There are no short answers to this complex topic. Recognize that the utility distribution system relies on a multi-grounded neutral. At the pole top transformers, ground rods are connected to the system neutral, and the primary and secondary neutrals are connected together.Nothing in the shop is GFCI equipped,
All of this is bringing up a question in my head, not to start another discussion or definitely not an argument but....
The power pole with the transformer on it has a copper plate on the base and a copper wire running up to the transformer which is the ground, from the triansformer triplex runs from the transformer to the meter, two hots and a neutral.
That meter in the main panel is then grounded similarly with about a 6 ft ground rod pounded into the ground. That is in fact how my entire house is grounded, built in 95 for what it's worth.
So now not to stir up controversy, just for my knowledge what is the difference between running two hots and a neutral from the main panel to a sub panel on the shop, via a circuit breaker, which also has a 6-ft ground rod pounded into the ground.
Obviously not an electrician and I don't want to be one!
It is nice to not go a day without learning something though.
A GFCI has nothing to do with EGCs or grounding electrodes.... A GFCI doesnt even need an EGC to functionNothing in the shop is GFCI equipped,
EGCs and grounding electrodes are different animals. both are required for subpanels in detached buildings however that requirement came with the 2008 code cycle UNLESS there are parallel metallic pathways between buildings (electrical conduit, gas line, water line, phone line, etc). then it was required even before 2008.The power pole with the transformer on it has a copper plate on the base and a copper wire running up to the transformer which is the ground, from the transformer triplex runs from the transformer to the meter, two hots and a neutral.
That meter in the main panel is then grounded similarly with about a 6 ft ground rod pounded into the ground. That is in fact how my entire house is grounded, built in 95 for what it's worth.
So now not to stir up controversy, just for my knowledge what is the difference between running two hots and a neutral from the main panel to a sub panel on the shop, via a circuit breaker, which also has a 6-ft ground rod pounded into the ground.
Obviously not an electrician and I don't want to be one!
It is nice to not go a day without learning something though.
just an FYI- a neutral is just called a grounded conductor not a GEC. a GEC is a grounding electrode conductor- ie. the wire that connects the electrodes to the GES- grounding electrode system....There are no short answers to this complex topic. Recognize that the utility distribution system relies on a multi-grounded neutral. At the pole top transformers, ground rods are connected to the system neutral, and the primary and secondary neutrals are connected together.
Neutral conductors carry normal load current----- a full time job. The neutral is called the GEC - grounded electrical conductor.
Under normal operation, the neutral conductor can have a voltage drop across it and this gives rise to neutral to earth voltages.
Grounding conductors carry fault current --- during fault conditions. This is the EGC - equipment grounding conductor.
Under normal conditions there is no current in the EGC.
Under fault conditions, this provides a current path for the OCP - overcurrent protection ---- typically a breaker ---- to operate.
The current code would require your shop subpanel be connected to the main panel with a neutral conductor -GEC- and a grounding conductor -EGC. And those two remain separated or isolated. So when your neutral conductor carries load current -- and a voltage drop across it -- that small voltage WILL NOT appear on the metal junctions boxes many of us have in our shops. Those boxes are connected to the EGC all the way back to the main panel.
The ground rods serve to equalize the local voltage of the utility distribution system with the voltage at the earth. What does that mean? Well the earth is not a perfect conductor. When there is a voltage drop across a neutral and it is connected to the ground rod at the main panel, the soil around the rod will have a small voltage present. This is called NEV or neutral to earth voltage. That voltage will dissipate as you move away from the ground rod. This limits the step potential that could cause a shock.
Consider this... when all this stuff is connected properly and working correctly.....
You can have a few volts dropped across the neutral due to normal load, and still stand barefoot while touching the hose bib on the side of your house and not get a shock or tingle. Of course there are many other safety conditions this properly connected system protects us from, this is only one example.
I'll edit. I missed a gear. Thanksjust an FYI- a neutral is just called a grounded conductor not a GEC. a GEC is a grounding electrode conductor- ie. the wire that connects the electrodes to the GES- grounding electrode system....
The ground is the same gauge in 12/2 and 14/2 cables. In large cables, service cables etc. it is smaller than the current carrying conductors.Well this is all very interesting and very immersive.
So since the neutral is a normal current carrying conductor and the ground is merely a fault carrying conductor, does the ground have to be the same AWG as the hots and the neutral?
In the buried wire it was but if I remember correctly my hot tub which is 6-3 with ground, I believe the ground was a considerably smaller AWG.
its a little complicated but if the ungrounded conductors (hots) are larger than #10, then the answer is no and anyone telling you otherwise doesnt know what theyre talking about. see NEC table 250.122Well this is all very interesting and very immersive.
So since the neutral is a normal current carrying conductor and the ground is merely a fault carrying conductor, does the ground have to be the same AWG as the hots and the neutral?
who told you that the EGC/ground wire needed to be the same size as the ungrounded conductors?In the buried wire it was but if I remember correctly my hot tub which is 6-3 with ground, I believe the ground was a considerably smaller AWG.
who told you that the EGC/ground wire needed to be the same size as the ungrounded conductors?
post a pic of the direct buried wire. Im guessing you have quadplex URD which is meant for 3 phase service entrance and thus all 4 conductors (3 hots & neutral) are the same size. IF thats the case then you have the wrong wire entirely. a manufactured cable like mobile home feeder has reduced size EGC per code and you can even get it with a reduced size neutral as well...No one but I do know that the buried wire I have all four wires were the same AWG, but not so for the wiring going to my hot tub.
Hmmm. Listen to Wylie, he knows this stuff.Okay that's what I thought, so if I run #2 ariel from the house to the shop,
which I already have someone who has about 130 ft ready for me to pick up Monday,
it does not however, have a ground, it's merely service wire so what size ground wire would I need to add to that to be within code and correct.
Alternatively, could I use one of the buried conductors as a ground, which is #2, or should the ground actually be smaller AWG?
Of course doing that there's always the chance that some varmint will kill my ground one day!
EGCs and grounding electrodes are different animals. both are required for subpanels in detached buildings however that requirement came with the 2008 code cycle UNLESS there are parallel metallic pathways between buildings (electrical conduit, gas line, water line, phone line, etc). then it was required even before 2008.
I’m no sparkie.So does this mean that I can use the existing ground that is in ground and run three wires overhead for two hots and a neutral, and be acceptable?
no because code requires them to be all together unless youre running a ground wire for an existing circuit.So does this mean that I can use the existing ground that is in ground and run three wires overhead for two hots and a neutral, and be acceptable?
no because code requires them to be all together unless youre running a ground wire for an existing circuit.
No. You need a quadplex overhead wire. Two hots, neutral, and the bare messenger wire, which will be the ground. I haven't used any in a loooong time, but if I remember correctly the three insulated wires were black and I had to do a continuity test to identify one wire as the neutral.So does this mean that I can use the existing ground that is in ground and run three wires overhead for two hots and a neutral, and be acceptable?
You need a #6 ground, but you're not going to find anything that you can just add on to the overhead run if that's what you are trying to find out. The messenger ground wire will be a #2 if you use #2. You could probably get by with #4 since it's free air.Okay that's what I thought you were going to say I guess I was trying to read between the lines. So what would be the AWG size required if I'm running #2 wire?
Just trench and do it right with conduit.
@billrigsby how long is the proposed aerial run? How long is current run?
Is that overall distance or point to point?Both are / would be about 125 ft
Is that overall distance or point to point?
Free Air (as applied to conductors). Open or ventilated environment that allows for air flow around an installed conductor with no other conductors closer than one cable diameter and no insulation or building materials in contact with the conductor insulation for more than 75 mm (3 in.) for every 3 m (10 ft) of conductor.You could probably get by with #4 since it's free air.
Makes me want to run a 2 conductor aerial across my backyard with some coating the squirrels will find tasty. I could watch those fireworks all dayand I remember watching the squirrels chew the insulating jackets off the overhead wires at my late parent's house. The rodents would chew and chew and chew, until they went thru two jackets in the same place, then **** and the utility company would come out to replace the wires again.
and I remember watching the squirrels chew the insulating jackets off the overhead wires at my late parent's house.