Yup, trying my best to get it right. With the resources and support on the GJ I’m thinking it’ll be a nice slab.

What I find interesting is my “concrete buddy”, an old friend who works doing architectural and decorative concrete, was “vocal” about my decision to use a vapor barrier and rebar chairs. “Not necessary.....just going to be in the way....”

In the end he’s doing my concrete work, so I’ve been trying to listen, learn, and maintain our friendship. He likes to ***** and moan a bit, so I expected this. He’s a bit of perfectionist too as it regards to this sort of thing, so his reaction was interesting to me :)
 
Last edited:

gagecalman

Well-known member
Joined
Feb 5, 2020
Messages
194
Location
MD
That's interesting about the rebar chairs.
I had a concrete driveway done years ago. The owner didn't use the chairs.
He had to keep yelling at his guys "pull up the steel, this guy paid good money for it".
Still makes me wonder how much of my rebar is at the bottom of my slab.
 

ConCretin

Well-known member
Joined
Jan 20, 2011
Messages
3,378
Location
Central Maine
What I find interesting is my “concrete buddy”, an old friend who works doing architectural and decorative concrete, was “vocal” about my decision to use a vapor barrier and rebar chairs. “Not necessary.....just going to be in the way....”

In the end he’s doing my concrete work, so I’ve been trying to listen, learn, and maintain our friendship. He likes to ***** and moan a bit, so I expected this. He’s a bit of perfectionist too as it regards to this sort of thing, so his reaction was interesting to me :)

A vapor barrier is really only necessary if you have moisture in your soils and intend to apply an adhered flooring or coating. Finishers often don't like to see them because it complicates finishing with increased bleed water.

It's possible to pull up the mesh as you go but it takes a lot of diligence on the part of the finisher and is too often neglected. Most of us don't trust them as far as we can throw them. Supports provide peace of mind that your reinforcing is where it should be.
 
Last edited:
OP
D

Dyno Dan

Well-known member
Joined
Jan 31, 2012
Messages
121
Location
Southwest Montana
Well we live in a narrow valley with a creek on both sides, and we’re essentially in the lowlands. Our 20 acres has plenty of marshy spots, and the water “pumps up” each spring to ground level in certain spots. I built the shop on the highest ground we have, and brought in 650+ yards of 4-5” gravel to mitigate moisture concerns.

Beyond that I do want a floor coating. So, in the end I get the best vapor barrier I could find.

In regards to the bleed. Any tips or tricks to make sure I don’t end up with a piss poor finish. Is it just time and patience by the finishing crew?
 
OP
D

Dyno Dan

Well-known member
Joined
Jan 31, 2012
Messages
121
Location
Southwest Montana
I started like this with the chairs, but have since removed every other chair, and then offset that pattern in the next now. With the 18” OC grid, the chairs are spaced at 36”.

Here’s a pic when I started. I’ll get new pics soon

261fcaac30320b2a9509056f89718ce7.jpg
 

Attachments

  • 261fcaac30320b2a9509056f89718ce7.jpg
    261fcaac30320b2a9509056f89718ce7.jpg
    227.2 KB · Views: 2

ConCretin

Well-known member
Joined
Jan 20, 2011
Messages
3,378
Location
Central Maine
Well we live in a narrow valley with a creek on both sides, and we’re essentially in the lowlands. Our 20 acres has plenty of marshy spots, and the water “pumps up” each spring to ground level in certain spots. I built the shop on the highest ground we have, and brought in 650+ yards of 4-5” gravel to mitigate moisture concerns.

Beyond that I do want a floor coating. So, in the end I get the best vapor barrier I could find.

In regards to the bleed. Any tips or tricks to make sure I don’t end up with a piss poor finish. Is it just time and patience by the finishing crew?

I think you made the right call with a vapor barrier. The best way to minimize bleed water is to minimize mix water. Specify a mid range water reducer when you order the concrete. It will give you a nice workable 5-6" slump with less water than would normally be required to achieve a 4" slump.

You'll also be aided by the fact that you have roof over your slab. One risk from excess bleed water occurs when then the slab surface sets up too fast due to sun or wind. If the finisher moves too quickly and seals up the surface, water pools underneath and creates blisters and de-lamination. If its a hot, windy day, you might be prepared to put up shades and wind blocks. A calm, cool day is always ideal.
 
Last edited:
OP
D

Dyno Dan

Well-known member
Joined
Jan 31, 2012
Messages
121
Location
Southwest Montana
It would be for sure. Now that it’s 90-92 degrees in Southwest Montana I may use it as such.

More progress on laying rebar.

34d839c579d5612b631628e7ae38952b.jpg
47e28b809303d3d8a4e87f490dd037f8.jpg
 

Attachments

  • 34d839c579d5612b631628e7ae38952b.jpg
    34d839c579d5612b631628e7ae38952b.jpg
    286.6 KB · Views: 3
  • 47e28b809303d3d8a4e87f490dd037f8.jpg
    47e28b809303d3d8a4e87f490dd037f8.jpg
    287.8 KB · Views: 2

DJF3

Well-known member
Joined
Feb 15, 2020
Messages
186
Location
British Columbia, Canada
Nope. I decided against in floor heat this go around. Do some folks still insulate under the slab even without in floor heat? I’ll likely end up with an overhead radiant tube heater set to about 45 in the winter months.

Yes....I am going with an overhead radiant heater and no in floor heat. I'm going to put 3" R12 EPS under my slab. Thought process is that the overhead will heat the concrete, and the heat will be retained better than if the slab were directly on the ground. There will be a vapor barrier as well. And 4 ft ICF foundation walls. Might be overkill, but I don't think I will have cold concrete!
 
OP
D

Dyno Dan

Well-known member
Joined
Jan 31, 2012
Messages
121
Location
Southwest Montana
That sounds perfect. Yes on the extra bars. I'd thicken the edge to 8" or so and install a couple bars in the bottom.


Ok, 1 step closer. I’m at 8” of depth at the door thresholds. Just a bit more rebar and then the “pour boys” are coming in Wednesday. My concrete buddy said we’ll need a couple sheets of plywood to wheelbarrow the mud to the back of the shop (36’ depth, and concrete shute won’t reach that far). Plan is to lay it on top of rebar, I just hope it doesn’t crush the chairs.

24f728e3a20e2466a613a0196532a71f.jpg
5e59c43a3a6d73ecd42bddfd2e93297f.jpg
 

Attachments

  • 5e59c43a3a6d73ecd42bddfd2e93297f.jpg
    5e59c43a3a6d73ecd42bddfd2e93297f.jpg
    180.7 KB · Views: 2
  • 24f728e3a20e2466a613a0196532a71f.jpg
    24f728e3a20e2466a613a0196532a71f.jpg
    179.7 KB · Views: 4

joes169

Well-known member
Joined
Sep 19, 2011
Messages
663
Location
WI
Very nice prep work!

I would lay 2x4's on the flat under the rebar grid to help support the plywood. Obviously, pull them out as they fill with concrete.
 

joes169

Well-known member
Joined
Sep 19, 2011
Messages
663
Location
WI
In regards to the bleed. Any tips or tricks to make sure I don’t end up with a piss poor finish. Is it just time and patience by the finishing crew?

You've probably come up with a plan with the main concrete guy by now, but it's not really a big issue to pour over a vapor barrier in a shed like this. We always use some air entrainment (usually about 4-4.5%) for power troweled floors on VB, as well as a small dosage of mid-range water reducer. We typically pour a 5" slump or tighter, which limits the bleeding issues as well. I would be prepared to have the ability to close the OH doors if necessary, depending on sun and wind conditions.

Good Luck!
 
OP
D

Dyno Dan

Well-known member
Joined
Jan 31, 2012
Messages
121
Location
Southwest Montana
Pouring on Wednesday! Concrete buddy said to pull strings and triple check the depth measurement. “You don’t want to run out of concrete during the pour”. We’re pouring a 26x36 slab, 5” thick with 8” thickened edges at the two 10’ door thresholds.

Never been so excited for a chunk of flat surface. Woohoo.
 
To avoid these ads, REGISTER NOW!
OP
D

Dyno Dan

Well-known member
Joined
Jan 31, 2012
Messages
121
Location
Southwest Montana
I got roped into running a wheelbarrow but I can officially say I was part of the process.

It’s poured!

98b3786daf55bf827e4886cbdf2f54df.jpg
a588c656c9d9614971f215609a0f163f.jpg
f9a9429ba0ab3e98a8dc2bd6c450236f.jpg
956f8edc2423dbb36390cec76adc35a6.jpg
a8e595d0e25b76fcd988dbf82010f2b5.jpg
a0e7b45b015b5e8d4edb6a33403a0400.jpg
5a800d75af99ecc81fed0226d7aac1e7.jpg
1ed12f81d8311ef9e6f782ff7dcd1307.jpg
19b0099bd8c327b82267f18a7286267e.jpg
 

Attachments

  • 19b0099bd8c327b82267f18a7286267e.jpg
    19b0099bd8c327b82267f18a7286267e.jpg
    87.2 KB · Views: 2
  • 1ed12f81d8311ef9e6f782ff7dcd1307.jpg
    1ed12f81d8311ef9e6f782ff7dcd1307.jpg
    118.1 KB · Views: 2
  • 956f8edc2423dbb36390cec76adc35a6.jpg
    956f8edc2423dbb36390cec76adc35a6.jpg
    160.6 KB · Views: 2
  • f9a9429ba0ab3e98a8dc2bd6c450236f.jpg
    f9a9429ba0ab3e98a8dc2bd6c450236f.jpg
    166.9 KB · Views: 2
  • a588c656c9d9614971f215609a0f163f.jpg
    a588c656c9d9614971f215609a0f163f.jpg
    113.3 KB · Views: 2
  • 98b3786daf55bf827e4886cbdf2f54df.jpg
    98b3786daf55bf827e4886cbdf2f54df.jpg
    171.6 KB · Views: 1
  • a8e595d0e25b76fcd988dbf82010f2b5.jpg
    a8e595d0e25b76fcd988dbf82010f2b5.jpg
    158.2 KB · Views: 1
  • a0e7b45b015b5e8d4edb6a33403a0400.jpg
    a0e7b45b015b5e8d4edb6a33403a0400.jpg
    172.5 KB · Views: 1
  • 5a800d75af99ecc81fed0226d7aac1e7.jpg
    5a800d75af99ecc81fed0226d7aac1e7.jpg
    89.8 KB · Views: 1
OP
D

Dyno Dan

Well-known member
Joined
Jan 31, 2012
Messages
121
Location
Southwest Montana
And they did a slight taper downwards at the door sill.

262c9160df9965577f8585bfc3e9a9ea.jpg
93b83d37a67c0c246f01044e5044b9a4.jpg
491047c8459def264cbb1b244bdbd307.jpg
 

Attachments

  • 491047c8459def264cbb1b244bdbd307.jpg
    491047c8459def264cbb1b244bdbd307.jpg
    161.8 KB · Views: 2
  • 93b83d37a67c0c246f01044e5044b9a4.jpg
    93b83d37a67c0c246f01044e5044b9a4.jpg
    143.6 KB · Views: 3
  • 262c9160df9965577f8585bfc3e9a9ea.jpg
    262c9160df9965577f8585bfc3e9a9ea.jpg
    165.8 KB · Views: 3

joes169

Well-known member
Joined
Sep 19, 2011
Messages
663
Location
WI
Looks great, enjoy the new floor!

That's how we treat OH door openings as well, pitch them down about 3/4" in the last 16"or so to keep rain splash from entering.
 
OP
D

Dyno Dan

Well-known member
Joined
Jan 31, 2012
Messages
121
Location
Southwest Montana
So I've been looking at floor coating options, both expoxy and polyurea. I have questions...

What temperature is acceptable for application on either product. It's getting cold at night, as low as 28 degrees thus far. Is the concrete temp a concern, or the ambient temp, or combo of both.

Concrete was left naked and the finisher left some "fuzz". Do I need to grind in order to get proper adhesion, or can I apply as is.

What's the hot ticket to fill my expansion joints. Do they get filled before or after the coating goes down?
 
OP
D

Dyno Dan

Well-known member
Joined
Jan 31, 2012
Messages
121
Location
Southwest Montana
Can someone help me understand what’s going on here? I did “water the slab” for about 20 days after the slab was cut (which happened the day after the pour). I’m on day 37 now, so it should be cured, and I did put two 16” pieces of plastic to check for moisture and there wasn’t a drop.

I intend on coating, so I don care what this looks like now, I’m just curious about the difference in color. Also, there are a couple of spots where there are some tiny cracks, pits, and voids. I’m thinking I had better mechanically grind the slab, etching may not be the hot ticket.

6545212d243f5e2ea14c226bc501a69c.jpg
56e9122c7e188c4e103967b208a001bd.jpg
db0d5e1140d921e49c506ead9bb48315.jpg
c708f1dcd0c93530397ea02edd61a667.jpg
7e550fa9d4ff6415bf20327765461520.jpg
a6818b6ab6ea0172ac461e15e4f78976.jpg
f968660b212e72d86c86bbd1093680a2.jpg
 

Attachments

  • f968660b212e72d86c86bbd1093680a2.jpg
    f968660b212e72d86c86bbd1093680a2.jpg
    132.7 KB · Views: 3
  • a6818b6ab6ea0172ac461e15e4f78976.jpg
    a6818b6ab6ea0172ac461e15e4f78976.jpg
    132.6 KB · Views: 2
  • 6545212d243f5e2ea14c226bc501a69c.jpg
    6545212d243f5e2ea14c226bc501a69c.jpg
    131.6 KB · Views: 2
  • 56e9122c7e188c4e103967b208a001bd.jpg
    56e9122c7e188c4e103967b208a001bd.jpg
    122.9 KB · Views: 2
  • db0d5e1140d921e49c506ead9bb48315.jpg
    db0d5e1140d921e49c506ead9bb48315.jpg
    111.5 KB · Views: 2
  • c708f1dcd0c93530397ea02edd61a667.jpg
    c708f1dcd0c93530397ea02edd61a667.jpg
    72.8 KB · Views: 2
  • 7e550fa9d4ff6415bf20327765461520.jpg
    7e550fa9d4ff6415bf20327765461520.jpg
    121.5 KB · Views: 2

TractorJeff

Well-known member
Joined
Dec 8, 2013
Messages
3,309
Location
Elkhorn, WI
That's interesting!
Mine stayed that same black/dark color! I didn't get those white splotches like yours.
I assumed it was because it was poured in October and cured real slow? The Concrete Guys sprayed it with some type of Sealer also?
 
OP
D

Dyno Dan

Well-known member
Joined
Jan 31, 2012
Messages
121
Location
Southwest Montana
Poured on the 26th of September. No sealer, completely raw.

After a good cleaning (heck it’s new concrete), and 2 etching sessions, pressure washing 3x, this is where I’m at. I had some trouble with white powdery residue that persisted after the etching, hence the 3x rinsing.

Nice spell of warm weather here in Montana, so I hope to coat with Rust-oleum Rock Solid when I return from a business trip on Tuesday. I did my best and I hope this product works well.

5f2e0b137093b0126dd2bca5fedbe737.jpg
88792a44caf0fcad045e25b3bfffd8cc.jpg
406de39d665ca0b2ed28d71aae513576.jpg
8b2365ac731ac6f1b40eb0144de79e88.jpg
 

Attachments

  • 8b2365ac731ac6f1b40eb0144de79e88.jpg
    8b2365ac731ac6f1b40eb0144de79e88.jpg
    89.9 KB · Views: 1
  • 406de39d665ca0b2ed28d71aae513576.jpg
    406de39d665ca0b2ed28d71aae513576.jpg
    100.4 KB · Views: 1
  • 88792a44caf0fcad045e25b3bfffd8cc.jpg
    88792a44caf0fcad045e25b3bfffd8cc.jpg
    93.8 KB · Views: 1
  • 5f2e0b137093b0126dd2bca5fedbe737.jpg
    5f2e0b137093b0126dd2bca5fedbe737.jpg
    88.1 KB · Views: 1
Last edited:

Falcon67

Well-known member
Joined
Jun 11, 2009
Messages
18,371
Location
Merkel, TX
The higher the epoxy content of the floor paint, the better IMHO. I used an K-M industrial floor coating that was engineered for less than perfect surfaces. Etched, dried and rolled. 9 years, no problems or lift. Warm drag tires leafe rubber on the floor, no paint lift.

Mine was blotchy even after etch. As long as it's good and dry, should not be any problems I'd think. And mine cured in 100F+ weather. This pre-paint etch pic was 6 months after pour
Floor2.jpg


And after
Floor3.jpg
 
OP
D

Dyno Dan

Well-known member
Joined
Jan 31, 2012
Messages
121
Location
Southwest Montana
The deed is done. 2 coats of Rock Solid dark gray with a medium broadcast.

a053c648447e58079ec3a79c696c5601.jpg
98fc112d96b87ca89b464f948cbde569.jpg
 

Attachments

  • a053c648447e58079ec3a79c696c5601.jpg
    a053c648447e58079ec3a79c696c5601.jpg
    480.5 KB · Views: 2
  • 98fc112d96b87ca89b464f948cbde569.jpg
    98fc112d96b87ca89b464f948cbde569.jpg
    392.4 KB · Views: 1
OP
D

Dyno Dan

Well-known member
Joined
Jan 31, 2012
Messages
121
Location
Southwest Montana
Well, now that I’m in this state, I would say that I will be filling the expansion joints after my coating. I’m open to suggestions on what product to use.
 
OP
D

Dyno Dan

Well-known member
Joined
Jan 31, 2012
Messages
121
Location
Southwest Montana
Parked a couple rigs on the shiny new floor. Mother Nature decided to drop temps and some snow, so it was a perfect time to break-in the new shop. e6783fc9069abc1ef8234b4e1f7f28d2.jpg
a7873ce7d24487556380ee3feff6cbc6.jpg
66fe3da53e3bcc704dbd0c81ea3ded08.jpg
 

Attachments

  • 66fe3da53e3bcc704dbd0c81ea3ded08.jpg
    66fe3da53e3bcc704dbd0c81ea3ded08.jpg
    174.8 KB · Views: 2
  • a7873ce7d24487556380ee3feff6cbc6.jpg
    a7873ce7d24487556380ee3feff6cbc6.jpg
    176 KB · Views: 1
  • e6783fc9069abc1ef8234b4e1f7f28d2.jpg
    e6783fc9069abc1ef8234b4e1f7f28d2.jpg
    136.4 KB · Views: 2

Chris705

Well-known member
Joined
Nov 1, 2012
Messages
834
Location
The Finger Lakes of NY
The grey Sika-flex self leveling caulk available at HD is a lighter grey than your floor color (I believe closer to the light grey chips you used)....so I don’t know how you would like it..
I believe these caulks can be tinted to any of several colors, not sure where you found your vapor barrier and rebar chairs but if it was a real contractor supply house they may have insight on availability of colors?
Btw - awesome job on your project!
 

Mowerpan

Well-known member
Joined
Jun 21, 2005
Messages
116
Location
Sarasota, FL
Is Sika Polyurethane Gray acceptable to use to fill in my saw cuts? Just looking to keep those voids clean / free of debris.



I would not fill them in with this. I did this to mine and the caulk is slightly sticky after install just enough to pick up dust/dirt and now the caulk is darker and just looks dirty. If I did it again I would not fill them in.


Sent from my iPad using The Garage Journal mobile app
 