There is three.
dont you need 4? what code cycle are you under? Is the house attached to the garage? Or are there 2 seperate buildings? What size conduit is that? What exactly are you doing? Are you setting a new service, then using this cable to refeed the existing panel from the new service?

I was told that I don't need four. The new service will be at the garage and the house will be the sub. the braker box is going to be a 200 amp. feed through combo it has the meter slot and lugs to feed the house. The old meter will be removed and I will use 2" conduit where the old weather head is now. As for what code cycle I'm under![]()
Is there a problem with three wires?
1. Is the garage attached?
2. Specifically, what kind of wire did you pull? It looks like 4/0 4/0 2/0 URD(Sweetbriar)
3. Is it in conduit the whole way?
4/0 4/0 2/0 Sweetbriar1. Is the garage attached?
2. Specifically, what kind of wire did you pull? It looks like 4/0 4/0 2/0 URD(Sweetbriar)
3. Is it in conduit the whole way?
4. Have you called the power co. and made sure they'll accept your new service location?
5. Have you called the building department for a permit yet?
FYI, all the ground rods in the world dont mean everything's bonded properly. The purpose of the grounding conductor is to provide a path for fault current. Ground rods dont accomplish this.
I know it comes to a surprise to most of you but the OP is correct.
In Texas, the homeowner can do all his own work. Most jurisdictions there is NO permitting and NO inspections. Only in the last year has Texas adopted any building codes. It looks like 2003 IBC is currently being used.
I don't believe you can run URD in a house?
the state of Texas adopted the 2008 NEC effective Sept 1, 2008 for all unincorporated areas, if you are within municipal limits you have to check with them.
I REALLY think you cant use URD inside, it is not a recognized wire type and is made for underground service entrances.
I also think you need the ground wire.
It used to be you could run 3 wire to a detached structure, but now you need 4 wire. Doesnt matter for the OP because the garage is attached to the house.
When I tried to get a permit and they said I didn't need it, I put on file a plot plan of what I was doing and the date was 10/13/07 so maybe I'm grandfathered.
Are you saying that I need the wire or are you reconnending.
to elaborate on the URD issue, you cant use it inside because the insulation doesnt meet any of the flame travel standards. NOW, look carefully at your cable. Some URD has a dual rating, it will say RHW or XHW or something like that on it. If it does then youre ok.
mrb I did not notice anything harsh And I like to do thing right.
If I remember I was told that the cable having it's own breaker in the new box that it's ok to run it in the attic
As for the cable there is no problem with it running in the attic (in or out of conduit.) so I'm leaving it the way it is.
All things said, bottom line, you can do what you like, it's your house.Just figured you might like to hear an electricians perspective on it.
I hear what you'r saying. I had two different electrician come out who had the biggest ads in the yollow book. And they both were going to do it this way. I used their material list to order from. And it's in conduit just not at the ends
2 different licensed electricians were going to use 3 wire URD inside a home for a subpanel?
2 different licensed electricians were going to use 3 wire URD inside a home for a subpanel?
2 different licensed electricians were going to use 3 wire URD inside a home for a subpanel?