Electric unit heater

qmdv

Well-known member
Joined
Dec 20, 2012
Messages
54
I found a used 10,000 watt unit hater. It was wired from the factory for 480 volt. It says it can be wired single phase. If it is wired single phase will it still be 10,000. Here is the rating plate attached.
 

Attachments

  • 10 kw unit.jpg
    10 kw unit.jpg
    68.9 KB · Views: 27
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,862
Location
NJ
Even if you were able to reconfigure the element connections (just a maybe) the fan would still be 480v.

The wiring and contactor sizes would need to increase.

Probably also a transformer with only 480v input.

I would pass on it.
 