Good morning,
I received a permit for moving my electrical main and service entrance, but there is one thing that I can't seem to find a straight answer on. Most forum responses seem to get grounding to a water pipe and bonding to a water pipe confused and it is hard to get an answer. I am going to word it as simple as I can and appreciate any answers.
Situation: I have a new 200a main panel on the attached garage, overhead service. It has four wires (3ea # 3 CU for the hot and neutral and 1ea #4 CU for ground) feeding the old 100A main (now a sub) in the house. The neutral bus has been unbonded in the 100A panel. There are two ground electrodes at the new main panel with #4 CU. All wiring in EMT. The old ground rods are still located by the new subpanel and can be used if necessary, but are not in use currently since it is attached. I am on a private well and the copper water pipe is NOT USED as a ground in anyway (this seems to be where the responses get sideways).
Short question: Can I BOND the water and gas pipes to a subpanel instead of going back to the main?
Follow up: If the answer is "No" to the above, is it ok to splice the copper bonding wire, since it currently terminates at the old main (now sub) and then feed it back to the new main, about 30' away?
I know the main ground wire cannot be spliced unless it is a non-reversible splice, but it is not a ground wire I am asking about, but a bonding wire. Again, this seems to derail the responses.
I did find this answer : https://www.mikeholt.com/videodisplaynew.php?pageid=4328
"(3) Building or Structure Supplied by a Feeder. The metal water piping system of a building or structure that is supplied by a feeder must be bonded to:
The equipment grounding terminal of the building disconnect enclosure,
The feeder equipment grounding (bonding) conductor, or
One of the electrodes of the grounding electrode system.
The bonding jumper for the metal water piping system must be sized to the feeder circuit conductors that supply the building or structure in accordance with Table 250.66. The bonding jumper is not required to be larger than the ungrounded feeder conductors. "
and that says it can be BONDED to the subpanel (if I am reading it correctly) as the "building's disconnect enclosure" = subpanel?
I really appreciate any responses.
Thank you!
I received a permit for moving my electrical main and service entrance, but there is one thing that I can't seem to find a straight answer on. Most forum responses seem to get grounding to a water pipe and bonding to a water pipe confused and it is hard to get an answer. I am going to word it as simple as I can and appreciate any answers.
Situation: I have a new 200a main panel on the attached garage, overhead service. It has four wires (3ea # 3 CU for the hot and neutral and 1ea #4 CU for ground) feeding the old 100A main (now a sub) in the house. The neutral bus has been unbonded in the 100A panel. There are two ground electrodes at the new main panel with #4 CU. All wiring in EMT. The old ground rods are still located by the new subpanel and can be used if necessary, but are not in use currently since it is attached. I am on a private well and the copper water pipe is NOT USED as a ground in anyway (this seems to be where the responses get sideways).
Short question: Can I BOND the water and gas pipes to a subpanel instead of going back to the main?
Follow up: If the answer is "No" to the above, is it ok to splice the copper bonding wire, since it currently terminates at the old main (now sub) and then feed it back to the new main, about 30' away?
I know the main ground wire cannot be spliced unless it is a non-reversible splice, but it is not a ground wire I am asking about, but a bonding wire. Again, this seems to derail the responses.
I did find this answer : https://www.mikeholt.com/videodisplaynew.php?pageid=4328
"(3) Building or Structure Supplied by a Feeder. The metal water piping system of a building or structure that is supplied by a feeder must be bonded to:
The equipment grounding terminal of the building disconnect enclosure,
The feeder equipment grounding (bonding) conductor, or
One of the electrodes of the grounding electrode system.
The bonding jumper for the metal water piping system must be sized to the feeder circuit conductors that supply the building or structure in accordance with Table 250.66. The bonding jumper is not required to be larger than the ungrounded feeder conductors. "
and that says it can be BONDED to the subpanel (if I am reading it correctly) as the "building's disconnect enclosure" = subpanel?
I really appreciate any responses.
Thank you!