I will be replacing my old forced hot air up-flow furnace shortly with a new furnace that I have waiting in the wings. New furnace will sit on 4" concrete blocks which creates some ductwork adjustments in the return. New plenum is already made.
In reviewing my existing EAC against new units, I see today's models have post-filters as an option. My existing unit at the time made no mention of such. My unit had typical provisions for locating the pre-filters left or right of cells depending on air flow.
The new units mention an ionized surface filter to collect the finer particles that make their way thru the EAC and use the un-used pre-filter position. This style of post filter seems more like a revenue stream than a practical approach for manageable filtration.
Without putting an offset into the return duct, I don't have room to add a new media filter between EAC and furnace. I do however have a 4" wide spacer between furnace and EAC now.
Instead of dealing with more sheet metal work, I was thinking I could use the 4" space between the furnace and EAC to insert a 2" thick MERV 11 or 13 filter. I could support it on both sides with 4 removable rods on either side of the MERV filter. MERV filter replacement access would require removing the EAC cells. Not a problem as I should be cleaning the cells and this would get me moving on it.
I plan to put a delta P sensor on both sides of the EAC and on both sides of the MERV filter so I get an alarm when either is blocked. I will adjust the fan speed during furnace install. (The original media filter that was replaced with the EAC was for 1200 CFM and the current EAC is rated for 1600 - 2000 CFH. This size was chosen to nicely fit the ductwork size. The MERV filter would be 20" x 25" x 2".)
Thoughts? Pros/cons? Should I do the return duct offset instead to install a 4" thick MERV instead?

In reviewing my existing EAC against new units, I see today's models have post-filters as an option. My existing unit at the time made no mention of such. My unit had typical provisions for locating the pre-filters left or right of cells depending on air flow.
The new units mention an ionized surface filter to collect the finer particles that make their way thru the EAC and use the un-used pre-filter position. This style of post filter seems more like a revenue stream than a practical approach for manageable filtration.
Without putting an offset into the return duct, I don't have room to add a new media filter between EAC and furnace. I do however have a 4" wide spacer between furnace and EAC now.
Instead of dealing with more sheet metal work, I was thinking I could use the 4" space between the furnace and EAC to insert a 2" thick MERV 11 or 13 filter. I could support it on both sides with 4 removable rods on either side of the MERV filter. MERV filter replacement access would require removing the EAC cells. Not a problem as I should be cleaning the cells and this would get me moving on it.
I plan to put a delta P sensor on both sides of the EAC and on both sides of the MERV filter so I get an alarm when either is blocked. I will adjust the fan speed during furnace install. (The original media filter that was replaced with the EAC was for 1200 CFM and the current EAC is rated for 1600 - 2000 CFH. This size was chosen to nicely fit the ductwork size. The MERV filter would be 20" x 25" x 2".)
Thoughts? Pros/cons? Should I do the return duct offset instead to install a 4" thick MERV instead?




)