There is alot of studying when it comes to where to put these heaters. I think I have maybe failed on my first attempt. Thank God I have not starting cutting anything yet.
When I mounted the heater up in the ceiling earlier this year, I was planning on venting it horizontally. I was under the understanding that I had to be 18 inches below the soffit. Where I got this from I don't know. The manual says 4ft. That's pretty much a deal killer, because I would be over the 5 ft max length. Also lowering the vent exit through the wall puts me closer to a window.
So my next option is to go through the roof, which by the way intimidates me some. The directions are not real clear about what pieces go where. Here is were it gets interesting. My builder must have had an extra truss left over. The far side of the garage where they started are on 16" center, but when it get closer to the other side where the heater is, they are just under 10" oc. I'm wondering if I will have enough clearance and air space to run a 4" vent kit through it. Also I will have to move a little wiring. That's no big deal. Here are some pics:
If I'm reading the instructions right, it states 1" of air space for 3"-24" sizes. Which I should be ok.
I originally purchased a horizontal kit. I"m thinking I will need to purchase additional items:
roof flashing:
http://www.lowes.com/ProductDisplay...gId=10051&cmRelshp=req&rel=nofollow&cId=PDIO1
storm collar:
http://www.lowes.com/pd_373-41698-1...orm+collar&N=0&langId=-1&storeId=10151&rpp=48
Longer pipe:
http://www.lowes.com/pd_37418-41698...=1¤tURL=/pl__0__s?Ntt=b+vent&facetInfo=
Not sure if anything else is needed. I'm also concerned about the height of the pipe. The exit is on the backside of the building down towards the gutter. Its a 4X12 pitch.
I will also add that my trusses are scissor trusses, so I will have no attic access once the drywall is up.
I'm planning on contacting a neighbor of mine that runs a burner service business, but wanted to ask you guys so that I may gain some knowledge before I call him.
Let me know what you guys think. Thanks, Russ
When I mounted the heater up in the ceiling earlier this year, I was planning on venting it horizontally. I was under the understanding that I had to be 18 inches below the soffit. Where I got this from I don't know. The manual says 4ft. That's pretty much a deal killer, because I would be over the 5 ft max length. Also lowering the vent exit through the wall puts me closer to a window.
So my next option is to go through the roof, which by the way intimidates me some. The directions are not real clear about what pieces go where. Here is were it gets interesting. My builder must have had an extra truss left over. The far side of the garage where they started are on 16" center, but when it get closer to the other side where the heater is, they are just under 10" oc. I'm wondering if I will have enough clearance and air space to run a 4" vent kit through it. Also I will have to move a little wiring. That's no big deal. Here are some pics:
If I'm reading the instructions right, it states 1" of air space for 3"-24" sizes. Which I should be ok.
I originally purchased a horizontal kit. I"m thinking I will need to purchase additional items:
roof flashing:
http://www.lowes.com/ProductDisplay...gId=10051&cmRelshp=req&rel=nofollow&cId=PDIO1
storm collar:
http://www.lowes.com/pd_373-41698-1...orm+collar&N=0&langId=-1&storeId=10151&rpp=48
Longer pipe:
http://www.lowes.com/pd_37418-41698...=1¤tURL=/pl__0__s?Ntt=b+vent&facetInfo=
Not sure if anything else is needed. I'm also concerned about the height of the pipe. The exit is on the backside of the building down towards the gutter. Its a 4X12 pitch.
I will also add that my trusses are scissor trusses, so I will have no attic access once the drywall is up.
I'm planning on contacting a neighbor of mine that runs a burner service business, but wanted to ask you guys so that I may gain some knowledge before I call him.
Let me know what you guys think. Thanks, Russ
Last edited:
After looking at it for awhile the long piece of cooper doesn't bother me as much. Never mind the gutter pipe eyesore. That is getting fixed in the spring.