Meter/Main Disconnect Remote From Drop Questions

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,208
Location
VT
Here's 3 closeup shots of the fittings...I don't like itMWTE9778.JPGQJNR5372.JPGDDTN2901.JPG

Something I learned after I did mine, face the weather head the opposite direction, so when the drop loop curls down/up its smoother.

Other then I guess he could have trimmed a bit, looks like every other install I've seen in ME or VT.
 
To avoid these ads, REGISTER NOW!

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,208
Location
VT
Are those split bolts or something else?

I'll let the other guys confirm the official name, but no, that does not appear to be a split bolt

I believe that is the same connection on my line down a few years ago in VT. They used an impact, then snapped the plastic cover over it And gave it a few wraps of tape
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,759
Location
NW Iowa
Alliant uses those dumb things around here too. No idea what their reasoning is. Cost 5x as much as a crimp and less reliable.
 
OP
M

Mr onetwo

Well-known member
Joined
Apr 6, 2011
Messages
2,010
Location
Coastal Maine
This is just a noob question but, why was I required to use 2/0 aluminum when CMP's wire is obviously a lot smaller?
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,004
Location
NJ
PoCo doesn't subscribe to NEC (you had to) and wires in free air can carry more current then wires on/in a building.
And they have reams of data that shows most services don't come close to drawing the installed capacity. Possibly the load calc could sway things but i doubt that info makes it to the lineman.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,759
Location
NW Iowa
This is just a noob question but, why was I required to use 2/0 aluminum when CMP's wire is obviously a lot smaller?
Even the NEC allows higher ampacity for wires in open air. Better heat dissipation. The utility company uses different rules than the NEC anyway.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,905
And they have reams of data that shows most services don't come close to drawing the installed capacity. Possibly the load calc could sway things but i doubt that info makes it to the lineman.
When i bought my house, we upgraded from a 100A service to 200A. We've got 4/0 aluminum from the meter to the weatherhead, where it connects to 6AWG triplex. I asked about it when they hooked it back up, and the poco guy said they do the calculation by square footage, and since the house isn't changing size, the wire doesn't need to. I don't know know if telling them what the load is goign to be would hange that, or not. They do use bigger wire on new install and repairs, though.
 

Codyboy

Well-known member
Joined
Jan 31, 2019
Messages
1,680
Location
S.E. TEXAS
Ok, why would an electrician use split bolts on a service instead of a crimp?

Split bolts are usually what you see an owner do on their own stuff, because they don't have the tool for a crimp.
Idk.
Most likely they don't carry every size crimp connector that would be needed and just use split bolts.
PoCo here uses crimp connectors and they use a battery powered hydraulic crimper... doubt those ever fail
Yes we use compression type connectors.
It wasn't until not long ago we battery type crimpers and used wood or fiberglass handle squeeze guns.
Battery operated were a godsend tool.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,905
Got to be some reason

Utilities like the burndy style constant sheer connectors for a bunch of reasons. Most of them can deal with a range of sizes, so fewer parts to carry, doesn't need a special tool. They're supposed to be more reliable, and easier to verify that they're done correctly. if the tightening bolts break off, they're tight enough, crimps need to be tested with a gauge that's specific to the particular crimp in use. If you use the wrong die, the crimp can look good, but not be right, and it works loose after a bunch of heat cycles.
 