Anyone know of an old work box that will work with 2" thick walls?

I am adding an outlet above the kitchen counter, and the wall is 2" thick from the tile back splash
 
To avoid these ads, REGISTER NOW!
OP
P

Paulski

Well-known member
Joined
Sep 29, 2017
Messages
119
What is 2"? The thickness of the wall, the cavity, or the distance from the face of the wall to the back? There are some specialty boxes that are available.
The wall is 2" thick (tile, mortar, some sort of backer board/drywall), the cavity is is ~5 1/2" deep from the face of the tile to the back of the wall cavity
 
Last edited:

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,999
Location
Central Iowa
There are plenty. It's going to require a trip to the nearest box store. Don't forget that all kitchen counter receptacles are supposed to have GFCI protection. I don't think a GFCI receptacle will fit in a shallow box, but I've never tried.



https://www.homedepot.com/p/Carlon-...ical-Switch-and-Outlet-Box- 117RSWR/202077341

 
Last edited:

The Cobbler

Super Moderator
Staff member
Joined
Oct 24, 2013
Messages
25,966
Location
Niagara Region, Ontario, Canada
I think OP means his wall veneer is 2" thick and a 5-1/2 cavity . the issue is mounting the box to the studs.


can you get in to add some wood blocking or something to secure the box to? or secure a block by screwing from the other side of the wall to mount the box on? or mount a cleat to the back of the wall with screws to mount the box to ?
 
OP
P

Paulski

Well-known member
Joined
Sep 29, 2017
Messages
119
There are plenty. It's going to require a trip to the nearest box store. Don't forget that all kitchen counter receptacles are supposed to have GFCI protection. I don't think a GFCI receptacle will fit in a shallow box, but I've never tried.



https://www.homedepot.com/p/Carlon-...ical-Switch-and-Outlet-Box- 117RSWR/202077341

I am using a GFCI, I got a 3 1/2" deep old work PVC box, but the tabs only go back 1 1/2" so it wont reach behind the mortar to clamp. Longer screws will push the tab way past the track they ride in that keeps them vertical.

I saw the metal boxes with the plaster ears, but I don't think there is enough tile to drill and use wall anchors, plus the GFCI wouldn't fit in the box, the ground screw stuck out to far and hit the bottom of the box
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,278
Location
Coastal NJ
I am using a GFCI, I got a 3 1/2" deep old work PVC box, but the tabs only go back 1 1/2" so it wont reach behind the mortar to clamp. Longer screws will push the tab way past the track they ride in that keeps them vertical.

I saw the metal boxes with the plaster ears, but I don't think there is enough tile to drill and use wall anchors, plus the GFCI wouldn't fit in the box, the ground screw stuck out to far and hit the bottom of the box
Metal box with Madison bars. No wall anchors needed.
 

gahrajmahal

Well-known member
Joined
Dec 12, 2008
Messages
2,538
Location
Cincinnati, Ohio
I think I’d mount my GFCI in a water tight box under the sink cabinet, then daisy chain the others from there. I like the looks of that smart box. Where do you buy them?
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,999
Location
Central Iowa
I am using a GFCI, I got a 3 1/2" deep old work PVC box, but the tabs only go back 1 1/2" so it wont reach behind the mortar to clamp. Longer screws will push the tab way past the track they ride in that keeps them vertical.

I saw the metal boxes with the plaster ears, but I don't think there is enough tile to drill and use wall anchors, plus the GFCI wouldn't fit in the box, the ground screw stuck out to far and hit the bottom of the box
I misunderstood the original post, you explained it while I was making my post.

Use longer screws for the pvc box? I'd get one of these and use a longer screw. I do it with old work light boxes all the time. You could also shorten the bracket with some snips.

 
Last edited:

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,999
Location
Central Iowa
Metal box with Madison bars. No wall anchors needed.
I've seen long Madison bars that would work with two layers of drywall, but I don't think they would work with 2" wall covering. I have the standard depth on my van and I know they won't work.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,278
Location
Coastal NJ
I've seen long Madison bars that would work with two layers of drywall, but I don't think they would work with 2" wall covering. I have the standard depth on my van and I know they won't work.
Most are 1.5”. But the photo I posted are 2.5”. That might work. But if a stud is there a smart box would be good.
 
OP
P

Paulski

Well-known member
Joined
Sep 29, 2017
Messages
119
I misunderstood the original post, you explained it while I was making my post.

Use longer screws for the pvc box? I'd get one of these and use a longer screw. I do it with old work light boxes all the time. You could also shorten the bracket with some snips.

The Allied box looks like it may work with that style of clamp on the back, Thanks!
 
OP
P

Paulski

Well-known member
Joined
Sep 29, 2017
Messages
119
I was concerned the screws wouldn't go into he studs to well due to the wall thickness, but I'm thinking I could mount that box further back so it screws into the studs and add a box extender to bring it flush with the wall.

I just found this while googling box extenders, it looks like it extends the old work tab guides too so it might work with my original old work box I was trying to use

 
To avoid these ads, REGISTER NOW!

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,999
Location
Central Iowa
I was concerned the screws wouldn't go into he studs to well due to the wall thickness, but I'm thinking I could mount that box further back so it screws into the studs and add a box extender to bring it flush with the wall.

I just found this while googling box extenders, it looks like it extends the old work tab guides too so it might work with my original old work box I was trying to use

If you're on a stud, just get a regular nail on box, remove the nails, and cut the nail slots off. Then you can run your own screws through the side wherever you want to. I was doing that years before I ever saw the screw on type box.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,999
Location
Central Iowa
I didn't know the deeper style were 2-1/2". I do know that nobody around me carries them and I haven't seen any in years.
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
Technically ( I hate to cite code amongst professional electricians, but the homeowners must be made aware), screws aren't allowed inside a box unless it was designed for them like the example above. Have I ever used screws from the inside? I'll plead the 5th.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,999
Location
Central Iowa
Technically ( I hate to cite code amongst professional electricians, but the homeowners must be made aware), screws aren't allowed inside a box unless it was designed for them like the example above. Have I ever used screws from the inside? I'll plead the 5th.
Sometimes ya gotta do whatcha gotta do. It probably shouldn't be done with a fiberglass box though.

Using a drywall screw in place of a 6/32 to install a device is also a code violation but I've done it and so has everyone else.
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
Now that you bring that up, no pointed end screws can be used on any device if they enter any enclosure containing wires. Again, for the posterity should those reading in the future come across this thread about attaching a box.

I really like that box with the saddle bracket in back. Been awhile since I've seen one and there isn't one in my bin of boxes.
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,999
Location
Central Iowa
Now that you bring that up, no pointed end screws should be used on any device if they enter any enclosure containing wires. Again, for the posterity should those reading in the future come across this thread about attaching a box.
Fixed it for you. The screws don't enter the standard plastic/pvc/ fiberglass boxes. Some metal boxes and mud rings, yes, but drywall screws don't work worth a pinch of **** in those anyway. Gonna have to use longer 6/32's on those.

Anyway, I started screwing a standard two gang box to the stud after I would remove a single gang when replacing a standard light with a ceiling fan/light or putting a quad receptacle in place of a duplex. I don't believe a smart box was a thing yet and the existing hole was always too tall for an old work box. Then Arlington came out with the One Box, much more user friendly than smart boxes. I keep two vertical and one horizontal single gang, two two gang and one three and one four gang on my truck. The problem is finding them. Menards used to stock one and two gangs but switched to Southwire. I order them in by the case from the supply house. If I didn't have one, I wouldn't wait for it when I could make my own, even if it is breaking the rules a little bit.

 
Last edited:

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,999
Location
Central Iowa
I was thinking of non blunted sheet metal screws on some panels where they don't go outside the panel.
You said device. How many devices mount to panels? I see pointed sheet metal screws in panels all the time, but I don't do that one. I find it funny when a home inspector takes them out and won't put them back in. I keep a bag of Square D panel screws on hand for those $150 jobs. A Siemens or Eaton panel may not be listed for a SQD screw, but they fit.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,048
Location
NJ
I just found this while googling box extenders, it looks like it extends the old work tab guides too so it might work with my original old work box I was trying to use

Good find.
Make sure you have the correct box extender style. It appears there is an old-work box style extender (the one you want - pic on left) and also a new-work box style extender. Part #'s are very similar. Googling returns both styles under same number. You want the style with the track for the wings.
No mention of longer screws provided for the wings. May need to purchase separately?
1690756766167.png VS. 1690757242654.png

Worst case, go back to a steel old work box and cut your own dog ears long enough for the job.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
Sometimes ya gotta do whatcha gotta do. It probably shouldn't be done with a fiberglass box though.

Using a drywall screw in place of a 6/32 to install a device is also a code violation but I've done it and so has everyone else.
I use a thread insert, Heli-Coil is one brand, on plastic boxes so that the OEM screws can still be used.
 

u2slow

Well-known member
Joined
Nov 20, 2011
Messages
3,611
Location
BC
I would probably go for a 4x4" metal box and extension. Screws from the inside into a stud. Use a flat mud ring and a square cover plate. If desired, use 2 gang equivalents for 2 devices.

Screenshot_20230730-163144-601.pngScreenshot_20230730-163550-996.png
 

sparky 1971

Well-known member
Joined
Oct 9, 2018
Messages
7,999
Location
Central Iowa
I use a thread insert, Heli-Coil is one brand, on plastic boxes so that the OEM screws can still be used.
I've never seen heli coils that small, but never looked either. I haven't used very many drywall screws for devices, usually on a worn out fiberglass box, but I think every smoke detector I have ever installed (1000's) has been mounted to a single gang box with two 1-1/4 drywall screws.
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,769
I've never seen heli coils that small, but never looked either. I haven't used very many drywall screws for devices, usually on a worn out fiberglass box, but I think every smoke detector I have ever installed (1000's) has been mounted to a single gang box with two 1-1/4 drywall screws.
Not easy to find, needed 8-32 inserts for a Rockwell 1"X42" sander grinder that a screw holding the motor fan shroud had sheared off on & finally found it at one of the local NAPA branches. Not sure I have enough of the sanders though, have 3 1/2 of them, & hard to find parts for.
 

Zeke

Well-known member
Joined
Aug 13, 2009
Messages
17,176
Location
Long Beach CA, the sewer by the sea.
I bought a metal lathe from a guy that used to work on model airplane motors. The sellers gave me most of the tooling some of which I never had ID'd. In the mess were many tiny insert coils for those motors. AND the tool to run them in.

Sorry Sparky, I don't always get the terminology right. and I forgot to mention I was speaking of the covers on panels, outside and deadman. I think there are a lot of incorrect deadman cover screws out there.
 

SlappyWhite

Well-known member
Joined
Oct 3, 2012
Messages
1,819
Location
Upper Canada
Do you have anything like these available?

1690813161286.png

They are pushed in and they spring open inside the wall. You then tighten the centre screw (between the ground screws) to lock it in, they are very solid once mounted. May work with the current wall thickness, if not just use a longer middle screw.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,278
Location
Coastal NJ
I've seen long Madison bars that would work with two layers of drywall, but I don't think they would work with 2" wall covering. I have the standard depth on my van and I know they won't work.
Just for completeness, here is the link to deep Madison bars. As always YMMV.
That said, there are other viable solutions in this thread that would work well.

 