined
Jun 7, 2022
Messages
16
Wrong picture is what that is, again, sorry. Just figuring this site, here is what I have
 
OP
R

Roostzilla

Member
Joined
Jun 7, 2022
Messages
16
The 2 breakers are a 2 pole 30, home depot. And the 30 50 the guy got from lowes. The 30 50 has the rejection clips
 

Attachments

  • 20220608_104059.jpg
    20220608_104059.jpg
    128.7 KB · Views: 57
  • 20220608_104242.jpg
    20220608_104242.jpg
    150.9 KB · Views: 45
  • 20220608_104251.jpg
    20220608_104251.jpg
    170.1 KB · Views: 46
OP
R

Roostzilla

Member
Joined
Jun 7, 2022
Messages
16
The 2 breakers are a 2 pole 30, home depot. And the 30 50 the guy got from lowes. The 30 50 has the rejection
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,250
Location
Modesto, CA
ok so it says 6 max handles since its a main. so i was wrong about 4 circuits max. you will need to find a non-ctl breaker in siemens QP or QT, cutler hammer QP, BO, BR or GE TQ, THQ. or THQL
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
If you look very closely only one 2 pole breaker in the center will provide 240V with provisions for a single pole on each side of the 2 pole.
 
OP
R

Roostzilla

Member
Joined
Jun 7, 2022
Messages
16
If you look very closely only one 2 pole breaker in the center will provide 240V with provisions for a single pole on each side of the 2 pole.
Yeah, I got the 2 pole 30 and moved the 50 over, no 220, realized my mistake and just trying to get this guys car charging. Here's a better picture of the panel, got the name in there this time.
 

Attachments

  • 20220608_110342.jpg
    20220608_110342.jpg
    110.9 KB · Views: 44

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
Yeah, I got the 2 pole 30 and moved the 50 over, no 220, realized my mistake and just trying to get this guys car charging. Here's a better picture of the panel, got the name in there this time.
220 volts is a line to neutral voltage & not used in North America. Milbank got in the mobile home pedestal business after buying Unicorn some years back.
 
OP
R

Roostzilla

Member
Joined
Jun 7, 2022
Messages
16
This is a little better. So Norcal, is there any way to get what I need? Gotta tell you, I'm in SoCal and been to supply warehouses and nothing.
 

Attachments

  • 20220608_114011.jpg
    20220608_114011.jpg
    169.6 KB · Views: 47

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,792
This is a little better. So Norcal, is there any way to get what I need? Gotta tell you, I'm in SoCal and been to supply warehouses and nothing.
What Wyliesdiesels suggested, a quad breaker is about the simplest way to do it.
 