Well, the latest update is as follows;
I contacted the manufacturer and suggested it could be an opportunity to send me a replacement unit as what I have maybe faulty.

They did not agree, but have continued to offer programming adjustments that have been of no consequence.

There is definitely a problem with something whether it be my motor or there unit, but I do fail to see how my motor at one time did run at the setting programmed prior to going remote.

The part of the equation is the language barrier, whereby they are using a young non technical girl to translate my comments and feedback to the Tech.

Since going remote the issues came into play.
I have tried as they suggested to go back to the panel control, but for now the issue remains with binding to a full stall.

I have taken the initiative for now and have advised them, that I plan to rest the upper speed limit from 120hz down to 87hz.
The motor starts to bind at about 90hz and grinds to a halt by 120hz.
Sadly, this limits my top speed which was factored into my original mechanical gearing, so I have elected to try and increase the size of one of my small sprockets to try and regain some top speed that way.

I guess we have parted friends as they are just employees in this massive corporation and have limited capacity to deal.
The girl did say that should she or the Tech ever determine a similar fault or a solution that may also be a possible help to me that they would email me to advise me of any program ideas, I guess like a bulletin.

So for now at least I have a solution that should work for me but no thanks to my manufacturer.
Should the opportunity arise I may consider doing a swap later to a more widely used and reliable brand, but for now I will just run with my plan B solution...
 

laser3kw

Well-known member
Joined
Nov 17, 2012
Messages
7,276
Location
northen IL
there is a function in the vfd to "reset to factory parameters".
maybe give that a try and start over just operating of key pad, then add in each tweek?:headscrat
 

fiftyv8

Well-known member
Joined
Dec 29, 2018
Messages
237
Location
Perth
Just an update for those who maybe interested and here is hoping I am not being premature in say that I have good news.
I sat down and went thru another parameter check which included considering the numbers that were offered up yesterday by a very helpful and persistent forum member.
It would seem by changing;
F00.00 = 2 and by setting
F00.03 & F00.04 = 120hz and setting
F00.07 = 0
My motor will run all the way upto 120hz without a problem.
Similarly, it sits on 20hz at lower limit until foot pedal is released.

I can not believe how simple that was to solve in the end.
I guess we knew it was probably just some annoying glitch.
You just don't know how happy I am to be done with that problem.
 
Joined
Jan 12, 2019
Messages
8
Location
Mooresville, IN
Hey folks. I apologize if this has already been mentioned but there are a metric $&?! Ton of posts. VFD produce a buildup of rotor current that is discharged through the bearings particularly at frequency less than 30 hz. This may not be a factor considering run hours of shop equipment. But in motors running continuous I can document bearing failures because of running on a freq drive without rotor grounding. If you’re only using the equipment a limited number of hours don’t worry, it’s just food for thought.


Sent from my iPhone using The Garage Journal mobile app
 

fiftyv8

Well-known member
Joined
Dec 29, 2018
Messages
237
Location
Perth
Thanks for your comments and good intentions.

Funny thing is I don't generally ever expect to get down to such a low speed and had been considering raising my setting from 20hz upto approx 30hz just for reducing the risk of things going wrong.
 

slodat

ALLIANCE MEMBER
Joined
Feb 6, 2010
Messages
3,679
Location
Central-ish, WA
check to see if there is a control parameter that turns the brake function on / off. You should see a voltage when it is dumping to the resistor.
It may be set to "coast to stop" which inhibits the brake.
PS - I just noticed the drum switch which seems to have connection between the motor and the VFD? If so I hope you are not using it to interrupt the power from the VFD and the motor (on /off - forward / reverse). That will lead to VFD failure.
Or did you run both high (motor) and low voltage (vfd 10v dc control functions on/off- forward/ reverse) in the same conduit?

It's still tripping the VFD on motor stop. The drum switch is the start input to the drive. I just ran the conduit that way to keep things a little cleaner.

For the life of me I'm not seeing any setting to change to get the braking enabled, that aren't already enabled. Either I'm missing something (most likely) or the braking ***** for this large rotating mass..? I welcome any input on this braking issue. Maybe I need a different drive?
 

MattT

Well-known member
Joined
Feb 20, 2010
Messages
3,201
For the life of me I'm not seeing any setting to change to get the braking enabled, that aren't already enabled. Either I'm missing something (most likely) or the braking ***** for this large rotating mass..? I welcome any input on this braking issue. Maybe I need a different drive?

When in the decel ramp is the drive faulting?

What fault is the drive displaying?

What are F14 thru' F17 set to?

Regards large mass how fast are you able to accelerate up to speed? With 100% braking capability you should be able to decel at close to the same rate as accel.
 

454ragtop

Well-known member
Joined
Mar 24, 2008
Messages
5,010
Location
Carver, MA
It's still tripping the VFD on motor stop. The drum switch is the start input to the drive. I just ran the conduit that way to keep things a little cleaner.

For the life of me I'm not seeing any setting to change to get the braking enabled, that aren't already enabled. Either I'm missing something (most likely) or the braking ***** for this large rotating mass..? I welcome any input on this braking issue. Maybe I need a different drive?

Try increasing the deceleration time, most likely not enough internal braking capacity to stop it as soon as you have it set. If you need a quick stop, probably have to add an external braking resistor.
 

laser3kw

Well-known member
Joined
Nov 17, 2012
Messages
7,276
Location
northen IL
It's still tripping the VFD on motor stop.

When in the decel ramp is the drive faulting?

What fault is the drive displaying?

What are F14 thru' F17 set to?

Regards large mass how fast are you able to accelerate up to speed? With 100% braking capability you should be able to decel at close to the same rate as accel.
^^^^^
What fault is the drive displaying?
OCd?
OCb?
OVC?
F14 ~F17 are the braking function. The manual shows default should be controlled stop.
what size is your braking resistor and what terminals is it hooked up to?
I went back to SloDat's post #522 which shows an external braking resistor ( although it is inside the enclosure).
Later SloDat stated moving the decel to 90 seconds got rid of the fault on stop. And the resistor was not building any heat after multiple stop events.

PS- page 63 of the manual shows, depending on VFD model, there may not be a braking circuit requiring an external braking resistor.
 
Last edited:

MattT

Well-known member
Joined
Feb 20, 2010
Messages
3,201
Later SloDat stated moving the decel to 90 seconds got rid of the fault on stop. And the resistor was not building any heat after multiple stop events.

I remember now. Just skimmed back earlier to find out what drive. No heat and no DC voltage going to the resistor.

PS- page 63 of the manual shows, depending on VFD model, there may not be a braking circuit requiring an external braking resistor.

Manual I've got doesn't show the chopper as optional. It's built in to the 2 HP and larger, which SloDat appears to have, and not available on 1 HP and fractional. Though it's certainly possible the drive doesn't have a chopper if it's an OEM special or something.
 

laser3kw

Well-known member
Joined
Nov 17, 2012
Messages
7,276
Location
northen IL
I remember now. Just skimmed back earlier to find out what drive. No heat and no DC voltage going to the resistor.



Manual I've got doesn't show the chopper as optional. It's built in to the 2 HP and larger, which SloDat appears to have, and not available on 1 HP and fractional. Though it's certainly possible the drive doesn't have a chopper if it's an OEM special or something.
Can SloDat post the model numer so we can check the manual?
I took a stab at it from the picture and searched for a Teco fm50
 

MattT

Well-known member
Joined
Feb 20, 2010
Messages
3,201
Can SloDat post the model numer so we can check the manual?
I took a stab at it from the picture and searched for a Teco fm50

It definitely looks like a large frame FM50 which should have the chopper according to the documentation I've got. Would be good to have the drives full model # though.

3A%2F%2Fwww.garagejournal.com%2Fforum%2Fshowthread.jpg
 

Attachments

  • 3A%2F%2Fwww.garagejournal.com%2Fforum%2Fshowthread.jpg
    3A%2F%2Fwww.garagejournal.com%2Fforum%2Fshowthread.jpg
    114 KB · Views: 0

slodat

ALLIANCE MEMBER
Joined
Feb 6, 2010
Messages
3,679
Location
Central-ish, WA
F01: Accel time: 5 sec
F02: Decel time: 90 sec
F14: Stop Method: 0 (controlled deceleration stop)
F15: DC Braking Time: 0.5 s
F16: DC Braking injection freq: 3.0
F17: DC Braking Level: 15.0

Model is FM50-202 - 2HP, 7.5A, single/3 phase input.

cf5310dc3104f1af92422cd1c4d70bca.jpg
 

Attachments

  • cf5310dc3104f1af92422cd1c4d70bca.jpg
    cf5310dc3104f1af92422cd1c4d70bca.jpg
    270.4 KB · Views: 0

laser3kw

Well-known member
Joined
Nov 17, 2012
Messages
7,276
Location
northen IL
F01: Accel time: 5 sec
F02: Decel time: 90 sec
F14: Stop Method: 0 (controlled deceleration stop)
F15: DC Braking Time: 0.5 s
F16: DC Braking injection freq: 3.0
F17: DC Braking Level: 15.0

Model is FM50-202 - 2HP, 7.5A, single/3 phase input.

cf5310dc3104f1af92422cd1c4d70bca.jpg

Thanks
That confirms that it does have the braking circuit. It also show that it requires a "FM100-2BR2 resistor 150 watt, 100 ohm. Is that the correct specs for the resistor shown in the pics? And connected to terminal "P" and "R"?
 

Attachments

  • cf5310dc3104f1af92422cd1c4d70bca.jpg
    cf5310dc3104f1af92422cd1c4d70bca.jpg
    120.4 KB · Views: 0

slodat

ALLIANCE MEMBER
Joined
Feb 6, 2010
Messages
3,679
Location
Central-ish, WA
From the invoice:

DBR-2002-C1TECO Dynamic Brake Resistor, 230V, 2HP **JNBR-150W100**$20.00

I’ll double check the terminal connections tonight. Last night the damn thing start/stopped about 6 times with no trip. I’d like it stop it a lot faster. I’m willing to buy a different vfd to get it stopping faster if anyone has a solid recommendation.
 

laser3kw

Well-known member
Joined
Nov 17, 2012
Messages
7,276
Location
northen IL
From the invoice:

DBR-2002-C1TECO Dynamic Brake Resistor, 230V, 2HP **JNBR-150W100**$20.00

I’ll double check the terminal connections tonight. Last night the damn thing start/stopped about 6 times with no trip. I’d like it stop it a lot faster. I’m willing to buy a different vfd to get it stopping faster if anyone has a solid recommendation.

I see know reason it shouldn't
I have much bigger / mass and am stopping in program decal in the 1 second range.
 

slodat

ALLIANCE MEMBER
Joined
Feb 6, 2010
Messages
3,679
Location
Central-ish, WA
I see know reason it shouldn't
I have much bigger / mass and am stopping in program decal in the 1 second range.

Tonight I'll change F02 to 10 seconds, which is what I would like to have for a stop time. Do you suggest changing any of the braking settings?
 

laser3kw

Well-known member
Joined
Nov 17, 2012
Messages
7,276
Location
northen IL
Tonight I'll change F02 to 10 seconds, which is what I would like to have for a stop time. Do you suggest changing any of the braking settings?

try cutting your decel down as far as you can with no fault. Then set your
f14 = 0
f15 - 1.0
f16 = 5 (** play with this a little may help - values 1-10 sec)
f17 = 8
 
To avoid these ads, REGISTER NOW!

laser3kw

Well-known member
Joined
Nov 17, 2012
Messages
7,276
Location
northen IL
rotary wire straightening arbor spinning around 6000rpm.
Also the reciprocating cutting arm cycles in and out in under a second
 

slodat

ALLIANCE MEMBER
Joined
Feb 6, 2010
Messages
3,679
Location
Central-ish, WA
Lowered decal to 60 and it tripped on "OL1" - motor overload.

The motor is listed as "2HP", 2A @ 220v. This is simply not true. If it's a true 2hp, 3 phase current at 230v would be ~6.8A. If the 2A is true it's more like a 1/2 hp motor. It seems to have a ton of power when I lean into it. I'm thinking I'll up the overload setting to 5A and see how it goes..

a6e915d75a33468156e14bce688c710d.jpg
 

Attachments

  • a6e915d75a33468156e14bce688c710d.jpg
    a6e915d75a33468156e14bce688c710d.jpg
    742.4 KB · Views: 0

slodat

ALLIANCE MEMBER
Joined
Feb 6, 2010
Messages
3,679
Location
Central-ish, WA
Well.... it was the F18 (Motor rated current) setting. It's now happily stopping the motor without incident. Current settings:

F02: Decel time: 8 sec
F15: DC Braking Time: 1.5 s
F16: DC Braking injection freq: 3.0
F17: DC Braking Level: 15.0
F18: Motor Current: .67

I'm seeing voltage across the braking resistor now during deceleration. Drive is not tripping out. It appears to be stopping as fast as it can. It's taking about 26 seconds from 60 to 3 Hz. I'm happy. It works and I've start/stopped it a bunch of times.

Thanks guys!
 

laser3kw

Well-known member
Joined
Nov 17, 2012
Messages
7,276
Location
northen IL
A different drive?
Yes, we use Yaskawa drives. I find a lot of vfd program and run similar.
Good deal on your settings, I hope it helps others in the future. I am still curious as to why it win't stop faster . I realize it is a larger flywheel and little drag from drive train. We have a radial arm saw in our shipping department that we added a vfd to. Our safety committee recognized the run on as a safety concern. The vfd stops it in a short order.Maybe the parameter setting will shed some light on this
 

slodat

ALLIANCE MEMBER
Joined
Feb 6, 2010
Messages
3,679
Location
Central-ish, WA
Like I said, the disc takes an honest (timed) 45 minutes to coast to a stop. No matter how low I set F02, it's taking about 25 seconds 60-3 hz. I'm happy with the way it is working. Thanks for your help!

At my day job we use a lot of ABB in pump controls and Allen Bradley drives in our crane travel and hoist controls. For the ~$200 I have in the drive, I am happy with 30 second stop time.
 

MattT

Well-known member
Joined
Feb 20, 2010
Messages
3,201
Slodat,

Good catch on the chinese nameplate:thumbup: Aside from the amps being wrong the rpm also looks to be for 50Hz not 60.


I am still curious as to why it win't stop faster .

Sounds like the drive is automatically limiting decel to prevent overvolting the DC bus. Fairly common feature which can be turned off on some drives.

Agree it should be able to stop faster than 25s if it's capable of accelerating in 5s, at least in theory. I guess this raises the question of whether it's actually accelerating up to full speed in 5s?
 

slodat

ALLIANCE MEMBER
Joined
Feb 6, 2010
Messages
3,679
Location
Central-ish, WA
Agree it should be able to stop faster than 25s if it's capable of accelerating in 5s, at least in theory. I guess this raises the question of whether it's actually accelerating up to full speed in 5s?

Funny you say this. After I left the shop last night I was kicking myself for not timing the accel time to see how it looked. I will tonight.
 

slodat

ALLIANCE MEMBER
Joined
Feb 6, 2010
Messages
3,679
Location
Central-ish, WA
F01: Accel time: 5 sec
F02: Decel time: 9 sec

F05 was set to 4. Changing it to 6 => 11 second accel and 30 second decel.

Changing F05 = 5 changing F02 to 9 => 6.5 second accel and 22 second decel.

This is running really nice and the decel is really fast for the machine. The drive is clearly limiting the decel to limit over voltage on the DC bus. It's working well. I hadn't played with F05 yet, 4 was the default curve.

Video of start and stop.

 
Last edited:

laser3kw

Well-known member
Joined
Nov 17, 2012
Messages
7,276
Location
northen IL
F01: Accel time: 5 sec
F02: Decel time: 9 sec

F05 was set to 4. Changing it to 6 => 11 second accel and 30 second decel.

Changing F05 = 5 changing F02 to 9 => 6.5 second accel and 22 second decel.

This is running really nice and the decel is really fast for the machine. The drive is clearly limiting the decel to limit over voltage on the DC bus. It's working well. I hadn't played with F05 yet, 4 was the default curve.

Video of start and stop.

thanks for the video, that is really great performance of that unit. :thumbup: :beer:
Hope this inspires others to rescue industrial equipment. :bounce:
 

slodat

ALLIANCE MEMBER
Joined
Feb 6, 2010
Messages
3,679
Location
Central-ish, WA
Carrying my control panel style on to the disc sander.

Top is the test piece in 1/8 mdf. Bottom is the drill template for the indicator lamp.

b0c093d15c068750ec91d115f02a5f82.jpg

Finished part waiting for final assembly after work.

4032298ae2e20e3b43d6b85e898aaa0b.jpg

I have used these indicator lamps a few times in the shop. They help me make sure I’ve powered down at the end of the day. And, I like the look.
 

Attachments

  • 4032298ae2e20e3b43d6b85e898aaa0b.jpg
    4032298ae2e20e3b43d6b85e898aaa0b.jpg
    579.5 KB · Views: 1
  • b0c093d15c068750ec91d115f02a5f82.jpg
    b0c093d15c068750ec91d115f02a5f82.jpg
    926.1 KB · Views: 0

slodat

ALLIANCE MEMBER
Joined
Feb 6, 2010
Messages
3,679
Location
Central-ish, WA
Calling this one done. Well, I’m waiting for the dust chute to arrive, but that’s an easy bolt on.

798343808e0aeed80b56807166984694.jpg

c35f792980e2a2ec2cdfa578e9463d18.jpg
 

Attachments

  • c35f792980e2a2ec2cdfa578e9463d18.jpg
    c35f792980e2a2ec2cdfa578e9463d18.jpg
    694.7 KB · Views: 0
  • 798343808e0aeed80b56807166984694.jpg
    798343808e0aeed80b56807166984694.jpg
    497.2 KB · Views: 0

slodat

ALLIANCE MEMBER
Joined
Feb 6, 2010
Messages
3,679
Location
Central-ish, WA
Finished the Powermatic model 1200 variable speed drill press. Such a great machine. Very happy to have it running. Teco FM50 110v input 1hp drive. Braking works great on this one!

d53254290c23995adca7aed862196323.jpg

Video of it doing its thing:
 

Attachments

  • d53254290c23995adca7aed862196323.jpg
    d53254290c23995adca7aed862196323.jpg
    753.2 KB · Views: 1

laser3kw

Well-known member
Joined
Nov 17, 2012
Messages
7,276
Location
northen IL
you're gonna run out of projects!:thumbup:
unless you create projects to use your projects.
Are you using reversing on the drill press?
PS - on your disc sander, the resistor is a "20%" braking resistor - sort of like duty cycle. You could get a lower resistance / higher wattage and go to 50% or 70% and be ok. That will allow it to stop faster.
 

MattT

Well-known member
Joined
Feb 20, 2010
Messages
3,201
PS - on your disc sander, the resistor is a "20%" braking resistor - sort of like duty cycle. You could get a lower resistance / higher wattage and go to 50% or 70% and be ok. That will allow it to stop faster.

That resistor is more like 10% duty cycle. Upping the wattage might improve braking somewhat though dumping more heat into that small enclosure could cause problems.

Reducing resistance below the manufacturers recommendation is risky because it can nuke the chopper in the drive.
 
Last edited:

laser3kw

Well-known member
Joined
Nov 17, 2012
Messages
7,276
Location
northen IL
That resistor is more like 10% duty cycle. Upping the wattage might improve braking somewhat though dumping more heat into that small enclosure could cause problems.

Reducing resistance below the manufacturers recommendation is risky because it can nuke the chopper in the drive.
20% comes from the manufactures specs. "Upping the wattage" will do nothing except the resistor will not be as warm to the touch during the 26 seconds it is working. The braking is controlled by the dc buss voltage vs resistor value allowing the current of the field to dissipate - Ohm's law. Dump the current faster = better braking action.
I would guess a quick email or phone call to the manufacture will get you a good recommendation.
 