Looking for information on how to better support single piped boxes like this? (See pic) just afraid of plugging something in one day and basically the box shoves back and away from its position.

995b408e1c79313b33e6d7a7bc5490e0.jpg
 

Attachments

  • 995b408e1c79313b33e6d7a7bc5490e0.jpg
    995b408e1c79313b33e6d7a7bc5490e0.jpg
    54.5 KB · Views: 0
To avoid these ads, REGISTER NOW!
OP
P

polexican23

Banned
Joined
Jun 11, 2013
Messages
2,168
Location
burbs-Illinois
Thats easy enough, i figured there was some fancy electrical do dad or accessory to secure them kinda like the H23 caddys used for steel framed areas.
 

rburke65

Well-known member
Joined
Nov 10, 2007
Messages
12,349
Location
Canfield, Ohio
Yes....don't over think this. A 2x4" behind the box, nailed to the studs and the box screwed to the 2x4" will make it rock solid.
 

OzarkMan

Well-known member
Joined
Dec 3, 2014
Messages
556
Location
Ozark Missouri
Needs nothing if the wall covering is cut properly. The device tabs "Ears" will keep the box from shoving in let alone the device cover plate. The box has a bracket which is what it is intended for. If you really feel the need, like others mentioned a block of wood behind the box appropriately sized to fit will make it solid from flexing until the wall is complete.
 

D45

Well-known member
Joined
Mar 21, 2014
Messages
4,834
Location
NW INDIANA
Put a 2x4 under or over it or behind, or a combo of these

Then sink some screws and be done
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
Needs nothing if the wall covering is cut properly. The device tabs "Ears" will keep the box from shoving in let alone the device cover plate. The box has a bracket which is what it is intended for. If you really feel the need, like others mentioned a block of wood behind the box appropriately sized to fit will make it solid from flexing until the wall is complete.

Not always true, if the wrong depth ring is used like a 1/2" raised ring for 1/2" drywall, and/ or sloppy box cut outs in whatever the wall is to be covered in the receptacle will not secure. As to the ring depth, use one that is 1/8 inch deeper then the wall material, for example 5/8" ring for 1/2" material and 3/4" for 5/8" material.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,888
how the **** to do you fish conduit through the wall?

Half inch emt is pretty springy. First hole is drilled oversize and towards the front of the stud, rest are towards the back. No problem getting a 10' section in. I've got ten foot sections of rigid conduit in my walls (house built before emt was invented). I'm pretty sure they built the walls around the pipes.

In residential construction, most work is done through the ceiling or floor, and only vertical runs in the walls. If there's an attic or basement, it's done there, but most new construction uses trusses, which provide plenty of open space for conduit. Most commerical and multi-family residential uses metal studs, which have big holes for conduit
 
To avoid these ads, REGISTER NOW!

prostreetamx

Well-known member
Joined
Dec 19, 2016
Messages
222
Location
Las Vegas
A coworker from Chicago told me that when he did houses there that they would just precut most of the 1/2" EMT into 40" pieces. They just used lots of couplers which was faster than trying to make all the holes perfect just so you could use 10 footers. Personally I have used lots of 1/2" and 3/4" EMT in wood studs on commercial jobs. The companies were too cheap to just buy extra boxes of couplers. Personally I would use a metal spreader bar behind the 4s box if you want to firm it up. I don't want to use a block where I will be putting insulation in the future. I prefer good insulation over a space taking block of wood. Spreader bars are cheap and don't have to be cut to length in most cases.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,888
Is BX an option?

Only when adding to a finished space. If the walls are open (or the inspector thinks they should be), it's emt. Chicago electricians get very good at bending EMT, it's impressive to watch a good crew work.
 
OP
P

polexican23

Banned
Joined
Jun 11, 2013
Messages
2,168
Location
burbs-Illinois
A coworker from Chicago told me that when he did houses there that they would just precut most of the 1/2" EMT into 40" pieces. They just used lots of couplers which was faster than trying to make all the holes perfect just so you could use 10 footers. Personally I have used lots of 1/2" and 3/4" EMT in wood studs on commercial jobs. The companies were too cheap to just buy extra boxes of couplers. Personally I would use a metal spreader bar behind the 4s box if you want to firm it up. I don't want to use a block where I will be putting insulation in the future. I prefer good insulation over a space taking block of wood. Spreader bars are cheap and don't have to be cut to length in most cases.

you got a pic of what you are refering too as a spreader bar? I ran into the insulation situation last night when I was trying to fit wood blocks.
 

Firebrick43

Well-known member
Joined
May 12, 2015
Messages
14,008
Location
West central Indiana
I am building my house and using emt(but not in chicago). Only have wood studs on the interior walls and am using 4x4 x 2-1/8 deep boxes like your mounted with 4 1-1/4" screws. As such I am baffled why you need extra support? Did they screw them on or just a pair of nails?

If mine are slightly skewed I have to lay in quite a bit of my 240 lbs to bend the brackets so the face is in plane with the studs. I am seriously putting over 150 lbs of force on them. The studs twist drastically while doing this and is so solid I can't imagine how one could think that any person short of the Incredible Hulk could insert a plug between their fore finger and thumb with enough pressure to move the box. You would break the receptacle first!

View media item 71628
 
Last edited:

75gmck25

Well-known member
Joined
Jul 21, 2014
Messages
1,318
Location
Alexandria, VA
My house was built in 1940 and it has plaster walls with rock-lathe as a base layer. Every metal receptacle box is nailed to a 2x4 on one side, and then there is a very stiff metal spreader bar that runs over to the next stud for support. I guess they needed that much support to keep the boxes in place when they put on the plaster coats.

However, it makes it hard to replace the old small capacity metal boxes, since the metal on the nailing brackets and spreader bar is so thick. By the time I cut through them with a sawzall the vibration usually puts a bigger hole in the plaster than I really want.

Bruce
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,753
Is BX an option?

Where are you going to buy BX (AC)? What the big box stores sell is Metal Clad, MC. Edit: The areas requiring EMT limit the use of flexible wiring methods.
 
Last edited:
OP
P

polexican23

Banned
Joined
Jun 11, 2013
Messages
2,168
Location
burbs-Illinois
It is for the single run boxes, the one you posted has 3 lines coming in. The single runs have less support (according to inspector). Basically what i have found is that they refer to stuff like this as Far Side support.



I am building my house and using emt(but not in chicago). Only have wood studs on the interior walls and am using 4x4 x 2-1/8 deep boxes like your mounted with 4 1-1/4" screws. As such I am baffled why you need extra support? Did they screw them on or just a pair of nails?

If mine are slightly skewed I have to lay in quite a bit of my 240 lbs to bend the brackets so the face is in plane with the studs. I am seriously putting over 150 lbs of force on them. The studs twist drastically while doing this and is so solid I can't imagine how one could think that any person short of the Incredible Hulk could insert a plug between their fore finger and thumb with enough pressure to move the box. You would break the receptacle first!

View media item 71628
 

ard

Well-known member
Joined
Feb 16, 2015
Messages
4,391
Location
Sierra Foothills... California
It is for the single run boxes, the one you posted has 3 lines coming in. The single runs have less support (according to inspector). Basically what i have found is that they refer to stuff like this as Far Side support.

I feel like your inspector likes to just make **** up to make himself feel smart...

:(
 

Marctrees

Well-known member
Joined
Mar 5, 2015
Messages
6,265
Location
TX/LA border - Toledo Bend
30 posts about what is everyday handled w a common 2x4 block behind box? ? ? ?

Buying a steel box support ? ? ?

Why ?? NO benefit, actually not as sturdy as wood block and a few screws in real life.



Marc
 
Last edited:

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
5,875
Location
NJ
If Illinois is so concerned about safety, why are they still on the 2008 code? Basically 3 rev's behind!!!

Making all buildings out of masonry units would be safer than running conduit.
 

dscheidt

Well-known member
Joined
Apr 26, 2017
Messages
2,888
If Illinois is so concerned about safety, why are they still on the 2008 code? Basically 3 rev's behind!!!

Making all buildings out of masonry units would be safer than running conduit.

Not much in the last three code revisions about safety.
 

barnjunkie

Well-known member
Joined
Feb 3, 2015
Messages
181
Location
TN
The city officials must be concerned about safety and well being of the citizens there, I'm sure. They will waste their time arguing about something over and above their own adoption of code while the city turns into a third world ghetto.
Illinois is bankrupt according to the news girl. I drove north to Chicago the other day and the total negligence to the roadway system was amazing. Paid $18.50 in tolls to drive on the most dilapidated roadways in America. They are not too concerned about that too much though.
 

2Big2Ride

Well-known member
Joined
Oct 24, 2010
Messages
258
Location
d/FW, Texas - more FW than D
I used similar styled metal boxes, mud plates with MC for our shop. Boxes mounted to a wood stud with no additional support. Yes, the finished boxes have some deflection when you plug something in to the receptacle. I have a few boxes with EMT in the wall so that I could change wiring for a dedicated tool if needed - the connection to EMT makes the box firmer. Do I wish the boxes were more stable? Yes. But, weigh that with time, effort, and potentially insulation capacity and I will live with our wiggle boxes.
 
OP
P

polexican23

Banned
Joined
Jun 11, 2013
Messages
2,168
Location
burbs-Illinois
This is what I used and it worked fine (meaning inspector leaving me alone now). thanks for all your help, input and opinions.

abs.jpg
 

toplessHO

Well-known member
Joined
Oct 20, 2014
Messages
14,013
Location
central florida
tip for those using wood blocking.
if the box is plumb level square
put the screws in the box first
then screw the blocking to studs while holding box and support block.
 