Holeshot
Active member
Here's a few tidbits about the garage:
Attached, stick-built structure 32'x40'x13.5'
4" slab
6 loops of 1/2" oxygen barrier PEX (~1200' total)...probably should have done 4 loops...
PEX was Malco stapled to 2" 25 PSI EPS insulation under the slab
There is also 2" EPS around the perimeter of the slab where it meets the foundation/frost walls.
R15 fiberglass in the walls and I will be blowing 12-18" of celluose in the attic very soon.
Columbia County, WI - it's chilly in the winter to say the least.
Heat source:
Takagi T-H3M-DV-P
15k-120k modulating, condensing and rated for space heating
Primary/secondary loop:
Two Grundfos 15-58FC circulators
Type-L copper throughout
Webstone primary/secondary purge valves
Webstone flange valves
3/4" Spirovent
Amtrol RX-15
Embassy manifolds (bought these way back in 2008 on a friend's recommendation)
Very rough heat loss calcs were between 45-75k BTU.
I have 60% Cryo-Tek -100 glycol in the system because I travel for work fairly regularly and can't risk letting it freeze/burst if we lose power or system malfunctions.
I first fired it about a week ago and let it run for a while with the Takagi set to temps between 100-115°F. As expected, it took forever and a day (4-6 hours?) to bring the return temps from ~40°F to 70°F.
With the Webstone purge tee/valve open, I had a hard time getting the supply temp to 80°F. With it closed (as seen in the picture), the supply to the loops is very close to the output temp of the Takagi.
Second Webstone purge tee was added for future use, but with the return temp of the floor overwhelming the primary loop, I'm not sure how viable this will be.
I've tried running both 15-58FC's on all 3 speeds...the maximum flow with both on 'High' as reported on the Takagi's readout is ~2.4 GPM. With the Webstone purge tee/valve open, it drops to about 1.8 GPM. I'm not sure how accurate this flow meter is, nor am I familiar with what kind of flow I should be seeing in the primary loop.
What am I doing wrong?
What do you guys typically run for supply temp?
I'm getting fairly consistent ΔT of ~20°F
The slab will get very slightly warm to the touch after running many hours...perhaps I just need to let it run longer...?
Note: thermal image was taken not long after system was fired off and with the Takagi set to 100°F...it was modulated very low...draft inducer speed and burner changes instantly on demand.
Many thanks in advance for your assistance!
Beers,
Matt
Attached, stick-built structure 32'x40'x13.5'
4" slab
6 loops of 1/2" oxygen barrier PEX (~1200' total)...probably should have done 4 loops...
PEX was Malco stapled to 2" 25 PSI EPS insulation under the slab
There is also 2" EPS around the perimeter of the slab where it meets the foundation/frost walls.
R15 fiberglass in the walls and I will be blowing 12-18" of celluose in the attic very soon.
Columbia County, WI - it's chilly in the winter to say the least.
Heat source:
Takagi T-H3M-DV-P
15k-120k modulating, condensing and rated for space heating
Primary/secondary loop:
Two Grundfos 15-58FC circulators
Type-L copper throughout
Webstone primary/secondary purge valves
Webstone flange valves
3/4" Spirovent
Amtrol RX-15
Embassy manifolds (bought these way back in 2008 on a friend's recommendation)
Very rough heat loss calcs were between 45-75k BTU.
I have 60% Cryo-Tek -100 glycol in the system because I travel for work fairly regularly and can't risk letting it freeze/burst if we lose power or system malfunctions.
I first fired it about a week ago and let it run for a while with the Takagi set to temps between 100-115°F. As expected, it took forever and a day (4-6 hours?) to bring the return temps from ~40°F to 70°F.
With the Webstone purge tee/valve open, I had a hard time getting the supply temp to 80°F. With it closed (as seen in the picture), the supply to the loops is very close to the output temp of the Takagi.
Second Webstone purge tee was added for future use, but with the return temp of the floor overwhelming the primary loop, I'm not sure how viable this will be.
I've tried running both 15-58FC's on all 3 speeds...the maximum flow with both on 'High' as reported on the Takagi's readout is ~2.4 GPM. With the Webstone purge tee/valve open, it drops to about 1.8 GPM. I'm not sure how accurate this flow meter is, nor am I familiar with what kind of flow I should be seeing in the primary loop.
What am I doing wrong?
What do you guys typically run for supply temp?
I'm getting fairly consistent ΔT of ~20°F
The slab will get very slightly warm to the touch after running many hours...perhaps I just need to let it run longer...?
Note: thermal image was taken not long after system was fired off and with the Takagi set to 100°F...it was modulated very low...draft inducer speed and burner changes instantly on demand.
Many thanks in advance for your assistance!
Beers,
Matt