sparky 1971
Well-known member
I'm not betting on it but it sure looks like a modular home with a crawl space to me. If I'm right, the panel is more than likely going to be a PITA. The few I've dealt with were ridiculous, the last one being a 200 amp 16 space Siemens completely full of twins and quads from the factory and no place to add another breaker. On top of that, every effing cable enters through the bottom and there are no knockouts left to bring anything in if there is a space.I'd put money that the panel is probably in the basement right below that meter main combo. If i was doing this job id just add a breaker in the main panel and from the basement stub out into a box then down underground with an expansion fitting into the garage. I'd use a panel with a main.. and dont forget the uffer ground or ground rod or rods ... otherwise you would need to add a splice box next to the existing meter main and run from the load side of that exterior main breaker into the box and then down to the main panel and use the tap rule to tap and add fused disco or a small 2/4 3r panel with the appropriate breaker size within 10' of the tap. Sounds easier to just run the work from inside!