258v on a 240v outlet

Status
Not open for further replies.

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
Yes, OK, now I get it - post #1, he said it was 258 V - 263 V at the load, but 243 V at the breaker. Both measurements would have had to be done at the 600 V range.

I guess this is where I get out my oscilloscope and actually look at the waveform shape, as well as ask it to do an AC RMS measurement.
Nothing to do with True RMS…
 
To avoid these ads, REGISTER NOW!

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,609
Location
Long Island
Nothing to do with True RMS…
It sure can have something to do with true RMS. A non-true RMS digital meter will measure the peak-to-peak voltage and divide by radical 2/2 (around .707) to give you the readout. That works perfectly for a clean sine wave, but reads high when there's harmonic distortion. Some distortion patterns may not deviate much, while others can deviate quite a bit from the true RMS value.
 

MovingAlong

Well-known member
Joined
Aug 17, 2013
Messages
1,223
Swapped the wires around and still getting high reading at wires.
Battery was replaced as well.

I see some of y’all have questioned the accuracy of this device. I’ll see if my neighbor has one and compare the readings.

Your post is based on the premise that you're seeing a voltage increase at the end of the wire.. now that you've configured your DVM differently, both measurements should be redone. Is panel voltage still less than wire voltage?
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,016
Location
Modesto, CA
Swapped the wires around and still getting high reading at wires.
Battery was replaced as well.

I see some of y’all have questioned the accuracy of this device. I’ll see if my neighbor has one and compare the readings.
Do you have this circuit connected to a load at all? Is this in conduit with other circuits?
 

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
It sure can have something to do with true RMS. A non-true RMS digital meter will measure the peak-to-peak voltage and divide by radical 2/2 (around .707) to give you the readout. That works perfectly for a clean sine wave, but reads high when there's harmonic distortion. Some distortion patterns may not deviate much, while others can deviate quite a bit from the true RMS value.
what is RMS?
and my math is really bad.

what is LoZ ?
 

johnre

Well-known member
Joined
Dec 1, 2016
Messages
1,051
Location
Portland, OR
Nothing to do with True RMS…
Since I mentioned both a DMM and an oscilloscope in my post, I'm not sure which one you are referring to with this statement.
  • If you're talking about an oscilloscope, then the scope's AC RMS measurement will be true RMS, provided you've sampled at a reasonable density (easy for a 60 Hz sinusoid).
  • If you're talking about a DMM, then refer to @Ritman's post #42 about a non-true-RMS (or standard) DMM.
Note that a true RMS DMM behaves somewhat like an oscilloscope without a display; it oversamples the waveform, figures out the period, then calculates the RMS voltage from the sample values over one period. For me, if it really matters that much that I need to know for sure, I'd rather have the scope.

what is RMS?
Root mean square.

Odd that you first make a bold statement about RMS, then you proceed to ask us what it means.
 

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
Since I mentioned both a DMM and an oscilloscope in my post, I'm not sure which one you are referring to with this statement.
  • If you're talking about an oscilloscope, then the scope's AC RMS measurement will be true RMS, provided you've sampled at a reasonable density (easy for a 60 Hz sinusoid).
  • If you're talking about a DMM, then refer to @Ritman's post #42 about a non-true-RMS (or standard) DMM.
Note that a true RMS DMM behaves somewhat like an oscilloscope without a display; it oversamples the waveform, figures out the period, then calculates the RMS voltage from the sample values over one period. For me, if it really matters that much that I need to know for sure, I'd rather have the scope.


Root mean square.

Odd that you first make a bold statement about RMS, then you proceed to ask us what it means.
So what is root mean square of an ac power wave form ?

What is LoZ?
 

Gozo

Well-known member
Joined
Oct 10, 2013
Messages
250
Location
Central VA
Since the OP hasn’t been back in a while, I’ll toss a real easy test he can do when (if) he checks this thread.
Turn off the breakers then measure the voltage at the long end. If it’s anything other than 0, it’s stray induced voltage. Won’t hurt a thing; the smallest load will swamp it out. Move on with life.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,609
Location
Long Island
what is RMS?
and my math is really bad...
Ok, so you want me to explain something that requires calculus, without calculus. Let's see what I can do (which is probably not much, since I'm not a good teacher).

If you're familiar with Ohm's law and Joule's law (V=IR and P=IV), and you've applied them to AC systems, then you've used RMS. An AC waveform is constantly changing voltage, up, down, positive, negative, so what number do you plug into those equations? It isn't the peak to peak (wave amplitude), or the peak above midline. That's where RMS voltage comes in, though RMS can apply to current as well, and RMS voltage and current can be used to calculate thermal power (there is no such thing as RMS power).

Let's start with a hypothetical 50% duty cycle 2V peak to peak square wave. It spends half it's time at +1V and the other half at -1V. The square of 1 is 1. But the square of -1 is ALSO 1. So step 1, "square", this wave is always 1 (i.e. the square step flips any negative half into positive territory, so an RMS value is always a positive number).

Now the "mean". In this case, we now have a flat line at 1, which averages out to 1, so the mean is just 1. Now we take the square root of 1, and get 1. So a 2V peak to peak square wave has an RMS voltage of 1.

620px-Waveforms.svg.png

Moving onto a triangle wave, also 2V peak to peak. Here, the square still gets us an all positive wave that peaks at 1V, but now we have peaks, rather than a straight line. The mean here is the average voltage over the cycle. Without math, picture a wave made out of play-doh. It's a nice shape until a gigantic sky foot comes down and squashes it. Well, that level is the mean, and that foot unfortunately just did calculus. So I guess my explanation needs to end there.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,268
Location
Coastal NJ
RMS can be thought of as the heating value.

Apply 10V DC to a resistor. Measure its temperature. Let’s say it heats up to 100 degrees.

Now substitute your wackiest noisiest AC waveform to power the resistor. If it goes up to exactly 100 degrees then your waveform was 10V RMS.

Some waveforms are very complex and there is no equation available to calculate the RMS value.

Others are quite simple and have a direct calculation available.
 

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
Ok, so you want me to explain something that requires calculus, without calculus. Let's see what I can do (which is probably not much, since I'm not a good teacher).

If you're familiar with Ohm's law and Joule's law (V=IR and P=IV), and you've applied them to AC systems, then you've used RMS. An AC waveform is constantly changing voltage, up, down, positive, negative, so what number do you plug into those equations? It isn't the peak to peak (wave amplitude), or the peak above midline. That's where RMS voltage comes in, though RMS can apply to current as well, and RMS voltage and current can be used to calculate thermal power (there is no such thing as RMS power).

Let's start with a hypothetical 50% duty cycle 2V peak to peak square wave. It spends half it's time at +1V and the other half at -1V. The square of 1 is 1. But the square of -1 is ALSO 1. So step 1, "square", this wave is always 1 (i.e. the square step flips any negative half into positive territory, so an RMS value is always a positive number).

Now the "mean". In this case, we now have a flat line at 1, which averages out to 1, so the mean is just 1. Now we take the square root of 1, and get 1. So a 2V peak to peak square wave has an RMS voltage of 1.

620px-Waveforms.svg.png

Moving onto a triangle wave, also 2V peak to peak. Here, the square still gets us an all positive wave that peaks at 1V, but now we have peaks, rather than a straight line. The mean here is the average voltage over the cycle. Without math, picture a wave made out of play-doh. It's a nice shape until a gigantic sky foot comes down and squashes it. Well, that level is the mean, and that foot unfortunately just did calculus. So I guess my explanation needs to end there.
Free energy for all ? The op have this problem that he probe voltage at breaker is different from voltage probed (higher) at the end of a 70’ electrical run ? So rms is the answer?
 
To avoid these ads, REGISTER NOW!

Metal-Marc

Well-known member
Joined
Aug 31, 2009
Messages
7,177
Location
Foothills of the Adirondacks
Free energy for all ? The op have this problem that he probe voltage at breaker is different from voltage probed (higher) at the end of a 70’ electrical run ? So rms is the answer?

Nah, OP is using a crappy meter that is most likely out of wack on top of being crappy and everyone is out there running crazy trying to solve the problem by using differential equations. or something.
 

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
Nah, OP is using a crappy meter that is most likely out of wack on top of being crappy and everyone is out there running crazy trying to solve the problem by using differential equations. or something.

It’s been point out multiple times. Op have a crappy meter, but as long as he took the measurements correctly on the same setting and time frame, the voltage differential should not increase and should only be decrease under normal circumstances at the end of a 70’ run. Vs doesn’t change right ? Why would Vpp be higher at the end of a 70’ run and not at closer to the Vs? Right ? Breaker is Vs. let’s say it’s a crappy meter but still a meter that behave the same for point a and point b measurements right.

Pretty sure this is the wire condition when op took the measurements, doesn’t look like there is a load on the end of those wires, doesn’t looks like it’s in any flex conduit or it is pulled into a conduit yet. (Maybe, dunno for sure) but this pic. From his other thread says, it ain’t looking liking it.

Other thread


1719336956841.jpeg
 
Last edited:

SlappyWhite

Well-known member
Joined
Oct 3, 2012
Messages
1,819
Location
Upper Canada
O

Ok math solutions then what does it mean
Is this a serious question or trolling?

Assuming it was serious it is the equivalent AC voltage (based on power) compared to a DC voltage. For example 240 VAC (RMS) will dissipate the same amount of power for a fixed resistance value as 240 VDC. RMS is more or less a given (it is redundant and not noted) when someone says 120v, 240v, etc. it is RMS. The formula is how it is calculated.

What we call 240 VAC is the actually the RMS value (as per above) and it is around 340 v peak. When we say 120 VAC is will be around 170 v peak. We don't generally use peak and if we do, peak will specifically be noted. All this is the very, very, very basics of alternating current electricity.
 

SlappyWhite

Well-known member
Joined
Oct 3, 2012
Messages
1,819
Location
Upper Canada
Does it sounds like any one explains rms ?
Or how it fits into the op?

Every one throws out acronyms like they are Rapping like that half dollar guy
Perfectly clear what people are saying to most. RMS is not just some acronym, it is the very, very basics of understanding AC.

A cheap or bad meter can get RMS wrong and it is a possible explanation on how the measured voltage increased.
 

Cruzan80

Well-known member
Joined
Jul 22, 2015
Messages
4,216
Location
Denver, CO
Since I mentioned both a DMM and an oscilloscope in my post, I'm not sure which one you are referring to with this statement.
  • If you're talking about an oscilloscope, then the scope's AC RMS measurement will be true RMS, provided you've sampled at a reasonable density (easy for a 60 Hz sinusoid).
  • If you're talking about a DMM, then refer to @Ritman's post #42 about a non-true-RMS (or standard) DMM
But what happens when your oscilloscope comes with a DMM attached? Stole pic off eBay, faster than digging mine out. :evil:
s-l1600-3081445922.jpg






In seriousness, I get where you are going with this.
 

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
Perfectly clear what people are saying to most. RMS is not just some acronym, it is the very, very basics of understanding AC.

A cheap or bad meter can get RMS wrong and it is a possible explanation on how the measured voltage increased.
A bad meter gets rms wrong on the same Voltage source? Should have the same result on point a or point b right not just point b and not point a ? Must be a smart meter.
 

SlappyWhite

Well-known member
Joined
Oct 3, 2012
Messages
1,819
Location
Upper Canada
A bad meter gets rms wrong on the same Voltage source? Should have the same result on point a or point b right not just point b and not point a ? Must be a smart meter.
Multiple posters explained this already. The RMS formula is for a perfect sinusoidal wave aka sinewave. If there is EMI, induction, whatever along the path the output may have distortions and maybe that meter does not deal well with them. A true RMS meter may give better results. But this is just a possible cause for a false reading not an end diagnosis.
 

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
Multiple posters explained this already. The RMS formula is for a perfect sinusoidal wave aka sinewave. If there is EMI, induction, whatever along the path the output may have distortions and maybe that meter does not deal well with them. A true RMS meter may give better results. But this is just a possible cause for a false reading not an end diagnosis.
Emi? Ok. Can’t disagree with that. It would have to be at least 20Vpp higher in order for that meter to get that 258Vrms right according to that these internet formula?
 

cmandp

Well-known member
Joined
Dec 22, 2011
Messages
1,282
Location
New Jersey
Nah, OP is using a crappy meter that is most likely out of wack on top of being crappy and everyone is out there running crazy trying to solve the problem by using differential equations. or something.
No, calculus. Specifically integrals. Differentials equations comes after Calc 3 ;)
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,939
Location
NJ
Does it sounds like any one explains rms ?
Or how it fits into the op?

Every one throws out acronyms like they are Rapping like that half dollar guy
Think of it this way:
In a simple dc circuit, the power flowing is V*I. That's pretty easy to calculate as the voltage and current are constant through a fixed load (resistor).

If you graph (or use an oscope) the voltage and current over time (or use a voltmeter and ammeter), they show constant non-zero values. You can read right off of the graph for each or both meters.

Let's say a 125 vdc battery has a 25 ohm resistor placed across it. Then 5 amps will flow from the battery through the resistor and return to the battery. The voltmeter reads 125 volts, ammeter reads 5a. So P=VI = 125v * 5a = 625 watts.

When a square looped wire is symmetrically rotated within a magnetic field, a symetrical sinusoidal voltage is produced in that wire. (red line in graph.)

Instead of a battery, we now connect a symmetrical sinusoidal voltage output (what the grid provides) to the resistor. The voltage in this case is constanly changing: from 0 to a positive peak, back through zero, continue to a negative peak and then return to zero. Our grid voltage does this 60 time per second.
The average of the area traced out by the sinusoid above 0 and of that below 0 are identical values in magnitude but one is negative and the other 1/2 of the sinusoid is positive.

1719351064344.png

But we know current had to flow through the resistor b/c voltage was placed across it. However the voltage is varying and that makes the current vary.

So what values to use to calculate power??? To make it worse, during the other 1/2 of the sinewave, the voltage is negative and makes the current flow in the opposite direction. The resistor got hot from the current flowing in both directions. It didn't heat up with current flowing in one direction and then cool down when current reversed!! It got hotter.

To make life easier, constant values are easier to communicate, just like in the original dc circuit. 125vac is the rms voltage of a symmetrical ac sinusoid that has a peak value of 177 volts - first positive and then -177 volts negative. (That is "A" on the graph.)

So what does RMS mean? Root, mean, square >> Square root, average, square.

1st) square every value along the trace of the sinsusoid represented at the black dashed lines. (Squaring makes the negative values positive.)
2nd) Add all "N" of these values together. (N is the number of black dashed lines.)
3rd) Divide that total amount by (n+1) to get the average of the sum of all of those values.
4th) Since all of the values were squared, take the square root to "undo" the squaring.

When this is calculated using an integral (calculus) the answer is very precise because the black dashed lines infinitely increase in quantity for higher precision vs. an approximation using only a few dozen lines.

A symmetrical sinusoidal wave with a magnitude of 177volts peak (or 354 volts peak-peak) at 60 cycles per second is 125 vac (rms).
(Which would you rather say?)

So now P in the ac circuit is VI = 125vac (rms) * 5 amps = 625w.

All of this has nothing to do with the OP's question o_O but you asked! :lol:
 
Last edited:

johnre

Well-known member
Joined
Dec 1, 2016
Messages
1,051
Location
Portland, OR
But what happens when your oscilloscope comes with a DMM attached?
Use the DMM for more accurate DC readings, or whenever differential measurements are needed and you lack a differential probe.

Use the scope for everything else.
 

dogdog

Well-known member
Joined
Nov 15, 2011
Messages
12,711
It’s been point out multiple times. Op have a crappy meter, but as long as he took the measurements correctly on the same setting and time frame, the voltage differential should not increase and should only be decrease under normal circumstances at the end of a 70’ run. Vs doesn’t change right ? Why would Vpp be higher at the end of a 70’ run and not at closer to the Vs? Right ? Breaker is Vs. let’s say it’s a crappy meter but still a meter that behave the same for point a and point b measurements right.

Pretty sure this is the wire condition when op took the measurements, doesn’t look like there is a load on the end of those wires, doesn’t looks like it’s in any flex conduit or it is pulled into a conduit yet. (Maybe, dunno for sure) but this pic. From his other thread says, it ain’t looking liking it.

Other thread


1719336956841.jpeg

@Tynee is this the RMS thread you are referring to ? let me know where science failed you.
 