Multiple 240v outlets on one circuit?
I think it is. #10 conductors get a #12 bond/EGC per table 16. Doesn't matter if its in a 20A or 30A circuit.
Here's the 2018 CEC: (3a and 3b most pertinent)
per 250.122, the EGC is sized the same for #14, #12, and #10.
Also a bond is not the same thing as an EGC
u2slow
BC
AntonLargiader
Charlottesville, VA
I don't know if this is exactly the same thing, but my dad's house has some sort of situation where it seems two items (the furnace and I think the pool) are apparently physically swapped on the same 240V breaker each spring and fall!! I just found out about this and am going up to investigate now because he needs his furnace hooked up again. He has lived there for about 15 years and apparently this has been going on the whole time with a friend switching wires around. This year we have been keeping the pool open longer so it has become an issue.
Given that his 240V loads each have a disconnect anyway and are therefore enabled and disabled at will, is there anything wrong with two simply being on the same breaker (if the breaker will take double taps) since he will only use one at a time?
u2slow
BC
@AntonLargiader IMHO, decide this one for yourself. You clearly understand the practical limitation. I doubt its code compliant however. (I have lots of things like that.)
I'm assuming the circuits are the same ampacity where the breaker continues to protect the conductors. Only certain breakers are approved to land 2 wires, otherwise you need a splice.
AntonLargiader
Charlottesville, VA
The compliance thing is the only thing I'm asking. I know it would be manageable. Many people here talk about using few enough items on a circuit that they wouldn't overload it. With 120V circuits we are all in that position (I can plug three vacuums and a blow dryer into one circuit any time I want) but I don't know if hard-wired 240V is the same. I could look it up but I thought I'd ask first as it seems like one of those things that deserves more context.
I don't know if this is exactly the same thing, but my dad's house has some sort of situation where it seems two items (the furnace and I think the pool) ...
Not sure what kind of furnace requires 240V !
If you put them both on the same breaker at the same time, you are violating NEC.
Onebean
Nebraska
I’m not an electrician, but I’ve been around quite a bit of wiring in my life. Electricians have always re-enforced to me that the breakers job is to protect the wire between the outlet and the breaker. Assuming your wire and breaker are sized correctly, I see no harm in pigging backing another outlet off the existing line. In the event both machines were started at the same time (typically max amp draw is on start up, once the tool is running, amp draw typically drops), the breaker would trip protecting the wiring. I might be oversimplifying it, but it seems logical to me that you could have 10 outlets on a line, as long as the breaker is sized to the wire size, not the machine amp draw.
AntonLargiader
Charlottesville, VA
Yeah, but thinking back I think there's a restriction on doing that with 240. This comes up sometimes when people ask about having several receps to allow powering a single welder from multiple spots. Been a while since I've had to think about this.
nadogail
Coronado, CA
I see no problem in having multiple outlets on a circuit as long as they don’t overload the conductors and the breaker.
Norcal
If the wiring & circuit breakers are properly sized, the worst that can happen is the breaker trips, but that applies to everything, not just multiple 240V receptacles.
u2slow
BC
Who's checking?
No permit or receipt... no record any work happened.
Real estate laws usually have a time limit on disclosure... 2 years for my jurisdiction. (Good luck proving/disproving.)