Adding circuits to an already full panel - what are my options?
stickshift
northeastern US
Update: If you've been following along, just skip ahead to post #81 for updates.
OP:
I'm looking to add several circuits - 3 x 120V 20A lines and 1 x 220V 20A line. Is that possible with this panel - seems there is some free space underneath the existing breakers. Meaning, can I either extend the main line feed strips that the breakers connect to (not sure if they make extension kits), or can I replace the existing breakers with slimmer breakers? The existing breakers are ~1" tall (the bottom ones are connected together, and some of the others are split into 2 separate circuits).
Or is the better option to set up a sub-panel, and move one of the existing circuits over (to free up a slot to feed the sub-panel), and add all the new circuits to the sub?
PCustoms
VT
You could free up 1 breaker, max.
That panel is full. I'd do a replacement. You could do a sub, but probably just as easy to replace the whole thing wit a modern, larger panel.
How is this fed?
Attached or detached building?
Bert_
NW Iowa
First I would find and slap the guy who put in that 12 space service panel. Unfortunately this type of thing was sort of common at one point.
Best thing to do is is replace the whole thing with at least a 20 space panel, 30 would be better.
I would also take a look at that service cable. It looks like it should be replaced. Especially if any part of it runs outside.
mm08822
This panel is ripe for an upgrade. Even if you keep it at 100a service, you could still upgrade to a panel with more branch circuit space.
You can probably add a quad breaker also free up 2 more spaces, but then you are 100% maxed out.
Provide a readable pic of the panel label - cb's, accessories, ratings, etc.
What is the load on the 2 pole 40a cb? It looks like #12 (possibly #10) wired to it?
alfredeneuman
Fullerton, CA
What's with the 15A breakers on the bottom left side ganged together with a copper wire?
If 240 it should have a 2 pole like the 40 directly across from it.
sreeb
SoCal
Replace the 220v, 40 with a quad 220v, 40a,20a. Replace the copper ganged 220v, 15a with a quad 220v,15a 2x120v, 15a.
ez-duzit
Marina del Rey
Replace the panel with one that uses the same style breakers. That way you can reuse all the existing breakers.
Stuff
Best to replace the panel. Not enough free spaces in the neutral bar even if you add a separate ground bar.
Adding a sub-panel can work, just not as clean. It is a lot easier for DIY as don't have to involve power company.
You are probably OK but technically should do a load calc to see if 100 amp is still a large enough service with the additional loads.
stickshift
northeastern US
How is this fed?
Standalone house, wire coming from power line on pole outside.
From the 1960s.
What does upgrading to a larger amperage circuit entail? Power co. or my electrician runs a new line from the transformer up on the pole?
Those are BRs and are garbage. No point in reusing them to save a few bucks.
Is there a disconnect after your meter?
From the 1960s.
PoCos disconnects power, new line ran in riser pipe down to meter and then new line ran from meter pan or disconnect into main panel.
Bert_
NW Iowa
You would need to replace the service cable that connects to your main breaker (looks like in needs replaced anyway), the meter box and the wire going up the side of the house. The overhead wire is the utility company's responsibility, they probably won't even change it unless you are adding serious load.
Looks like wylie is a faster typer the me.
James-W
Southeastern Wisconsin
From the 1960s.
To upgrade the service panel with a new larger one, you need to kill power to the house so that all the wiring can be removed from the old panel and the new panel installed. Check with the AHJ and see if you can do the work yourself, or if you have to have a licensed electrician do it. Different jurisdictions have different rules so be sure to check into it before you do anything.
You will need a permit (at least around here you do) and you will need to have it inspected when you are finished. To kill power to the house usually the meter is pulled, but if you upgrade to a 200 amp service you will most likely need to replace the wires from the meter base to the main service panel so having the power shut off at the pole would make more sense. Depending on what gauge the wires are from the pole to the meter, they may also need to be replaced, but the power company will replace them so that isn't something you need to worry about. You will need to replace the wires from the meter up to the mast head, but the connections to the main power line will be done by the power company.
mm08822
From the 1960s.
100 to 200a upgrade for o/h service in my neck of the woods requires replacement of the weatherhead, se cable, meterpan, and into new main panel. Add 2 grd rods and bonding to water and gas lines.
Some POCO's will provide a meterpan, others let you purchase it.
Always best to call POCO first and let them perform a "meter survey" to confirm if existing meter location is acceptable for new service. Usually it is fine where it currently is.
Occasionally they want a load calc to determine if they need to upgrade more of their equipment than just replacing the o/h drop from the pole to the house. Make the call and inquire. It won't cost you anything.
If most of your hardware is from 60/70's, the exterior components are due for replacement.
Lot's of people go with 200a upgrade whether needed or not, b/c it is an eventual selling point. If you have gas appliances and heater, you probably dont need 200a.
A 100a service panel is easily found up to 30 spaces. A 200a service panel can easily be found with 40 spaces.
I would not re-use ~50 year old cb's in a service upgrade.
stickshift
northeastern US
Agreed. If replacing everything else, the CBs are the least of the expenses.
Between the meter and the main breaker on the panel? I don't think so.
Wouldn't pulling the meter out disconnect power downstream of the meter? Otherwise we could all get free electricity.
stickshift
northeastern US
Seems the consensus is replace the panel (and upgrade to 200A service - though I doubt we'd ever trip 100A). Why not add a sub-panel? Seems like that would be easier - something I could do myself.
ez-duzit
Marina del Rey
Since you're just going to ignore the advice you asked for anyway, sure, go ahead and just add a sub-panel. You can do any of it yourself, including replacement.
stickshift
northeastern US
Post some pics of the outside hardware.
Not much to see - just a pipe running down from the power line connection high up, near the roof, down to the meter, and then another pipe running down from the meter and turning into the house. Definitely no disconnect downstream of the meter. And I can't remove the meter; can't even have an electrician remove it, I think only the power co is authorized to do that.
Pic of service line running into the panel below.
stickshift
northeastern US
The easiest DIY solution is to add a subpanel provided the 100A is enough supply for your added circuit loads.
That's what I was thinking. I think 100A will be sufficient because the simultaneous loads are never high.
That said, if I were going to replace the main panel, I would certainly consider upgrading to 200A since the marginal expense is probably not large, and as was pointed out earlier, it's a selling point because most prospective homebuyers would probably look at a 100A service and factor in the cost of upgrading to 200A.
I know this is GJ and moar power is always preferred, but seems to me that replacing the main panel would be quite a bit more expensive than adding a sub-panel. That said, I don't know all the pros/cons, so I'm definitely open-minded on the route to take here.
Stuff
If you see an electric car in your future then an upgraded panel is the way to go.
mike93lx
Richmond, VA
If you have gas appliances and no intention to get an electric car, just keep it at 100a, although if you are replacing everything, the incremental cost is not significant.
Around me, swapping everything for new 100a would be about 1500-2000. Upgrading to 200a would be 200-500 more
stickshift
northeastern US
Yep, on gas for stove, boiler, water heater.
Yeah, if I go the new panel route, I'd opt to bump it up to 200A - not much more expensive and probably increases value of house by at least as much as the cost differential.
So the real question is new panel or sub-panel.
Bert_
NW Iowa
If the outside stuff is decent you can just replace the panel. I would seriously consider replacing the service cable that is connected to the main breaker since it looks kind of ratty.
The reason most people, myself included, say replace it all is that when it looks like your first picture everything is usually shot.
It would be different if you had a more modern 20sp 100a panel that happened to be full. The panel you have was the bottom of the barrel when it was put in. If you're going to to add a few circuits this is the time to update it.
mike93lx
Richmond, VA
Why are you still asking that? The advice is clear, new panel
stickshift
northeastern US
Because the cost differential between sub-panel and new main panel is huge (the small cost differential I was referring to above is new 100A main panel vs new 200A main panel, where I agree that IF going with new panel, might as well go whole hog and make it 200A).
Sub-panel I can do myself. Main panel I have to hire an electrician. How much does a new sub-panel and sufficiently large gauge wires run? Probably on the order of a $100. New 200A panel? I'm guessing NY prices are in the same general vicinity as what you have in MA. So I'm looking at ~$100 vs ~$2000. In some cases, it's definitely worth the more expensive option. But is that the case here? That's what I'm trying to get a handle on.
Yes, the advice was get a new main panel. I'm just not clear on the rationale, given that I have gas appliances and don't expect to run 100A loads. Is my current main panel a fire hazard? If it's to increase home value, sure, I agree that it would. But there's lots of things I can do to increase home value that I'm not planning on doing anytime soon.
mike93lx
Richmond, VA
Do what you want.
Your panel is past its useful life and should be replaced. Like many other maintenance items around the house
Stuff
OP's panel looks more like late 1970s. What is the useful life of an electrical panel? I haven't seen anything definitive.
Did find UL study: https://web.archive.org/web/2012022....org/assets/files/pdf/research/resareport.pdf
Residential overcurrent devices, which consisted mostly of fuses before the
1950s and circuit breakers after the 1950s, continue to perform as expected,
unless they have been subjected to abuse or misuse. If properly installed and
maintained, these overcurrent devices continue to provide protection to the wires
and cables installed on the residential circuits.
mm08822
Pics still needed as requested.
What is conduit size?
How does conduit transition to se cable?
Who is the Poco?
You know for a fact or you are quessing about meter removal? It varies by poco.
James-W
It sounds to me like you are going with the sub-panel because it would be less expensive, so I suggest going ahead and doing it. Just keep in mind that the cheapest way is usually not the best way.
75gmck25
Alexandria, VA
Most folks on GJ like to plan for future upgrades, and they also like new stuff that looks good and is installed neatly. That's probably why you get so many recommendations for a new main panel. However, adding a subpanel would also work fine.
In your price comparison you are mixing apples and oranges (more or less). If you can install a subpanel for $100, then you can install a 100 amp main panel for about $200-250 (mainly because you need more breakers). The cost to upgrade to 200 amp service and replace a panel is probably $2000, but you can install a new panel without upgrading service.
One possibility: If you install a 200 amp main panel (or lower amperage) and but use a 100 amp main breaker, you will have a new panel that is code compliant and be ready for a future 200 amp heavy up. If you want to spend more money later, do the heavy up then and put the 200 amp main breaker back in the panel.
Bruce
mike93lx
Richmond, VA
IMO, past its useful life doesn't mean it is going to fail imminently or that it doesn't function.
It is old enough that it is reasonable to expect breakers to fail, corrosion to take over, it can't be expanded/upgraded, etc.
Just because it flows electricity doesn't mean it's fine. Sure it may not be top priority for replacement, but I would be planning for it.
BigGarage
Just south of Detroit, MI.
My main panel is very old and uses the Pushamatic breakers. It was an upgrade at the time it was installed. It only has 20 spaces and I wanted more.
I had already mounted a 60 amp sub-panel and had the wiring ran to the 1st floor and had the wiring going into the main panel. I added a 60 amp breaker and was all set to go when my boiler went bad in January. After having a new one installed I needed to have it inspected by a electrical and also a mechanical inspector. I took down the subpanel and all the attendant wiring and stored it away out of sight. I knew that my work had to be inspected and I did not know if I needed a permit for it.
I have since decided to get the main panel upgraded so it's bigger and new. For me it's simply not worth the work to remount everything I had done when I can have newer & bigger for probably $2000 or less.
You'll need to make your own choice but I'd recommend a new panel. When I get mine done, hopefully in the next two weeks, I'll post the cost here and take a few pics.
Dennis
Stuff
What is old enough to expect failures? No one will give an answer in years, let alone justify it with evidence.
If old enough what about swapping out all the breakers for new (if availalble)?