So I've been adding outlets in my garage when I came across this...
This is the outlet that my garage door is plugged into. It is on a 20 amp circuit and it has 12 ga Romex going to the receptacle. Everything I've read has said that the 20 amp outlets have the extra little cutout in the the slots. Do ALL 20 amp outlets have this extra little cutout? In other words, is the outlet shown above definitely a 15 amp outlet?
The house was built in 2009 if that's relevant.
This is the outlet that my garage door is plugged into. It is on a 20 amp circuit and it has 12 ga Romex going to the receptacle. Everything I've read has said that the 20 amp outlets have the extra little cutout in the the slots. Do ALL 20 amp outlets have this extra little cutout? In other words, is the outlet shown above definitely a 15 amp outlet?