Panels for a 400 amp service

OP
B

Bigredford

Well-known member
Joined
Oct 31, 2018
Messages
193
Location
Hull Ga
again how often are you going to use 60hp worth of **** at once? what does american rotary say their most popular size is? why is that the case?

I haven't asked. But I thought id look at getting either a 40 or a 60.

This is starting as a hobby shop but my goal is self employment. :)

Anything smaller then a 40 won't run my big welder.
 
To avoid these ads, REGISTER NOW!

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,858
I haven't asked. But I thought id look at getting either a 40 or a 60.

This is starting as a hobby shop but my goal is self employment. :)

Anything smaller then a 40 won't run my big welder.

how often are you welding 2" steel in a single pass? :eek:


Look i'm all for overkill now. My vote is dual 60hp's just cause. but its not my money. :rocker:
 
OP
B

Bigredford

Well-known member
Joined
Oct 31, 2018
Messages
193
Location
Hull Ga
Maybe this will work....

Meeting with a electrician tomorrow afternoon
 

Attachments

  • received_116492707067031.jpg
    received_116492707067031.jpg
    80.7 KB · Views: 78

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,734
Location
NW Iowa
You have to try to make it that ugly.

Gutter should have gone under the meter and both disconnects.

Can't tell what kind of connector you used on top of the gutter. Needs to keep out water.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,021
Location
Modesto, CA
damn thats gonna be real fun bending the wire through those 2 LBs

Id get rid of the LBs, move the main disconnects over closer to the meter pan and move the gutten under the meter pan. then drop a pipe from the meter pan to the gutter.

youll thank me later
 

Mthomas1686

Well-known member
Joined
Sep 28, 2020
Messages
84
Location
My house, New Jersey
I do not have a massive rpc but did do a cl320 meter and "400amp service. 200amp panel in the house and the garage. All this work was done by an electrician.
 

Attachments

  • 20201222_153259.jpg
    20201222_153259.jpg
    93.9 KB · Views: 57
  • 20201223_124923.jpg
    20201223_124923.jpg
    78.3 KB · Views: 57
  • 20201229_131244.jpg
    20201229_131244.jpg
    146.4 KB · Views: 35
  • 20210114_165858.jpg
    20210114_165858.jpg
    73.7 KB · Views: 39

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,734
Location
NW Iowa
Sorry if we came down a little hard. This is one of those things were experience goes a long way. I can't speak for everybody but I'm still happy to answer questions.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,734
Location
NW Iowa
I do not have a massive rpc but did do a cl320 meter and "400amp service. 200amp panel in the house and the garage. All this work was done by an electrician.

Had to laugh at the second picture. You might be putting in a 400 amp service but the utility company knows that the real load isn't squat. 500? MCM tied to #4 or maybe#2 overhead
 

Mthomas1686

Well-known member
Joined
Sep 28, 2020
Messages
84
Location
My house, New Jersey
Had to laugh at the second picture. You might be putting in a 400 amp service but the utility company knows that the real load isn't squat. 500? MCM tied to #4 or maybe#2 overhead

Seriously its crazy they didn't up the wire size....its 400mcm to I believe #4 overhead. And its tied to my neighbors house from the transformer across the street (about 200' away). I was hoping they would come back and up the wire size.
 
OP
B

Bigredford

Well-known member
Joined
Oct 31, 2018
Messages
193
Location
Hull Ga
Had a electrician out today to qote doing some work.

Basicly fix what I've done outside. Wire everything up from the meter to the disconnects to my main panels.

Ground rods and ground the building frame.
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,858
Do they even follow NEC on sizing for those? I thought utilities had their own rules past the weather head?
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,734
Location
NW Iowa
They mostly follow NESC. If it really needed 400A they'd probably be somewhere around 2/0-4/0 aluminum.

Thing is they know his load isn't even close to 400A. I bet most of the time it's under 100A.

When I'm replacing a service I usually end up putting in a 200A. Hardly ever enough load to actually need it but the cost difference isn't much. The utility company will ask if you're adding any load. unless there is something substantial they're not changing anything on their end. Really no reason to.
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,858
free air offers a lot of cooling on the lines. I get it. makes sense to not swap if not really needed.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,734
Location
NW Iowa
free air offers a lot of cooling on the lines. I get it. makes sense to not swap if not really needed.

I replaced a service a few years ago. It was overloaded and burned up a 400 amp pole top switch. Ended up just bypassing it to get through the fall and put in a 600 in the spring.

The old 400A was fed with #4 AL. That wire had got pretty toasty. The plastic insulators were melting off the crimps and the insulation was drooping in a few spots.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,894
When I'm replacing a service I usually end up putting in a 200A. Hardly ever enough load to actually need it but the cost difference isn't much. The utility company will ask if you're adding any load. unless there is something substantial they're not changing anything on their end. Really no reason to.

when I bought my house, we had the service upgraded to 200A. Utility has a formula, based on square footage, that says what the load is going to be, and based on that, the wire they use to feed the house. That means they left the #6 triplex. (They will replace if the actual usage warrants, but usually that's after it's melted and shorted.) Looks pretty silly spliced to the 4/0 NEC requires for the customer size, but since I'm pretty sure the highest actual load has been less than 100A, I'm sure they're right about it.
 

mike93lx

ALLIANCE MEMBER
Joined
Dec 9, 2013
Messages
37,575
Location
Richmond, VA
when I bought my house, we had the service upgraded to 200A. Utility has a formula, based on square footage, that says what the load is going to be, and based on that, the wire they use to feed the house. That means they left the #6 triplex. (They will replace if the actual usage warrants, but usually that's after it's melted and shorted.) Looks pretty silly spliced to the 4/0 NEC requires for the customer size, but since I'm pretty sure the highest actual load has been less than 100A, I'm sure they're right about it.

My last house had 60a service. Electric dryer, electric range, two fridges, three sump pumps, two portable a/c's, a dehumidifier, computers, tvs, etc.

Never once had any issue.

My current house has 100a service, but even with two fridges, a freezer, some lights, my furnace and my well pump.running, I am pulling only 5kw per the meters on my generator inlet.

When I had that panel replaced, I thought about going up to 200a until the utility told me they would be changing exactly nothing. The extra cost on my end was a waste then.

People tend to grossly over estimate their needs.
 
To avoid these ads, REGISTER NOW!

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,858
My last house had 60a service. Electric dryer, electric range, two fridges, three sump pumps, two portable a/c's, a dehumidifier, computers, tvs, etc.

Never once had any issue.

My current house has 100a service, but even with two fridges, a freezer, some lights, my furnace and my well pump.running, I am pulling only 5kw per the meters on my generator inlet.

When I had that panel replaced, I thought about going up to 200a until the utility told me they would be changing exactly nothing. The extra cost on my end was a waste then.

People tend to grossly over estimate their needs.

i highly suggest power monitoring for people if they are curious. i use myeyedro

I can roll back to consumption at any point in time. heres a lovely summer day.
https://i.imgur.com/aZBL2V2l.png
 
OP
B

Bigredford

Well-known member
Joined
Oct 31, 2018
Messages
193
Location
Hull Ga
Sorry if we came down a little hard. This is one of those things were experience goes a long way. I can't speak for everybody but I'm still happy to answer questions.

No your fine. I need the advice. :beer:

I learned today what Myers hubs are. Didn't know they existed.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,894
When I had that panel replaced, I thought about going up to 200a until the utility told me they would be changing exactly nothing. The extra cost on my end was a waste then.

People tend to grossly over estimate their needs.

100A would have been enough, but here wasn't a panel with the number of spaces required that comes with a 100A main installed, so it would have meant buying a 200A panel, and changing the main. As I recall, that was about the same as the difference in wire, and the only difference was the size of conduit installed between the panel to the weatherhead. The cost difference was less than $200, on a job that cost many thousands (total rewire).
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,858
The picture does not load

aZBL2V2.png


how about this?


edit humm
https://i.imgur.com/aZBL2V2.png
 

jeepxj

Well-known member
Joined
Mar 2, 2008
Messages
17,858
good. thats the photo of a nice june or july day at my place.
 

86turbodsl

Well-known member
Joined
Jul 1, 2005
Messages
6,558
Location
Michigan
My opinion, but i don't think there's much a single guy in a hobby shop can do without multiple CNC machines running that could use up a 60hp RPC. Even your air compressor is overkill. 20hp. No way a single guy working could use that much air by himself. If all your machines are manual, consider sizing your rpc and service down. I used to have a 50hp rpc, and it was overkill. Most of my machines are manual and i'm down to a 20hp rpc. There just aren't any machines big enough to need that kind of capacity unless you are running some GIANT stuff in your hobby shop.
 
OP
B

Bigredford

Well-known member
Joined
Oct 31, 2018
Messages
193
Location
Hull Ga
Interesting. I've always been told you need your phase converter to be 2x the largest motor.

The 400 amp service is a done deal at this point.
 

Bert_

Well-known member
Joined
Dec 24, 2016
Messages
9,734
Location
NW Iowa
Interesting. I've always been told you need your phase converter to be 2x the largest motor.

The 400 amp service is a done deal at this point.

Really depends on the phase converter and the load. I've ran a 75hp motor on a 60hp phase converter before (60hp idler, rated to run 120hp total). I would absolutely not recommend doing that but it was an existing phase converter and it worked other than the soft start occasionally kicking out on phase loss during startup. Eventually the bearings got bad in the converter and I convinced the guy to get a bigger phase converter.
 

aussieblake

Active member
Joined
Dec 26, 2013
Messages
34
I apologize as I did not read through all the responses. In my experience in the electrical industry as an electrical contractor and as a electrical design professional, you probably need to have a supply house quote you a custom panel. Most single phase stock panels have a limit branch mounted breaker size limitation of 100 amps, some manufacturers will actually allow a 110 amp breaker for BRANCH MOUNTED, Branch mounted refers to same space as say a 20 amp breaker. When you get above the branch mounted breaker limitation it becomes SEPARATELY MOUNTED, which is similar to when the MAIN breaker is mounted separately above or below the branch breakers. The terms Branch mounted and Separately mounted are what the industry uses. I write specifications for large projects, those are the terms in the software, and as an electrician it makes logical sense. If you need help with what to ask for feel free to PM me. It is pretty simple if you are familiar with the nomenclature. Just an FYI this is not going to be a $300 panel. You are into the commercial style panels with you have large separately mounted mains. Also figure out all the breakers you want for it, add some spares, because pricing a panel and breakers makes the breakers less expensive then buying the off the shelf.
 