Ah, I'm glad I found this thread. So, I am in the initial stages of planning a garage and want to store "light" things in the attic. I am working with a lumber yard which is preparing a price for a package of "everything" that I will need, including the trusses.

I would like to know what to tell them that I want, so that I get space for light storage, but NOT something designed ( and priced ) for engine blocks, which I don't intend to store up there. The firm that I'm dealing with is an old firm, and reputable, so I trust them, but I don't think I know enough about trusses to know what questions to ask them.

While I am on the subject, I am in my local volunteer fire department, and at drill last night, a local carpenter rattled on for quite a while about "gang nailed" trusses. He advocated trusses assembled with rectangles of plywood on each side of the truss, at all the places where 2x4's meet. So, when I talk with the firm building ( pricing ) my trusses, do I tell them "no gang nail plates"? My thinking is that there are millions of trusses assembled with them, and I don't hear about a lot of them collapsing, therefore, are gang nail plates okay, or not? I don't want to get the "Yugo" of trusses, OR the "Cadillac", but I'd like the Chevy" of the mix.



.

I would ask for 40 psf bottom chord live loading.
 

GMCGarage

Well-known member
Joined
Jan 31, 2017
Messages
1,264
I am still waiting to hear back from the builder although I did a little digging on my end. I believe its a 5/12 roof. Also its the same for 20'/22'. I attached a picture from the good ol' Menards website it appears they design everything to 62 lb per sq/ft. Appears they do not have a life load but the Dead load for btm cord is 10..

Thoughts? (I am not saying these are my trusses Although image looks close and stats look close)

10 psf is light, very light. 1/2" plywood is about 2psf, so that leaves 8psf. as reference thats about 1.5" depth of water. Find a 12x12 pan, put about 1.5" of water in it, and you get a feel for whats your capacity.
 
OP
M

MJBaldwin

Active member
Joined
Jun 19, 2012
Messages
36
Location
Delano, MN
Here is the document I got.

Thoughts?
 

Attachments

  • Pages from I30821912.301895-A.pdf
    117.4 KB · Views: 20
Last edited:

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
50,866
Location
Northern Central Ohio
While I am on the subject, I am in my local volunteer fire department, and at drill last night, a local carpenter rattled on for quite a while about "gang nailed" trusses. He advocated trusses assembled with rectangles of plywood on each side of the truss, at all the places where 2x4's meet. So, when I talk with the firm building ( pricing ) my trusses, do I tell them "no gang nail plates"? My thinking is that there are millions of trusses assembled with them, and I don't hear about a lot of them collapsing, therefore, are gang nail plates okay, or not? I don't want to get the "Yugo" of trusses, OR the "Cadillac", but I'd like the Chevy" of the mix.



.


I believe the standard used is 10 minutes for typical residential trusses built with plates. Ten minutes from their initial exposure to fire that can start failing.
 
OP
M

MJBaldwin

Active member
Joined
Jun 19, 2012
Messages
36
Location
Delano, MN
I believe the standard used is 10 minutes for typical residential trusses built with plates. Ten minutes from their initial exposure to fire that can start failing.

If you are worried about a fire why not add two layers of rock? That is your fire barrier.
 

NUTTSGT

Super Moderator
Staff member
Joined
Sep 14, 2009
Messages
50,866
Location
Northern Central Ohio
If you are worried about a fire why not add two layers of rock? That is your fire barrier.

You can do that, my response was to the other member asking about the plates and trusses used in typical residential trusses.

Drywall is a barrier but doesn't keep a place from burning down.
 

driftpin

Well-known member
Joined
Dec 22, 2016
Messages
11,192
Location
Miami-Dade/Broward Co. Florida
You're right-there in the hunt on that one. I believe the copy I have of Francis Brannigan's Building Construction for the Fire Service says, "...as-little as eight minutes before structural failure." Brannigan advocated for building placards to announce to arriving fire suppression units that the construction was light-truss constriction, because of the risk of catastrophic collapse in the event of a well-seated structure fire. He also didn't think much of light bar-joist construction either, for the same reason.

Here is a text for the fire service on building collapse by another world-wide respected authority, Vincent Dunn:

http://www.montgomerycountymd.gov/f...ollapse_of_burning_buildings_201606121459.pdf

Documentation of truss failure responsible for the deaths of two Memphis firefighters:
https://www.usfa.fema.gov/downloads/pdf/publications/tr-069.pdf

Unfortunately, there are many-more like this.

I am a career firefighter/paramedic, now retired, but still qualified as-such, and a Fire Service Instructor III, plans examiner, and Lifesafety Code Inspector. My career began 43 years-ago.


I believe the standard used is 10 minutes for typical residential trusses built with plates. Ten minutes from their initial exposure to fire that can start failing.
 

Vintage Veloce

Well-known member
Joined
Feb 27, 2015
Messages
1,076
Location
San Diego
Here is the document I got.

Thoughts?

This is your truss? 0 pounds live load and 10 pounds dead load? This means it is safe for a skinny cat to walk up there, that it.

Send this to a truss engineer (I suggested one earlier in this thread) and ask him what to do.
 

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
^^^ Yeah... not really ^^^

Here is the document I got.

Thoughts?

5 is better than 10, 15 would be better.

MJBaldwin it all depends on if you install drywall on the ceiling, if you install insulation and how much those weigh, pounds per square feet.

Do the numbers then see if the left over capacity is enough for you. It's pretty simple math.

As far as drywall for fire code, if you drywall the wall all the way up to the roof deck that isolates the garage from the home. Then you can do whatever you want with the ceiling in the garage. You won't be required to do anything for a ceiling.

My barn uses trusses rated for 15 psf for the lower chord. I built a loft and use it for light storage, but I am very mindful of what I place up there and where I put everything.
 
Last edited:

LifeLongWNYer

Well-known member
Joined
Oct 23, 2013
Messages
1,231
Location
South of Rochester, NY
Thanks guys, especially NUTTSGT for the reply, and understood about the sheetrock. That will probably so up, eventually, so I'm covered there. I did, coincidentally talk with the lumber yard today and asked my contact about the plywood vs: gang nails matter, he said he will contact the truss builder, but he suspects they are "set up for" gang nails and the plywood and galvanized nail method may no longer be possible.

I'd like to ask a question about the numbers in the truss design which was posted by MJBaldwin. The document sent to me by MY truss guy ( via the lumber yard ), with a couple of differences in that left hand column, is about the same. ( It appears they use either the same software, or the same format ) Mine has:
TCLL: 38.5
Snow: 50.0
TCDL: 10.0
BCDL: 0, and
BCDL: 10.0

The estimator told me that the statement "This truss has been designed for a live load of 20.0 psi on the bottom chord in all areas where a rectangle 3-6-0 tall by 2-0-0 wide will fit between the chord and any other members" PLUS another one "Bottom chord live load (40.0 psi) and additional chord dead load (5.0 psi) applied only to room. 16-18"

I guess I don't even know enough about this to be dangerous. Which of those numbers tells me what I can store in an attic, and what about the weight of the sheetrock on the bottom, and the plywood on the top? I guess the people who deal with trusses all the time know this, but why isn't there a legend to explain the abbreviations?



.
 

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
Thanks guys, especially NUTTSGT for the reply, and understood about the sheetrock. That will probably so up, eventually, so I'm covered there. I did, coincidentally talk with the lumber yard today and asked my contact about the plywood vs: gang nails matter, he said he will contact the truss builder, but he suspects they are "set up for" gang nails and the plywood and galvanized nail method may no longer be possible.

I'd like to ask a question about the numbers in the truss design which was posted by MJBaldwin. The document sent to me by MY truss guy ( via the lumber yard ), with a couple of differences in that left hand column, is about the same. ( It appears they use either the same software, or the same format ) Mine has:
TCLL: 38.5
Snow: 50.0
TCDL: 10.0
BCDL: 0, and
BCDL: 10.0

The estimator told me that the statement "This truss has been designed for a live load of 20.0 psi on the bottom chord in all areas where a rectangle 3-6-0 tall by 2-0-0 wide will fit between the chord and any other members" PLUS another one "Bottom chord live load (40.0 psi) and additional chord dead load (5.0 psi) applied only to room. 16-18"

I guess I don't even know enough about this to be dangerous. Which of those numbers tells me what I can store in an attic, and what about the weight of the sheetrock on the bottom, and the plywood on the top? I guess the people who deal with trusses all the time know this, but why isn't there a legend to explain the abbreviations?



.


Dude... start another thread. You've hijacked this one.
 
To avoid these ads, REGISTER NOW!
OP
M

MJBaldwin

Active member
Joined
Jun 19, 2012
Messages
36
Location
Delano, MN
LifeLongWNYer: You're not hijacking anything - we are all trying to learn here.

Its hard when you have one guy telling you that 10 will not even hold a cat although another guy saying that 15 he stores light objects up there. I am sure they have some sort of a safety factor built into it although I don't really want to rely on that. This is a standard 2-story home. That being said this is the way the construction industry is going. Trying to get things cheaper and manufactured items some work better I think and others not so much.

I think I will check with my builder.
 

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
Its hard when you have one guy telling you that 10 will not even hold a cat although another guy saying that 15 he stores light objects up there.

It's not hard at all. Only you know what you plan to store up there.

Weigh the items and their size, do the math, and you will have your answer.

Let's say you go with the advice of GMCGarage and use 40 psf and you want a 10' x 10' storage area with your ladder going right into the middle of. That area will hold 4,000 lbs.

Let's say you go with what you already know, 10 psf and that same 10' x 10' storage area but no ceiling or insulation in the garage. That will hold 1,000 lbs. (That's one fat dead wet cat Vintage Veloce)

What's realistic for you in your world?

For what you've previously described... 1,000 lbs should be more than enough.
 
OP
M

MJBaldwin

Active member
Joined
Jun 19, 2012
Messages
36
Location
Delano, MN
It's not hard at all. Only you know what you plan to store up there.

Weigh the items and their size, do the math, and you will have your answer.

Let's say you go with the advice of GMCGarage and use 40 psf and you want a 10' x 10' storage area with your ladder going right into the middle of. That area will hold 4,000 lbs.

Let's say you go with what you already know, 10 psf and that same 10' x 10' storage area but no ceiling or insulation in the garage. That will hold 1,000 lbs. (That's one fat dead wet cat Vintage Veloce)

What's realistic for you in your world?

For what you've previously described... 1,000 lbs should be more than enough.

Thanks for the info, what does the insulation/sheetrock/and plywood 7/16 oe 1/2 do I use OSB or ply? typically weight for that? I do plan on finishing it off
 

Vintage Veloce

Well-known member
Joined
Feb 27, 2015
Messages
1,076
Location
San Diego
I may be over cautious, because the garage attic at my old house had been "reinforced" by the owner and was sagging really badly, more than a 3 or 4 inches in the middle. It creaked and groaned and I was concerned goin up there. Then at my new house, the old garage there had a sagging roof, and we had to replace the lower cords with 2x6 and add supports to the ridgeboard and other upper pieces under the roof.

In out new building's attic I spent the $200 with a truss engineer (listed in the thread above) for about an hour of his time to really design what we wanted. The extra cost of minimal to upgrade to 2x6 trusses, space them in a custom way (less than 24" except where the stairway is placed) and to maximize the space and to support the attic stairway.

I'll note we are taking book boxes out of storage. They are 10"x10"x16" and full, weigh about 38 pounds each. So that is about the limit of a 40 PSF truss. I wouldn't put a stack of these in a 40 PSF attic, Personally I'd be sure to spread them out.
 

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
Thanks for the info, what does the insulation/sheetrock/and plywood 7/16 oe 1/2 do I use OSB or ply? typically weight for that? I do plan on finishing it off

Weights of Building Materials – Pounds Per Square Foot [PSF]

____________________________________

In our new building's attic I spent the $200 with a truss engineer (listed in the thread above) for about an hour of his time to really design what we wanted. The extra cost was minimal to upgrade to 2x6 trusses, space them in a custom way (less than 24" except where the stairway is placed) and to maximize the space and to support the attic stairway

Curious.... what did you end up using for the bottom chord loading, psf?
 
Last edited:

Vintage Veloce

Well-known member
Joined
Feb 27, 2015
Messages
1,076
Location
San Diego
My design was checked for 200# per truss for the stairs, plus 40 PSF total load in the 9’ wide attic area. Note also that my truss is worse case design at 28.5” on-center, with the trusses at 1’-4” and 2’ on center not carrying as much load.
The wide spacing was to accommodate the stairway, and that is only in one spot. Most of the trusses are on 24" centers, so that effectively makes things more robust than the calcs show.
These are still pretty basic trusses made of 2x6, 21' long, 6/12 pitch. 13 trusses (9 attic plus 2 end trusses) cost me $1870, delivered, here in expensive San Diego.
 

nolimits76

Well-known member
Joined
Jul 11, 2013
Messages
959
Location
Oklahoma
Weights of Building Materials – Pounds Per Square Foot [PSF]

____________________________________



Curious.... what did you end up using for the bottom chord loading, psf?

Thanks for the link.

Hey OP, notice the link states to include 1.5 PSF for misc items as the minimum (towards bottom of second page in bold).

Gyp board/sheetrock = 2.75 PSF
11/32” or 3/8" Plywood – OSB(3)1.0 - 1.2 PSF
15/32” or 1/2" Plywood - OSB(3)1.4 - 1.7 PSF
19/32” or 5/8" Plywood - OSB(3)1.8 - 2.1 PSF
23/32” or 3/4" Plywood - OSB(3)2.2 - 2.5 PSF
3" of insulation x .04 PSF = .12 PSF

Just for ease....

2.75 PSF gyp board + 2 PSF plywood + .12 PSF insulation + 1.5 PSF misc = 6.37 PSF total in building materials

That leaves you 3.63 PSF for storage. Or 363# for a perfectly distributed fat cat in a 10' x 10' space. :D
 

lakeroadster

Well-known member
Joined
Jan 19, 2015
Messages
5,166
Location
Central Colorado
Thanks for the link.

Hey OP, notice the link states to include 1.5 PSF for misc items as the minimum (towards bottom of second page in bold).

Gyp board/sheetrock = 2.75 PSF
11/32” or 3/8" Plywood – OSB(3)1.0 - 1.2 PSF
15/32” or 1/2" Plywood - OSB(3)1.4 - 1.7 PSF
19/32” or 5/8" Plywood - OSB(3)1.8 - 2.1 PSF
23/32” or 3/4" Plywood - OSB(3)2.2 - 2.5 PSF
3" of insulation x .04 PSF = .12 PSF

Just for ease....

2.75 PSF gyp board + 2 PSF plywood + .12 PSF insulation + 1.5 PSF misc = 6.37 PSF total in building materials

That leaves you 3.63 PSF for storage. Or 363# for a perfectly distributed fat cat in a 10' x 10' space. :D

Nolimits.. Your numbers are bloated, just like the cat. ;)

Your using 5/8" Gypsum and 5/8" plywood? And what's with the 1.5 psf misc?

Use 1/2" drywall for ceiling: 2.2 psf
Use 7/16" OSB as decking: 1.4 psf
Insulation.......................: 0.12 psf

Total weight = 2.2 + 1.4 + 0.12 = 3.72 psf

10 psf - 3.72 psf = 6.28 psf for your stuff.

That's 628 lbs of boxes and ****... :lol:

OP: Don't use a pull down ladder.. you need 6 psf just to support the ladder.

53 lbs ladder ***'y that measure 24" x 54": 53 / ((24*54)/144) = 5.88 psf

Build the shed in the backyard or some shelves in the garage... the attic storage is inconvenient, dirty and hotter than the hinges of hell. You ever try carrying boxes that are full of stuff up one of those pull down ladders? Now if it were just empty boxes.. sure.
 
Last edited:
OP
M

MJBaldwin

Active member
Joined
Jun 19, 2012
Messages
36
Location
Delano, MN
You could build a storage shed like I did. Collect the lumber from the builders "trash piles" & get paint, tools & other stuff on craigslist. It would only cost a few hundred bucks & be able to support anything.

https://www.garagejournal.com/forum/showthread.php?t=386711

Shed is in the plans for the future but I want this stuff up high and out of the way. Also a side note to that comment I dont know what kind of builders you have around there but the ones around my new house are very lean when it comes to materials used. They dont throw as much as one would think.
 

nolimits76

Well-known member
Joined
Jul 11, 2013
Messages
959
Location
Oklahoma
Nolimits.. Your numbers are bloated, just like the cat. ;)

Your using 5/8" Gypsum and 5/8" plywood? And what's with the 1.5 psf misc?

Use 1/2" drywall for ceiling: 2.2 psf
Use 7/16" OSB as decking: 1.4 psf
Insulation.......................: 0.12 psf

Total weight = 2.2 + 1.4 + 0.12 = 3.72 psf

10 psf - 3.72 psf = 6.28 psf for your stuff.

That's 628 lbs of boxes and ****... :lol:

OP: Don't use a pull down ladder.. you need 6 psf just to support the ladder.

53 lbs ladder ***'y that measure 24" x 54": 53 / ((24*54)/144) = 5.88 psf

Build the shed in the backyard or some shelves in the garage... the attic storage is inconvenient, dirty and hotter than the hinges of hell. You ever try carrying boxes that are full of stuff up one of those pull down ladders? Now if it were just empty boxes.. sure.

LOL, good call on the cat and my numbers. :lol::lol::lol:

By the way, you are spot on about the attic storage. I'm not sure I'd put as much work & effort into creating a storage space I know I will cuss time after time later on, but each to his own.

In two of the houses I've owned, I had attic access from an upstairs and that was the cat's meow. Those access ladders are just meant to piss people off I'm pretty sure. Currently i'm renting but when I build/buy again, I will seriously consider installing an attic lift/winch system.

One final thought....even at 628# of capacity that is for an EVENLY distributed load. Not to mention the weight of the OP should he decide to walk up there. Hopefully he's skinnier than these damn 1,000#, 600# and 300# cats we've been discussing.
 