AC Soft Start Kit

To avoid these ads, REGISTER NOW!

fitter30

Well-known member
Joined
Jun 23, 2019
Messages
2,981
Location
Peace Valley,mo
Most (all?) electric motors that have high starting loads have a start capacitor. The cheap soft starters are usually just a very large capacitor which can make the starting current WORSE !

Without getting into the gory details of electrical engineering, when a capacitor is discharged (empty) it "look like" a dead short, trying to "fill up" instantaneously (high current draw).

The MicroAir Easy Start "limits" how fast that start capacitor is charged (maybe from less than 10 msec to over 100 msec) Once full, the capacitor discharges and gets the motor spinning. There is a centrifugal switch that cuts out the capacitor once the motor is up to speed.
Ac compressors are psc motors.
 

gregs

Well-known member
Joined
Mar 16, 2007
Messages
1,602
I haven’t seen the older starter kits referred to as “soft start”, they where usually called “hard start” kits. The “hard” part was because the motor had a hard time starting due to low voltage, age, etc. They typically use a large start capacitor and a potential relay to “release “ the charged capacitor. This was how a lot of older equipment was built from the factory. I guess at some point they figured they could get by without it and removed it. Also not all of these type of motors have a centrifugal switch built in.

These newer “soft starts” seem to use the existing start capacitor and some type of electronics to alter how it’s used. The wiring I saw has you disconnecting the existing capacitor from the ac wiring and it gets connected to the soft start device.

Not sure what else happens in the soft start box, but it seems there would be more than just the start capacitor being regulated.
 

Tinkerer2

Well-known member
Joined
Jun 19, 2020
Messages
345
Location
Central Florida
Most (all?) electric motors that have high starting loads have a start capacitor. The cheap soft starters are usually just a very large capacitor which can make the starting current WORSE !

The MicroAir Easy Start "limits" how fast that start capacitor is charged (maybe from less than 10 msec to over 100 msec) Once full, the capacitor discharges and gets the motor spinning. There is a centrifugal switch that cuts out the capacitor once the motor is up to speed.


By "cheap soft starters" is that the category you put the Rectorseal Kickstart? If it makes the starting current WORSE, and the Easy Start is a gadget that "limits" how fast the start capacitor is charged, isn't the Easy Start start capacitor just as worse?

Rectorseal website says:
Relay drops out start capacitor at optimum time to avoid excessive heat
Avoids potential damage to compressor by never staying in the circuit too long
 

gregs

Well-known member
Joined
Mar 16, 2007
Messages
1,602
“Relay drops out start capacitor at optimum time to avoid excessive heat
Avoids potential damage to compressor by never staying in the circuit too long”

That’s the potential relay that has been around forever and is the key part of a hard start or kick start kit. It’s also a component that used to be in older ac equipment from the factory. My well starter box has one in it, I am guessing for the chance the impeller is stuck with sand or something and needs a kick to get it going. I don’t believe there is anything bad about these kits. But if I was trying to solve a start problem with a generator, I would probably go with one of these electronic soft starters. You have people here that are using them and say the work.
 

like2wheel

Well-known member
Joined
Oct 29, 2014
Messages
1,693
Location
On an as needed basis
Ok, what does it depend on whether I should make the switch to a soft starter?

I can't give you an intelligent answer other than to tell you that I needed to put a hard start kit on my 3 ton a/c unit when I self installed it 25 years ago, and it is still running with that today.
 

American Locomotive

Well-known member
Joined
Jan 8, 2017
Messages
10,977
Location
Rhode Island
Lots of people way all over the place. Let's break down the three systems being talked about very simply:

- "Hard Start" kit: These are a big start capacitor with a special relay you attach to your AC compressor. These actually increase starting current. But they make the compressor start faster. They are useful if you have low voltage/voltage sag problems or your system short cycles. Sometimes they can help get your system started on a marginal generator by getting the compressor at a high enough speed before your generator bogs down too much.

- "Soft Starter": These are basically giant automatic dimmer switches. When you turn the AC on, they start out on "dim" and quickly ramp up to full power in a controlled way. It softly starts the motor, reducing peak current. Will often reduce light dimming/flicker during start, and may help get a system running on a generator. These are NOT anything like an inverter - they're basically dimmer switches in how they work.

- "Inverter": Also known as a VFD (variable frequency drive). These actually directly control the speed of the compressor. You will not find commercial "kits" to convert your system to inverter. AC systems have to be designed with them integrated from the beginning to work properly.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,206
Location
SE MI
- "Inverter": Also known as a VFD (variable frequency drive). These actually directly control the speed of the compressor. You will not find commercial "kits" to convert your system to inverter. AC systems have to be designed with them integrated from the beginning to work properly.
Some inverters used on refrigeration compressors actually "create" a 3 phase output. The voltages are not the same as you would find in a commercial building, but it is 3 unique phases going to 3 unique windings in the motor.

3 phase motors are much more efficient compared to single phase so it makes up for the power lost by the inverter.
 

Tinkerer2

Well-known member
Joined
Jun 19, 2020
Messages
345
Location
Central Florida
Got the Micro-Air EasyStart installed today. Very easy install. I don't have inrush amp readings because I don't have a meter that can do that.

However, the electrical data specs for my AC unit is 75 LRA and 16.8 RLA. According to the Micro-Air app, my starting amps are down to 23.2 and running amps are 8.3. The unit starts a lot quieter too. In fact, you have to be fairly close to hear the compressor kick on with the fan running.

I'm going to test the generator tomorrow or Tuesday.
 

BSWS

Well-known member
Joined
Jun 2, 2019
Messages
360
Location
Tucson AZ
These newer “soft starts” seem to use the existing start capacitor and some type of electronics to alter how it’s used. The wiring I saw has you disconnecting the existing capacitor from the ac wiring and it gets connected to the soft start device.

Not sure what else happens in the soft start box, but it seems there would be more than just the start capacitor being regulated.
The AC on my RV didn't have a start capacitor, only a run capacitor. The Easy Start instruction did mention that if I had a start capacitor, to remove it. So my understanding is that it is replacing, not regulating the capacitor.

Whatever it does, it works great on my AC.
 
To avoid these ads, REGISTER NOW!

Tinkerer2

Well-known member
Joined
Jun 19, 2020
Messages
345
Location
Central Florida
Tested it with the generator this morning. Worked perfectly. Generator sound didn't change at all during the AC startup. Glad I made the switch from the hard start.
 

kinggsxr

Well-known member
Joined
Jan 20, 2015
Messages
46
Location
Northern VA
This might be off topic but would something like this help prevent my GFCI breaker from tripping when using a miter saw?
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,778
Location
Austin, TX
Could the non-start issue be the continuous load current rating of 87.5 with the 75 used for the AC along with whatever is being used in the house at the time?
Could be. Test it. Shut down all the other breakers in the home. Turn off the AC. Turn off the main and trigger the generator. Turn on the AC. See what happens.

I have a 20KW geneset, it'll run a 2 ton, 3 ton, and 1.5 ton AC all at the same time (not start them all at the same time). One of our ACs is on a "delay" to make sure that they don't start up at once.

I've also got a monitor in the main panel so I can see what my home pulls in terms of total power. It's never gone above about 15KW.

So if the Micro-Start will reduce the starting amps required, would it be better for the AC compressor than the kickstart unit? I'd rather this AC unit last a long time and not be damaged by having the wrong extra starting component installed.
I dunno which is better, but we use "soft start" capacitors in the RV arena all the time. I've got a 15K BTU unit with a soft start that I run on a 2500 watt generator.
 

vavet

Well-known member
Joined
Mar 6, 2012
Messages
5,325
Location
Ashland, VA
I installed the Micro-aire unit on my residential heat pump yesterday. I forgot to borrow my clamp meter from work to get the initial inrush current, but the micro-aire app showed it was initially about 52 amps. It worked its way down to about 30 amps, and then I saw another 46 amp startup. It started cooling off outside after that so I'm not sure what the subsequent starts were.
This was all done on utility power, but the intent is to help it start more easily on generator power when we have power outages. As it is, the lights dim, the wi-fi usually has to reset, and sometimes the TV turns off...yes, I know. First world problems.
Installation didn't take long, but it does take some interpretation of the instructions because every system is a little different. Mine has a control board with some monitoring functions and two LEDs that illuminate or blink to indicate a certain pattern/meaning, but it's not the emerson control board that gets it's own set of instructions.
 

Kezorm

Well-known member
Joined
Aug 18, 2021
Messages
174
Location
Twin Cities, MN
Just installed the micro-air easy start on my 5 ton ground source heat pump. What a difference! Starting current went from >150A peak down to just over 40A. Prior to easy start, the inrush was so high that you could actually hear the wires jump inside the EMT conduit and lights would flicker just a bit.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,206
Location
SE MI
Just installed the micro-air easy start on my 5 ton ground source heat pump. What a difference! Starting current went from >150A peak down to just over 40A. Prior to easy start, the inrush was so high that you could actually hear the wires jump inside the EMT conduit and lights would flicker just a bit.
Any noticeable delay in starting ?
 

Kezorm

Well-known member
Joined
Aug 18, 2021
Messages
174
Location
Twin Cities, MN
No delay. The compressor starts up smoothly and quickly. Far smoother than the jarring start from before. Generally, A/C compressors and heat pumps don’t start under any load. This is what allows method like easy start to work. It wouldn’t work with something like an air compressor that needs to start under load.

* as default, easy start has a ~5 second startup delay by design to let the fan start first, but this is by design. It doesn’t apply power at all to the compressor motor for those 5 seconds. Once power is applied to the compressor, there’s no delay / slow start at all. Just smoothly starts running vs. jarring instant dump of full voltage / high inrush current. This 5 second delay can be disabled if necessary (some compressors have diagnostic electronics that expect the compressor to start immediately)
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,048
No delay. The compressor starts up smoothly and quickly. Far smoother than the jarring start from before. Generally, A/C compressors and heat pumps don’t start under any load. This is what allows method like easy start to work. It wouldn’t work with something like an air compressor that needs to start under load.

* as default, easy start has a ~5 second startup delay by design to let the fan start first, but this is by design. It doesn’t apply power at all to the compressor motor for those 5 seconds. Once power is applied to the compressor, there’s no delay / slow start at all. Just smoothly starts running vs. jarring instant dump of full voltage / high inrush current. This 5 second delay can be disabled if necessary (some compressors have diagnostic electronics that expect the compressor to start immediately)
virtually all air compressors start "unloaded" btw. most can't start under load, necessitating an unloader. it goes "PSSSSSSSH" when it stops on the small ones.
 

dcg9381

Well-known member
Joined
Jun 20, 2018
Messages
11,778
Location
Austin, TX
Would you please elaborate on the monitor in the main panel? Brand, etc? What type of data does it give you?
See below. I bought this largely to be able to monitor overall power. I JUST use it as a monitor on the mains (it can measure solar back-feed). But it's also capable of monitoring downstream circuits inductively if you add additional pickups. Peak power use, daily power use, hourly use, various warnings if we're setting new power records, etc.


1698083608491.png
 

PoorUB

Well-known member
Joined
Mar 29, 2021
Messages
11,655
Location
Fargo, ND
virtually all air compressors start "unloaded" btw. most can't start under load, necessitating an unloader. it goes "PSSSSSSSH" when it stops on the small ones.
The unloaded compressor head and discharge line gets filled in a revolution or two, long before the motor gets up to speed so to some degree an air compressor starts under a load.
 

u3b3rg33k

Well-known member
Joined
Dec 18, 2017
Messages
4,048
The unloaded compressor head and discharge line gets filled in a revolution or two, long before the motor gets up to speed so to some degree an air compressor starts under a load.
in air compressor parlance, "loaded start" would imply tank pressure at the 2nd stage discharge valves. dirty unloaders can cause loaded starts. the compressor at my shop was doing them for years before I got there and fixed it. it's a QR-25 5120, 25hp, 3ø, DOL starter. 4 belts.

most VFD piston pumps I've seen cannot perform a "loaded start" if the cut in is set high. the ones I've seen try will make it once there's any inertia in the system. (i.e. if the compressor stopped with the piston just past TDC, it'll start, and if it stopped BDC, it won't make the first compression stroke.) but if the motor is programmed for rated torque, it won't overcome the no inertia stall condition.
once you've made the first revolution, it's not an issue anymore.
 

Beezfun

New member
Joined
Apr 29, 2012
Messages
1
I installed an easy start on my 23 year old 3T A/C system about a year ago. Inrush went from 115A to 23A. Here's a technical interview with the engineer who designed the easy start. Our lights used to dim when the AC came on, and it sounded like a 12ga shotgun. Now I can't even hear the thing come on when I'm standing by it until the fan gets up to speed.

When I installed my 24kW Generac about 10 years ago, I installed one of their smart modules on my A/C. The generator communicates with the module and disconnects the A/C power when the generator first starts up, and can disconnect it if the load from the rest of the house becomes too great. I installed the easy start because we had a few lengthy power outages that summer and it made me cringe when the A/C started on generator power.
 