This thread lacks serious context, from the standpoint of your question was too wide, and the answers are lacking detail..
As a refreh of my earlier post, Im a stand by dealer/factory cert tech. So that is my world, but being an independent guy, I work on everything, including portable gennies, up to commercial standbys ( small diesels and automotive gas ). I might work on 2 portables a month, so its not my area of expertise,... or very little of what I do.
Related, but not on point, right now I have two large portables waiting for repair, commercial units, branded " Briggs and Stratton ", and both have 420cc Honda GX Clones on them, telling me that Briggs has given up on their own product line in an attempt to sell a " somewhat " reliable generator, that is too funny ! But plays into what your asking about, and what Steve may have commented on, that is some of these small engines cant handle the load over time. The standbys dont appear to have this problem.
Back to the question, and it needing to be more specific,,,..
Each class has its own problems. to exaggerate the point, a harbor freight 2 cycle 15amp machine is going to **** the bed almost immediately compared to a Honda product of the same size, you literally can not compare the two, but they are sold in the same application and market, lets just assume " camping ". 900watts from Hazard Fraught is $124, and Honda's smallest at 2.2kw, is $1000.
This disparity is carried through all the sizes and class, although the bigger you get, the gap closes somewhat.
To have meaningful conversation, lets break down what it is exactly you are wanting to know.. it might help you and others that come along later looking to learn something.
It sounds like your in the 10kw'ish camp, are you wanting a portable or a standby ? You can get diesel in this size range, like a Kohler with a Kubota, or on the other side you can get gasoline China no name junk ? Clearly what ails the Kohler will not be ailing the China Junk.
Propane machines are likely not going to have the engine problems associated with gas small engines to some degree.. which I would hope is obvious.
Then there is honda, and the rest,....
As mentioned previously, I do standby, the machines I work on dont have prime mover problems.. they do have control problems, and in the same breath, time kills these machines because they are hardly ever used where Im at. We have good weather and really good infrastructure, so they almost always have more exercise time than run time.
Guys running a portable 10hrs a day building houses, yeah I can see where they are going to move through engines,.. and everything is going to fail from heat cycles, running WOT/heavy load most of the time...in open weather, UV damage to parts, etc,..
I could anecdotally run on for hours..
You do raise a good point. I had already asked other generator related questions on the general tool thread. All started because this past Feb I moved to a new area, rural, and we have 1-3 power outages /month, always 3 hours or more, and in winter it will be longer according to others living in the area.
I need something in the 10-20Kw size, this is not determined yet because I am having trouble determining how much is needed just for my 3 ton AC/Heat Pump (not heating coils, just a heat pump) which has a RLA just under 15 amps and an LRA of about 73 amps.
I have no NG in the area and not a fan of LP, had it at my previous house and find it expensive when the tank rental & delivery charges are added up, so I was hoping to find a decent diesel. Many thought diesel would have its own issues and LP is the way to go. Granted, I am sure they all have their issues, but for me in my situation, diesel seemed like the choice, but have not rules out LP, or even gas for that matter if I am able to get away with 10Kw or so. (You mention cheap Chinese ****, true there definitely are, but there are also some decent Chinese machines like Champion. They have made quite a name for themselves and ratings by users, be it on Amazon or elsewhere are always very high)
Getting back to the question, I was asking this because, looking at a generator as a 2 component system - the engine on 1 side and the electricity generating system on the other, I was always under the impression, engines were more prone to problems. Of course this being my limited experience with portables more than my zero experience with standby units.
If my suspicions were wrong, then what would I need to look for on the "generator" side, how different is one brand to the other (Like your example of Honda engines at 1 end of the spectrum or cheap Chinese & old B&S cast iron sleeve motors at the other end) when looking at the electronics or generator component. About 20 years ago I had done some research and the 10Kw and under portables, the consensus was that 2 or 3 companies were making the electronics, I believe Onan, Mitsubishi and 1 or 2 others for all generators on the market. Maybe that had changed today and maybe in the standby market each company (Generac, Kohler, Onan...etc) make their own...I don't know.
Seeing as you would be what I consider an expert, what is your advice in what to avoid and what to go for in the 10-20Kw, probably standby but a good portable could also be considered,
BTW, between Trane not responding, my contractor and other HVAC people I have spoken to, and articles such as this
https://generators.smps.us/start.html and the section on "SIZING GENERATOR TO START A MOTOR" stating a formula of (LRA x .7) x 240 volts x .7) = required VA. One HVAC guy found the specs for me which is my exact model
Based on these specs, the yellow highlight being mine, he stated I would need 14.75 continuous and 18 peek to start it....not sure how he came up with these numbers
So not counting other items I would need to run (2 sump pumps, 1 well pump + 1 fridge and a couple of other items), I have a low of 4500 watts to a high of 18,000 watts
just for the AC/Heat pump....very difficult finding the right gen size just for the actual startup need.
Another frequent contributor on GJ has suggested adding a soft start would help quite a bit (like this
https://www.microair.net/collection...or-115-and-230v-ac-motors?variant=29181662283 ) which I will probably get.
Add to all of this, I have recently come to the realization that my heat pump needs my furnace to be running (electric furnace 20Kw!!!) or it won't run. So I will need to have it added on the transfer switch panel, just not use the heating with the furnace.
I had one "tech" from the Trane contractor company (I have both the heat pump/AC + the furnace added about 2 months ago) state they don't give advice on how many staring watts/continuous watts are needed. These questions should be left to the generator experts.
My very first question/post is what people thought of a...A Used, less than 500 hour Honda EX12D 12Kw peak, 10Kw continuous, liquid cooled diesel, about $5200 USD, no tax, might be room for a little negotiation.
OR
A New Yamaha EDL11000SDE, similar to the Honda, 12Kw peak, 10Kw continuous, liquid cooled diesel - about $7200 USD tax in (no room for negotiation) which from what I can tell is a Kubota Lowboy GL1100 rebranded, and in my neck of the woods, cheaper to buy than the Kubota.
On about 80 posts, I think 1 person commented on the Yamaha being like the Kubota and another liked the Honda, about 78 posts were on I should go LP and storing diesel is bad....and so on.
If a 10-12Kw could work, I might even consider this unit
https://cdntoromontsites.azureedge....-443e-8aba-3a48560b45a1.pdf?sfvrsn=6b348ce3_2
Anyway, I hope this is enough context and if you have any advice (or anyone else) much appreciated.