Extra Outlets in my Shop
Model A Fan
NW Washington
I'm just looking for confirmation this is done correctly. Outside of the first outlet being a GFI, is anything incorrect? Should I go back and put a GFI as the first outlet?
I haven't powered it up yet, but the run is powered by a 15A breaker. I'll be doing three more quad outlets on this breaker. Is that too many? I will only be using one piece of equipment at a time. Thank you!
mm08822
You could have eliminated the wagos in the receptacle box.
Buy some white.
First recept should be gfci. Change out what is needed to make that happen. Not sure pics are of the first recept on the circuit.
Model A Fan
NW Washington
Buy some white.
I'll swap the first one for the GFI.
The first two pics are of the first outlet box.
I have the wagos as I got them for a little over $0.03/piece, so I figure why not. In the top junction box, I used a 5-way and 4-way Wagos as I plan to add more wire into that box and run it through the wall to the other side.
Model A Fan
NW Washington
Could I use one of these instead of a GFCI in the first outlet? If not, how/where do you use it?
I bought white THHN for this project and subsequent ones.
PCustoms
VT
No.
That's surge suppression, not ground fault.
As previously stated the black with white tape is not allowed.
I would also not use the blue backed outlet shown in your first post, that's $0.70 outlets area about the cheapest thing you can buy and don't hold up.
Other then that no safety issues I see.
loganb
Omaha, NE
Just curious, wouldnt it be easier to just use a GFCI breaker ?
Gfci outlets are cheaper than breakers, sometimes substantially depending on panel type. Some people also aren't comfortable swapping a breaker in a live panel....so the common solution is the first receptacle solution. Not sure one is that much faster or simpler than the other.
Higgins
Shepheardsville, KY
Socket replacement is lest costly and quicker !!!
Case in point… we had a church member had her fridge go out. Turned out it was a CB in the electrical panel in the lower basement level. They had lived there over 40 yrs and never had to look into electrical panel.
We changed out the CB and installed a GFI with the green/red LED.
Model A Fan
NW Washington
So I just installed the GFCI into the box. I'm using a double outlet cover and wanted a second outlet in that slot. That made it more complicated, but I think I figured it out. 😅
I've drawn out the circuit to show the wiring (wires are harder to photograph).
Basically I have Romex feeding THHN in 1/2" conduit as the line. They are "Wago'd" together at the junction box. The Romex feeds the first 3-strand of THHN down the conduit to the GFCI.
In the metallic box, I have the GFCI fed by THHN. The first set of THHN is connected to the GFCI at the TOP posts (black to gold, white to silver).
I then have a short wire running from the BOTTOM posts of the GFCI to the TOP posts of the regular outlet (black to gold, white to silver again).
From there, I have three more THHN strands running BACK UP the conduit to the Romex waiting up top. This second set of THHN is connected to the BOTTOM posts of the regular outlet. I believe this is considered "LOAD".
In both metallic boxes, there is a ground screw I attached a grounding wire to and put it into the 5-way Wago. Inbound Romex Ground, both sets of THHN grounds, metallic box ground, and outbound Romex are all Wago'd together in the top metallic junction box.
In the bottom box, I have both THHN grounds, ground "jumper" for GFCI, ground "jumper" for regular outlet, and metallic box grounding wire.
If need be, I'll eliminate the second outlet in this box to save the headache of this set up. But I think I have it correct. I'm not an artist, but I've tried to (amateurishly) draw the circuit. It's not fed live, it is not currently hooked up to power. I appreciate all help and criticism. I've also attached real pics. Romex is roughly 9' in the air between a wall and floor joist in a barn.
Is it OK to have all the grounds Wago'd together like this?
PCustoms
VT
Sorry, can't follow that.
Seems that you have a lot of grounds in the box, you don't need a "to" and "from".
Also the line should feed the GFCI on the "line" side, then all outlets from there on should be fed from the "load" side of that GFCI.
This may have been a case where a breaker was better, again I can't follow your diagram.
Where did the romex come from, was that pre-existing?
sparky 1971
Central Iowa
It's fine. An extra ground wire isn't going to hurt anything. One thing that I would do is connect the wires from the load side of the GFCI to the wires leaving, and pigtails to the standard receptacle.
sparky 1971
Central Iowa
Sure it works, but it isn't needed and can affect box fill
Two #12 hot, two neutrals, two grounds, and two devices require 20.25 cubic inches. The box is 21.0 and a raised cover is 6.5. It's not needed, but no different than if it had two sets of romex cables running to and from it.
(and be a headache).
I fail to see how sticking one wire under a Wago is a headache. Once again, it's no different than two romex cables. And, I realize there isn't a picture of the box with the GFCI, but the pictures that are posted show one ground wire in the pipe.
@Model A Fan is the "line" on the left of your sketch your feed side?
Ya suppose maybe he took the feed to the standard receptacle then from there to the GFCI?
PCustoms
VT
Dunno man, just pointing out it's redundant and not needed. Personally whenever I can minimize wires in a conduit of box it seems easier to me.
Not sure. When I glanced at the pics initially I didn't get it. With all the weird things we see here thought it's worth clarifying that his string of outlets are fed correctly.
Model A Fan
NW Washington
Ground #1-Romex ground coming from breaker panel to junction box Wago
Ground #2-THHN "No. 1" running from junction box Wago down conduit to Wago in switch box
Ground #3-Ground Screw in switch box connected to Wago
Ground #4-THHN "No. 2" running from Wago in switch box back up conduit to junction box Wago
Ground #5-Ground screw in junction box connected to Wago
Ground #6-Romex ground connected to junction box Wago leaving junction box to next junction box
The "line" (as indicated on my diagram) is the wire coming directly from the breaker to the GFCI. The Romex connects with the first THHN group running down the conduit. The neutral THHN is connected to the top silver screw, hot THHN to the top gold screw and the grounding THHN wire is connected to the Wago.
The "load" terminals (as I understand it) are the bottom screws. There is a short piece of black THHN to connect the gold "load" screw on the GFCI to the top gold "line" screw on the second/regular outlet. There is a short piece of white THHN to connect the silver "load" screw on the GFCI to the top silver "line" screw on the second/regular outlet.
From there, the second set of THHN is connected to the bottom screws on regular/second outlet to go back up the conduit to the Romex that is "leaving" the junction box.
I installed the Romex on this project and was under the impression that it was OK to run it like that. It is not hooked up to any power source, yet.
Sure it works, but it isn't needed and can affect box fill (and be a headache).
The "line" is the feed side, it runs from the breaker to the junction box and powers the inner workings.
Could the two sets of white/black THHN have shared one ground wire?
Feed is going to the GFCI top screws first, from GFCI bottom screws to the top screws on the standard receptacle, and from the bottom screws on the standard receptacle back up to the Romex that leaves the junction box and heads down the line.
Basically the Romex coming in is connected to THHN which runs down the conduit to the GFCI's top screws. The bottom screws have small wires running from them to the top screws of the standard receptacle. The standard receptacle has THHN running from its bottom screws to the junction box where it connects back to the Romex in the junction box and back outside to the next junction box.
I'm sorry if this is a little difficult to follow. I've tried to use correct terminology, but might have missed it in a few places. Thank you for your assistance everyone! :D
dave*99
Coastal NJ
I believe what you have connected will work. Pop the GFCI test button and confirm the downstream receptacles go dead.
Small issue, you only need 1 ground wire in your vertical conduit. Either ground 2 or 4 is redundant.
Ground #3-
Ground #5-
Model A Fan
NW Washington
Thank you for the info, I had begun to understand that after reading the other replies. What is the "science/theory" behind how that works? I find that by understanding the way something works helps me to do the project better (because I know how and why something is supposed to be a certain way). Sometimes "I just gots ta know".
How does one ground between both sets of black/white THHN provide adequate grounding for both sets of THHN?
As for the GFCI, I'll have to connect the Romex into the box before I can test it, but I'm hoping that will be next weekend. I have 2-3 more boxes to wire on this circuit so I can have lighting and equipment plugged into it. I'm overcoming my barn's status as storage space by installing lighting and outlets because that's what its been for so many years. Now I'll be able to work in my shop without running extension cords across the floor to my different pieces of equipment.
dave*99
Coastal NJ
There are 2 ways to look at this. You ran 2 wires in parallel from wago to wago. Only 1 wire of sufficient gauge is needed. If you had a fault from a 20A circuit hit your ground wire you only need to carry 20A in the ground wire. Not 40A. It’s a tad more complicated but that is the basics.
The other concept is all the grounded components in a 20A circuit need a 20A path to the service panel. This carries the trip or fault current needed for the breaker to act. The grounding conductors serve to tie it all together. Touch a live wire to anything connected to that ground wire and pop goes the breaker.
sparky 1971
Central Iowa
It's perfect as long as the top set of screws is the line side. The GFCI receptacles I use have the line terminals on the bottom.
Model A Fan
NW Washington
I'm doing all this on a 15A breaker, but I'm assuming I can just use 14AWG for the 15A circuit. If it works as it is, I may just leave the duplicate ground wire. The only benefit would be I could remove the 5-way Wagos and save them for later and just use the 4-way ones in their place after I remove a redundant ground wire from the conduit.
These GFCI outlets are taped on the bottom terminals when new from the package, so I was using the top terminals as the "line" and the bottom as the "load" (feeding the standard receptacle's top screws and then the outgoing Romex connects to the bottom screws via the second set of THHN).
djbmw
Ottawa, Ontario, Canada
If you want to do this to code then the romex cannot be exposed. It must be within a wall and/or conduit. Alternatively you can use armoured cable. Additionally, ensure you have the correct stapling/securing of the wire.
Norcal
AC or MC cable does not give you a pass over NM sheathed cable "Romex"®, they are subject to similar rules as NM cable to be protected from physical damage.
  • Like
Reactions: Max
djbmw
Im in Canada so the CEC applies and, for us, Rule 12-518 in the CEC states, "Protection for cable in exposed installations", and does allow for AC to fit the requirement.
  • Like
Reactions: Max
Max
Georgia
Works for you, but not the OP that is in the US...
Model A Fan
NW Washington
So, should I strip the Romex off and install some conduit? It adds a little expense, but it is nothing outrageous. Having the exposed Romex makes it easier to modify/see where the wire is instead of burying it in a wall.
PCustoms
VT
Code wise, probably.
Practically, leave it.
Every basement I've ever been in has wiring that is "exposed", yet somehow all these houses passed an inspection.
sparky 1971
Central Iowa
It looks to me like the Romex is run at the top of the wall so it's up to you. By code, it has to be protected from physical damage, but there is no definition of what that is, leaving it wide open to the interpretation of the AHJ and that is you if there are no inspections going to happen. There are places where it would pass as is, others it would have to be in conduit. If it's where I think it is, about the only damage that could happen aside from leaning tall things against the wall .is from rodents, and for some reason, mice find the jacket on romex tasty. I've been in many barns to find romex completely chewed down to bare conductor.
Norcal
If Romex® has the jacket stripped off to use the individual conductors in conduit, it is scrap metal since the conductors are not marked it is not a recognized wiring material code wise.
Model A Fan
NW Washington
The barn when I bought the place had Romex running through holes in the rafters. Its worked fine for decades, so that's why I chose to run it the way I did.
I appreciate the insight. My barn cats seem to take care of the ROUS. I have had to chase a possum and racoon out, but so far the worst pests are flies that seem to breed like crazy. I vacuum them up every so often so their carcasses aren't littering my window sills and work benches.
Can I run Romex through conduit and be within regs? I will refrain from stripping the jacket off and using the unmarked wire as THHN. Too bad it isn't marked, I'm sure it would not cost much to mark it like THHN is marked.
sparky 1971
Central Iowa
Not supposed to do that. I'd just buy the THHN...
Sure you can, unless there is a written amendment against it.
My bad... I was always taught it was a no-no... Locally... My inspector won't pass it. NO IDEA why but he won't.
The inspector is either an idiot or there is an amendment in place, but I can't think of one good reason to prevent Romex from being in conduit. The NEC even lists most, if not all, types of conduit as acceptable for running Romex in to protect it.
We do have one thing in our amendments that I don't like. I forget the exact wording, but it basically says the inspector is always right. I haven't had a problem with it yet but the potential is always there, maybe you have something similar and he just doesn't like it.