It's important to understand WHY folks are asking about this.Yes - all the breakers that I didn't intentionally turn off.
Here is what I have so far - let me know if there is something else. I tried to put the male side of the inlet into the female side of the power plug again. It goes in and I can hear it kind of snap into place. when I try to turn it I can feel a very minor movement. It doesn't actually lock as I can pull it apart at that point.need to see pics of the plugs and inlets so we can figure out whats wrong. kinda hard to do so blind.




Can you provide the specific text that requires this? This technical document (random search) doesn't support your analysis. https://lightning.org/wp-content/uploads/2014/12/Tech_Letter-NFPA_54_to_Include_Bonding_8-08.pdfBonding of the gas lines is an NFPA 54 requirement, with a #6 wire. All states have adopted some form of NFPA 54 as code and there is no “likely to be energized” quote like there is in the NEC/NFPA 70 that Mike Holt is an expert on.
NFPA 54 2024..............It requires #6 for csst but not for pipe or simple tubing systems. Is the OPs HW heater the only LPG device?Can you provide the specific text that requires this? This technical document (random search) doesn't support your analysis. https://lightning.org/wp-content/uploads/2014/12/Tech_Letter-NFPA_54_to_Include_Bonding_8-08.pdf
I only referenced Mike Holt as he has a number of well accepted illustrations explaining requirements.
Where does NFPA 54 state to bond the gas piping with a #6? This is probably the fundamental question. I'm not aware of it. I do have a copy of NFPA 54 at the office, and I'll look it up. If I'm mistaken, I'll gladly acknowledge.
If the NEC and local electrical codes do not require the bond to a gas piping system that is not likely to become energized, who is required to install the #6 bond in your analysis? What is it bonded to, as specified in the fuel gas code?
You realize that the gas pipe can't be used as part of the grounding electrode system?
You realize that the equipment grounding conductor of the supply to a gas-fired appliance bonds the gas pipe? It doesn't need to be a #6?


You need to get the plug to lock on or it may fall out at some point, and/or arc the connectors.Today's testing - I put the reliance inlet stuff back together. In the process of connecting the wires I discovered a broken ground. This device has a ground from the male outlet to the enclosure box. The ground from the main panel connects at that same point. It was the ground from the enclosure back to the main panel that was broken (broke off at the ring terminal). I replaced that ring terminal and got all the wires reconnected. Plugged the power cord in - tight going in, lots of effort to get it fully seated and very little twist. I did notice that I could no longer remove the female power line from the inlet box.
First thing I did was start the generator and checked the incoming voltage at the generator breaker in the main panel. L1 to L2 - 240, L1 to N - 120, L2 to N - 120, That was an improvement - yesterday L1 to L2 was around 180. I left all the circuits on, turned off the panel main and turned on the generator breaker. Everything in the whole house worked! Then I went back and shut off the circuits I would typically not want to run in an outage - they no longer worked and the desired circuits did work.
At this point I am declaring success. I do wonder what the problem was yesterday
1. Could the broken ground have caused the issue?
2. I still don't like the way the female power cord end connects to the inlet male. It feels like it takes way too much effort to get it connected and partially locked. From what I can find the locking feature is not required for the connection to work. Maybe the effort required is because the power cord is basically new/barely used and it needs to "wear" a bit?
I purchased a new reliance inlet box - that will be going back. I also purchased a new female cord end for the power cord. I may keep that in case of an emergency.
Comments are welcome
It seems a broken ground would not disrupt circuit functionality?
As said above it is locking but very marginally - i am not at all comfortable with it.You need to get the plug to lock on or it may fall out at some point, and/or arc the connectors.
It will lock. Get someone else to try
Certainly possible although I didn't notice any loose connectionsIt shouldn't. Did messing with/fixing the ground jostle a loose connection into working properly?
I'm leaning more and more to your long shot Dave. A new female twist lock goes on very smoothly and has a very positive lock. The problem one takes a lot of effort to just get it seated and barely turns to lock. I believe it is marginally locked but it still concerns me.This is a long shot - but is there any chance the material in this plug has gotten hard or taken a set interfering with mating?
Again - long shot.


There is a seal on the new molded plug shell. My generator inlet is vertical so the cord hangs down rather than horizontalAs said above it is locking but very marginally - i am not at all comfortable with it.
Certainly possible although I didn't notice any loose connections
I'm leaning more and more to your long shot Dave. A new female twist lock goes on very smoothly and has a very positive lock. The problem one takes a lot of effort to just get it seated and barely turns to lock. I believe it is marginally locked but it still concerns me.
I have this
I'm thinking I could cut off the old receptacle and install this on the the power cord. Upside - the new one works; i.e. it inserts and has a positive lock. Down side the old one is a molded plug - the new one is obviously not molded and I have a bit of concern about outdoor use
Rick
Yes, I edited it to add the shell is molded.New plug isn't molded dave but you probably didn't mean molded![]()
@Firebrick43
Your reply should be directed to @Firebrick43. I simply pulled the relavent code for you both.The first citation, 7.12.1.1 states "likely to become energized". "likely to become energized" is if the appliance or equipment has power to it. As far as CSST, the black coated and their fittings are rated as bonding, the yellow is not. At least as of a few years ago. A natural vent gas water heater is not likely to become energized. But if one wants to bond such, as someone suggest is a good practice, then by all means.
Thank you, I didn't realize he hadn't posted the reference, I need to read more thoroughly. I appreciate the posting, the language is consistent between the 2 standards.Your reply should be directed to @Firebrick43. I simply pulled the relavent code for you both.
Imo, likely to be energized is subjective and an AHJ could easily require it. Also, it does appear in NFPA 54 just like in 70.
That is so true - at least with me. Repetition is a required stepIf you exercise your generator quarterly, I'd go ahead and run your house on it for a couple of hours each time. Any load is fine for the genny, but a little repetition on the steps to switch everything over to the generator can be a good thing. Makes it less likely you'll make a mistake if you are under pressure to get the power back on in an emergency. You will also find any issues or loads that may not be generator compatible and come up with a solution for that before it's an emergency. Your checklist is a great way to keep it straight but practice and repetition are good.
I run mine in any weather. I have the generator to get power when I need it, not just when the weather is niceThat is so true - at least with me. Repetition is a required step.
I think I'm going to cut off the female side of the power cord and replace it with the field installed connector. Buying a new 25' cord will be plan B.
A couple of questions now that things are operational -
1. Storage - I will be draining the carb, cleaning the sediment cup and draining the fuel tank. Storage will be inside my basement shop - somewhat of a controlled climate. Should I be adding anything to the fuel tank to prevent future starting problems?
2. This should "generate" some discussion - The standard recommendation is to not run the generator in an active rain/snow storm. It is somewhat likely that an outage will occur during a storm. What are you folks doing in that situation - waiting out the rain/snow, ignoring the recommendations and just running the generator, investing in a generator tent, other? My first thought was to run it from a detached shed but that is also frowned upon?
Rick
Do you have a gas stove with an electric clock/ignition/oven controls? A furnace in the house?, A dryer, or even wires that run parallel to the gas piping for a couple of feet or more and create low voltage current via induction which can cause electrolysis of the under ground piping and severe corrosion in a manner of months.@Firebrick43
The first citation, 7.12.1.1 states "likely to become energized". "likely to become energized" is if the appliance or equipment has power to it. As far as CSST, the black coated and their fittings are rated as bonding, the yellow is not. At least as of a few years ago. A natural vent gas water heater is not likely to become energized. But if one wants to bond such, as someone suggest is a good practice, then by all means.
Do you have a gas stove with an electric clock/ignition/oven controls? A furnace in the house?, A dryer, or even wires that run parallel to the gas piping for a couple of feet or more and create low voltage current via induction which can cause electrolysis of the under ground piping and severe corrosion in a manner of months.
I haven't seen a house yet that the only gas appliance is a natural vent water heater? Only thing I have seen exempt is a simple out building/shed with a pilot light ventless heater.
Hell I was shocked last year touching a gas water heater during a safety inspection due to an undersink POU 110V mini water heater element shorting out and making the pipe to the water heater in the basement hot. My multimeter confirmed. The safety ground wasn't hooked up correctly so the breaker failed to trip. Obviously neither were the pipes nor the gas line bonded back to the service entrance either. The faucet was not live due to the nylon tubing connecting it to the water heater. Most of the rest of the house had been recently replumbed in PEX and I wonder if it started leaking everywhere due to the current leakage.

The expansion tank is oriented incorrectly. The inlet/outlet should be pointed downOK - time to circle back to the water heater install. Based on the comments I am concerned. Just to summarize - unit in question
Comments from above
odd place for the regulator. good way to put too much weight on the valve box and bend it especially considering the vertical pipe is not supported AT ALL and they switched to black iron pipe.
should be copper (or black iron) pipe > regulator > drip leg on bottom of tee, shut off valve on side of tee > flex line to valve box to allow for movement..... also that copper line is not allowed in many jurisdictions... definitely get a plumber in there to fix that mess
Bonding was also an ongoing discussion
Can we discuss specific details aimed at the uninitiated (me)
Rick
I have needed mine very little, thankfully.Mike - Uncovered? Have you seen any weather related effects on the generator?
OK - time to circle back to the water heater install. Based on the comments I am concerned. Just to summarize - unit in question
Comments from above
odd place for the regulator. good way to put too much weight on the valve box and bend it especially considering the vertical pipe is not supported AT ALL and they switched to black iron pipe.
should be copper (or black iron) pipe > regulator > drip leg on bottom of tee, shut off valve on side of tee > flex line to valve box to allow for movement..... also that copper line is not allowed in many jurisdictions... definitely get a plumber in there to fix that mess
Bonding was also an ongoing discussion
Can we discuss specific details aimed at the uninitiated (me)
Rick
A good friend of mine had their mult-million dollar house burn down last year after a major storm system took out their power for 2 days. It was because the generator was located improperly in relation to the house and when the generator overheated it took the house with it. No need to skimp on that area. Keep it away from the main structure. They were home but it was at night and they were sleeping when it started. They were fortunate to survive.I don't see the fuel source affecting that. Guessing that is to prevent exhaust fumes from entering windows. Nothing magic about 20 feet IMHO although maybe they are worried about the generator catching fire. Aim the exhaust away from the house or anything it might affect and avoid placing it near open windows/doors. Basic common sense.