Hey guys, coming back to this as I got sidetracked on other stuff.
Performed a rough calc - pic attached below. Instead of the minimum 2 small appliance circuits, I used 4. Ballparked the fixed appliance and central air loads.
Oven, dryer, and central heat are all nat gas. No electric vehicles.
So the total load works to ~16k VA and ~66 amps. Assuming my ballpark figures are not way off, I think it's safe to say that 100A service is plenty sufficient for current needs. I'm glad I went through this load calc exercise, so thanks for that suggestion.
As for nice-to-have uses, a 120V compressor would bump up the total load to ~19k VA and ~80A. A 220V welder would put us way over 100A, but arguably even that could probably be managed within a 100A service because it's a rare-use item, so we could schedule it for times when no other large loads are in use (e.g., no AC, compressor, microwave, or dishwasher).
I'm not too worried about potential future needs beyond this because we're not going to be here in 10 years; maybe not even 5 years.
All I know for sure is that our current use hasn't tripped the main breaker.
I found a NEC standard electrical load calc form for single family dwelling.Op, do a load calc. Odds are 100A is fine for your house.
Performed a rough calc - pic attached below. Instead of the minimum 2 small appliance circuits, I used 4. Ballparked the fixed appliance and central air loads.
Oven, dryer, and central heat are all nat gas. No electric vehicles.
So the total load works to ~16k VA and ~66 amps. Assuming my ballpark figures are not way off, I think it's safe to say that 100A service is plenty sufficient for current needs. I'm glad I went through this load calc exercise, so thanks for that suggestion.
As for nice-to-have uses, a 120V compressor would bump up the total load to ~19k VA and ~80A. A 220V welder would put us way over 100A, but arguably even that could probably be managed within a 100A service because it's a rare-use item, so we could schedule it for times when no other large loads are in use (e.g., no AC, compressor, microwave, or dishwasher).
I'm not too worried about potential future needs beyond this because we're not going to be here in 10 years; maybe not even 5 years.
I don't know the history, and yeah, there are some pretty old looking cables. Talked to a neighbor (our houses were built at the same time by the same builder) who upgraded to 200A panel a decade ago, and he said his old panel was a CB panel, not fused, but of course it's possible a prior owner made that upgrade.Looking at the main cable, it feels like this may have been a 60A fused service that got upgraded in 1970 with a 100A panel.
Is it REALLY a 100A 'service'?
Looking at the wires, seems like there is old romex, and much old cambric-covered cables. IMO it isn't a clean '1960 install'.
If it isn't wired properly to size for a 100A service, you don't even have that....
All I know for sure is that our current use hasn't tripped the main breaker.