Opener receptacle placement

va72mlibu

Member
Joined
Mar 14, 2018
Messages
14
Location
Alexandria, VA
Just starting the electrical rough-in. I will use a standard trolley opener on a 16x9' door. Is there a standard for where to place the box for the opener receptacle? I was thinking of adding 3' to the end of the door when up?
 
To avoid these ads, REGISTER NOW!

Hot Rod Grampa

Well-known member
Joined
Jul 7, 2017
Messages
812
Location
Near Cooperstown New York
Opener rail plus 3', since there is no 9' rail it will be a 10' so 13' back from the header and 12" off center. You don't want the outlet to end up buried by the opener. Assuming you are placing the opener in the center of the door.
 
OP
V

va72mlibu

Member
Joined
Mar 14, 2018
Messages
14
Location
Alexandria, VA
Opener rail plus 3', since there is no 9' rail it will be a 10' so 13' back from the header and 12" off center. You don't want the outlet to end up buried by the opener. Assuming you are placing the opener in the center of the door.

Yes the opener will be centered. This is great info, I never would have thought to place off center, thanks.
 
To avoid these ads, REGISTER NOW!

Barnabas

Well-known member
Joined
Nov 24, 2013
Messages
362
Location
Raleigh, NC
It could be a gfci receptacle, gfci breaker, or you could mount a blank face gfci on the wall of the garage.
 

exranger06

Well-known member
Joined
Aug 9, 2015
Messages
1,686
Location
CT
You're talking breaker not receptacle, right? Since it's up high?

The receptacle on the ceiling cannot be a GFCI, correct. However, you can connect it to another GFCI receptacle upstream that's located in an accessible location.
 

tfi racing

Well-known member
Joined
Apr 19, 2008
Messages
2,907
Location
Cedar,BC
Just to muck this up, how about moving your tracks up to the ceiling and using a wall mounted opener so you don't have to look at all that junk hanging in the middle of your shop...
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,906
Connect it to the load side of a GFCI that is accessible. No do not put the gfci on the ceiling.

GFCI is cheaper than a gfi breaker.

"readily accessible", which means you don't need tools (other than a key) or a ladder or have to move installed equipment. Accessible just means you can get to it without demolition. The outlet for opener on the ceiling is accessible, but not readily accessible.
 
OP
V

va72mlibu

Member
Joined
Mar 14, 2018
Messages
14
Location
Alexandria, VA
Just to muck this up, how about moving your tracks up to the ceiling and using a wall mounted opener so you don't have to look at all that junk hanging in the middle of your shop...

I hadn't seriously considered that (mostly just due to unfamiliarity), but I think I may go that route...
 
OP
V

va72mlibu

Member
Joined
Mar 14, 2018
Messages
14
Location
Alexandria, VA
Just to muck this up, how about moving your tracks up to the ceiling and using a wall mounted opener so you don't have to look at all that junk hanging in the middle of your shop...

I owe you a beer. I already ordered my wall mount opener. It solved a bunch of other problems. Cheers!
 