Vapor Sealed Electrical Boxes Required for 70+ boxes...

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,068
Location
NJ
No, the picture he posted is a sub panel. Grounds can't go to the neutral bars, bonding screw needs to be removed. Needs ground rods (doesn't look like there's any for the meter/mains anyway, but ...).

He's got all the circuits made up in the panel, even if it's got a ways to go before being energized, it's still wrong and will have to be changed
OK. Pcustoms replied to the metermain Pic. If the meter/main is simply a meter and 2 disconnects only(no ocp), then the panel in post 29 is a main panel.
 
To avoid these ads, REGISTER NOW!

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,068
Location
NJ
That will be my option if I need something more once the walls are done, but as it stands I've almost finished wiring in the panel, and I have 19 circuits in there. I still have to run two more outdoor outlet circuits but... its cold out lol.

panel.jpeg
What type of insulation on the panel feed conductors?
 
OP
G

Gopherboy6956

Well-known member
Joined
Dec 19, 2021
Messages
135
Well there's a whole bunch of other stuff your inspector should fail you for before he hits the boxes...

Gonna need a ground with that feeder, along with ground rods (I'm assuming it's a detached shop). Are your circuit grounds going to the neutral bar?

Unless I'm missing something, isn't this a sub panel?

He's missing a ground, needs to add ground bars to separate the grounds/neutrals and the bonding screw needs to be removed...

Nope. Not with what is shown. It is a meter/main.
Not until he hits the cbs is there need for gec, bonding, 4 th wire on feeder.

The 2 enclosures below the meter enclosure are for circuit breakers (cbs) or at least disconnects.

The service entrance conductors aren't even terminated and you're trying to pop him for finished job conditions. ???

No, the picture he posted is a sub panel. Grounds can't go to the neutral bars, bonding screw needs to be removed. Needs ground rods (doesn't look like there's any for the meter/mains anyway, but ...).

He's got all the circuits made up in the panel, even if it's got a ways to go before being energized, it's still wrong and will have to be changed


Just to get all this in one shot -

This is considered a main panel, not a sub panel. This does not in any way connect to my house's main panel. The picture posted above was from the socket upgrade on the house.

As this is a main panel, my electrical inspector told me that all the grounds and neutrals terminate in the same bar.

I do have a ground wire running into the panel, its right there in the picture :) I also have two 8' ground rods that I painstakenly pounded (not really) when I rented the skidster to cover up the trench.

The panel is fully live right now, and I unfortunately had to finish terminating all the circuits in there last night while it was live, because its around zero degrees F here right now, and the shop isn't yet insulated and I needed heat It was everything the 80k btu big maxx could do to keep it 43 degrees in there.

(I feel "Shed" is a bit reductive)
1.JPG

(ground wire)
2.JPG

(ground rod 1 of 2)
3.JPG
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,603
Location
VT
(I feel "Shed" is a bit reductive)
1.JPG

(ground wire)
2.JPG

(ground rod 1 of 2)
3.JPG

I must be missing something, I don't see how the "shed" is a main panel....

Does that bare copper ground go in the conduit, all the way back to the meter/disconnect, or just to the ground rods?
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,068
Location
NJ
This is a meter/main. The 2 blue handled devices are cb's.
1765160244947.jpeg
The panel in your house and the shed are sub panels.

So your shed sub panel needs a 4 wire feeder, unbonded neutral, and egc's seperated from the neutral blocks as Pcustoms mentioned. And this is true for BOTH SUB PANELS.

I hope that feeder is not URD.

I hope your electrical inspector doesn't think the shed panel is a main panel as you have it all wired up.
Did the inspector realize there would be cbs at the meter? Or just think it would have dual lugs?
 
Last edited:

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,068
Location
NJ
I must be missing something, I don't see how the "shed" is a main panel....

Does that bare copper ground go in the conduit, all the way back to the meter/disconnect, or just to the ground rods?
The bare copper exits through the enclosure shown in the 1st sub panel pic.
 

PCustoms

Well-known member
Joined
Jul 23, 2011
Messages
23,603
Location
VT
The bare copper exits through the enclosure shown in the 1st sub panel pic.

I figured, just like when I asked to see what this was fed from was hoping the OP would show me I was wrong.

Guy likely spent thousands on this install which appears pretty jacked up, but is complaining about the cost of air sealing his (excessive?) boxes.

SMH
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,068
Location
NJ
Likewise....no surprise there are cbs below meter.

I think both feeders will wind up being urd also.
 
OP
G

Gopherboy6956

Well-known member
Joined
Dec 19, 2021
Messages
135
Ok - let me see here -

First of all - I genuinely appreciate all of the comments, insight, questions, recommendations. This sub has been the best online source of information on my shop build, all the way from concept last january, through framing, to today. So from that standpoint, I appreciate you all.

I am not in any way, shape, or form an electrician - just a guy who's finished a basement, decent with electronics, and thinks I understand a fair amount about residential electric. There is ABSOLUTELY a chance that terminology I've used or the way i've described things is incorrect - but - I feel strongly that my panel is currently wired correctly, with the one exception that could be anything i've done recently hooking up the remaining circuits. I will 100% follow this up after my visit with the inspector tomorrow.

I used a licensed master electrician to upgrade the socket on my home - which came as a recommendation from my local power company when I inquired about what I wanted to do.

I have 4/0, 4/0, 2/0 triplex aluminum URD coming underground from the street box a few houses away, to the meter / disconnect on the side of my house. From there, it now splits 200a into my house, and 200a into the new shop. There is no ground wire that goes into that box, just the 3 wires from the street - the panel in my basement also has ground rods (one left visible in the concrete). I included a picture of the old meter box / disconnect they took off the wall before installing the new one (i guess I get to keep it?) - Eaton model CMBXB200BTS.

From there, I again used 4/0, 4/0, 2/0 triplex (as recommended by the power company and purchased from my electrician) and trenched it into the shop. I was not required to run a ground in the trench as I was going to have to pound in 2 new ground rods for the shop.

The inspector that i've been working with is also the inspector that checked and signed off on the electrician's work upgrading my socket. That same day we test energized my panel in the shop, and both the electrician and inspector were happy with it. All of the triplex connections, ground wire connections, and the bonding screw were present that day as they are now. I actually had purchased a ground bar for inside the panel assuming they'd need to be separate ground and neutral busses.

I also asked the inspector to stop over after I put in all of my boxes but before I ran the were, because I knew there were things I didn't know I didn't know - like GFCI outlets can't be out of reach, which I had planned a few for a future loft addition, 240v nuances - things like that.

Oddly enough, the thing that he was most adamant about was that we had one dedicated recepticle / circuit without switches or anything else for each 'stall' of the garage, calling mine a 3 stall. Thankfully I didn't have to change my plans, just how I grouped some outlets, because I had so damn many as was eluded to above lol.

Anyways - tomorrow i'll have the inspector stop by, i'm ready for my rough-in inspection. I'll keep you updated!

Old Meter Panel
4.JPG

Planning for the future, not knowing what I'm gonna need for recepticles lol
5.JPG

8ft LED Fixtures just arrived today, will be 12 of those total, 4 of some other yet to pick out lights over the future loft, and the fun hexagon lights under the loft floor
6.JPG
 
Last edited:
OP
G

Gopherboy6956

Well-known member
Joined
Dec 19, 2021
Messages
135
I must be missing something, I don't see how the "shed" is a main panel....

Does that bare copper ground go in the conduit, all the way back to the meter/disconnect, or just to the ground rods?
Just the ground rods outside the shop.
 
OP
G

Gopherboy6956

Well-known member
Joined
Dec 19, 2021
Messages
135
I figured, just like when I asked to see what this was fed from was hoping the OP would show me I was wrong.

Guy likely spent thousands on this install which appears pretty jacked up, but is complaining about the cost of air sealing his (excessive?) boxes.

SMH
I spent $3,200 on the new meter panel, labor to swap it, and 200ft of 4/0,4/0,2/0 Triplex. The rest of the electrical has been done by myself.
 
OP
G

Gopherboy6956

Well-known member
Joined
Dec 19, 2021
Messages
135
I figured, just like when I asked to see what this was fed from was hoping the OP would show me I was wrong.

Guy likely spent thousands on this install which appears pretty jacked up, but is complaining about the cost of air sealing his (excessive?) boxes.

SMH

Likewise....no surprise there are cbs below meter.

I think both feeders will wind up being urd also.

Ok - this all got my brain fired up - Not because i'm scared to be wrong, i'm wrong a lot! But because I couldn't believe that both my electrician (who has been in business for 18+ years) and the local inspector have it wrong.

So I ran outside, took a bunch of photos of my main meter box (brrr, also its 2am) and then read A LOT.

The conculsion that i've come to that makes everything right - is that the meter box on my house now has two DISCONNECTS, not circuit breakers. It's a Milbank U6585-X-2/200-5T9.

That makes my shop panel service equipment and not a subpanel.

My old meter box, the Eaton, has a CSR 25k circuit breaker in it and my panel in the house basement has 4 conductors and separate ground and neutral bars - installed when our house was built in 2015.

My understanding is that Utilities and AHJ's prefer this method because it's safer for firefighters, etc.

Now i'll be able to sleep but will still complain about the cost of air sealing my excessive boxes, @PCustoms :)


Thanks again for the comments everyone, because of this rabbit hole, I learned a bunch tonight.

20251208_010309.jpg

20251208_010425.jpg

20251208_010446.jpg
 

billconner

Well-known member
Joined
Jul 20, 2021
Messages
6,971
Location
Thousand Islands NYS
Can you use the typical "tile" shims to offset?

My NEC bane has been combo AFI/GFI breakers. I'll never do those again. They false all the time. From now on it's AFI breaker and GFI outlet, for some reason that works better.
Interesting. I installed several 2 years ago and no trips.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,068
Location
NJ
Ok - let me see here -

First of all - I genuinely appreciate all of the comments, insight, questions, recommendations. This sub has been the best online source of information on my shop build, all the way from concept last january, through framing, to today. So from that standpoint, I appreciate you all.

I am not in any way, shape, or form an electrician - just a guy who's finished a basement, decent with electronics, and thinks I understand a fair amount about residential electric. There is ABSOLUTELY a chance that terminology I've used or the way i've described things is incorrect - but - I feel strongly that my panel is currently wired correctly, with the one exception that could be anything i've done recently hooking up the remaining circuits. I will 100% follow this up after my visit with the inspector tomorrow.

Also for reference, I'm in Fargo, ND - just in case location / state laws differ from others.

I used a licensed master electrician to upgrade the socket on my home - which came as a recommendation from my local power company when I inquired about what I wanted to do.

I have 4/0, 4/0, 2/0 triplex aluminum URD coming underground from the street box a few houses away, to the meter / disconnect on the side of my house.(This is fine as it terminates in the metermain OUTSIDE.) From there, it now splits 200a into my house, and 200a into the new shop. There is no ground wire that goes into that box, just the 3 wires from the street - the panel in my basement also has ground rods (one left visible in the concrete). I included a picture of the old meter box / disconnect (Yes it does perform a disconnect function but it uses a circuit breaker, as does your new metermain.) they took off the wall before installing the new one (i guess I get to keep it?)(Yes, no one wants it.) - Eaton model CMBXB200BTS.

From there, I again used 4/0, 4/0, 2/0 triplex (as recommended by the power company (They told you the wrong info, they ae not NEC experts by any means) and purchased from my electrician) and trenched it into the shop. I was not required to run a ground in the trench as I was going to have to pound in 2 new ground rods for the shop. (Ground rods have nothing to do with the requirement for including an equipment grounding conductor as part of the feeder to the shed.)

The inspector that i've been working with is also the inspector that checked and signed off on the electrician's work upgrading my socket. That same day we test energized my panel in the shop, and both the electrician and inspector were happy with it. All of the triplex connections, ground wire connections, and the bonding screw were present that day as they are now. (Then they were both wrong with the feeder for the shed. Elsewhere you state the house panel has a 4 wire feeder. That is needed and is correct. The shed needs the same. I actually had purchased a ground bar for inside the panel assuming they'd need to be separate ground and neutral busses. That was/is the correct thinking.

I also asked the inspector to stop over after I put in all of my boxes but before I ran the were, because I knew there were things I didn't know I didn't know - like GFCI outlets can't be out of reach, which I had planned a few for a future loft addition, 240v nuances - things like that.

Oddly enough, the thing that he was most adamant about was that we had one dedicated recepticle / circuit without switches or anything else for each 'stall' of the garage, calling mine a 3 stall. Thankfully I didn't have to change my plans, just how I grouped some outlets, because I had so damn many as was eluded to above lol.

Anyways - tomorrow i'll have the inspector stop by, i'm ready for my rough-in inspection. I'll keep you updated!

Old Meter Panel
4.JPG

Ok - this all got my brain fired up - Not because i'm scared to be wrong, i'm wrong a lot! But because I couldn't believe that both my electrician (who has been in business for 18+ years) and the local inspector have it wrong.

So I ran outside, took a bunch of photos of my main meter box (brrr, also its 2am) and then read A LOT.

The conculsion that i've come to that makes everything right - is that the meter box on my house now has two DISCONNECTS, not circuit breakers. It's a Milbank U6585-X-2/200-5T9. (Those 2 disconnects are CIRCUIT BREAKERS. The labelling and spec sheet clearly indicate as such. The "200" on the trip handle also indicates as such.)

That makes my shop panel service equipment and not a subpanel. NOPE! The service entrance equipment stops at the metermain. Everything else from it is a feeder and sub-panel. Just like your house panel was/is.

My old meter box, the Eaton, has a CSR 25k circuit breaker in it and my panel in the house basement has 4 conductors and separate ground and neutral bars - installed when our house was built in 2015. Because it is a sub-panel. The metermain is the main panel.


My understanding is that Utilities and AHJ's prefer this method because it's safer for firefighters, etc.


20251208_010309.jpg

20251208_010425.jpg

20251208_010446.jpg

Sure looks like a breaker to me:

1000002891.png

 
To avoid these ads, REGISTER NOW!

Chuckster in NJ

Well-known member
Joined
Jan 26, 2010
Messages
2,332
Location
Hunterdon County NJ
Maybe just not up to date :headscrat
I learned something new each day and looking at that picture of the meter pan with the "gray goo" on the wires refreshed my memory when I failed a job for NO PENETROX on aluminum wires and the contractor told me I was wrong so I said: "Well, prove me wrong and I will approve the work" and he did with info from two wire companies.……… It is impossible to keep up to date on changing codes and I was "educated" by contractors (and other peers) and always open minded to intelligent conversations about the codes.

BTW! Respectful and intelligent conversations are "key" to getting your point across and winning with a "wrong" inspector……… Unless the inspector is a ****.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,290
Location
Coastal NJ
I learned something new each day and looking at that picture of the meter pan with the "gray goo" on the wires refreshed my memory when I failed a job for NO PENETROX on aluminum wires and the contractor told me I was wrong so I said: "Well, prove me wrong and I will approve the work" and he did with info from two wire companies.……… It is impossible to keep up to date on changing codes and I was "educated" by contractors (and other peers) and always open minded to intelligent conversations about the codes.

BTW! Respectful and intelligent conversations are "key" to getting your point across and winning with a "wrong" inspector……… Unless the inspector is a ****.
A friend asked me to tag along with their home inspector last Friday. This was a pre-purchase inspection. He showed me the "missing" Penetrox. I explained todays alloys. He never heard of that. I see it is still used quite often, I assume just to avoid getting questioned.
 

Bad Habit

Well-known member
Joined
Mar 19, 2014
Messages
2,017
Location
Chumstick WA
Maybe just not up to date :headscrat
ND has adopted the 2023 NEC, in enforced since since July of 2024. Possible Fargo and/or county could have local codes that over rule the NEC but doubtful they would make changes to lessen safety requirements for grounding. Regardless of raceway in the trench, a ground conductor needs to be run with the feeder.
 

Bad Habit

Well-known member
Joined
Mar 19, 2014
Messages
2,017
Location
Chumstick WA
A friend asked me to tag along with their home inspector last Friday. This was a pre-purchase inspection. He showed me the "missing" Penetrox. I explained todays alloys. He never heard of that. I see it is still used quite often, I assume just to avoid getting questioned.
big difference between a Home Inspector and an actual AHJ Electrical Inspector.
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,068
Location
NJ
ND has adopted the 2023 NEC, in enforced since since July of 2024. Possible Fargo and/or county could have local codes that over rule the NEC but doubtful they would make changes to lessen safety requirements for grounding. Regardless of raceway in the trench, a ground conductor needs to be run with the feeder.
That was a joke for Chuckster as he is a former AHJ. (joking about a 17 yr old code change.)
The 4 wire feeder requirement has been around since 2008, IIRC.
 

Bad Habit

Well-known member
Joined
Mar 19, 2014
Messages
2,017
Location
Chumstick WA
Yep, just dealt with this selling our home. To give the some credit though, he did ultimately investigate and corrected the ding on the report.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,290
Location
Coastal NJ
Home inspectors can just "suggest" things. They have no enforcement power. They're notoriously weak on electrical and are wrong most of the time (they often suggest calling a qualified electrician to verify their claims).
Very true. The reports I read mostly show a photo of something they saw and a comment to hire an expert or licensed professional from there. The buyer and seller then negotiate what boils down to price from there.
 

manwithtools

ALLIANCE MEMBER
Joined
Aug 24, 2015
Messages
14,195
Location
Lebanon, TN
Home inspectors can just "suggest" things. They have no enforcement power. They're notoriously weak on electrical and are wrong most of the time (they often suggest calling a qualified electrician to verify their claims).
And they do a terrible disservice to home sellers when they do that. An uneducated potential buyer will get nervous about the numerous "consult a licenced electrician" notes and potentially back out of the deal needlessly. Also in some states, those inspection notes have to be disclosed to the next potential buyers, causing a cascading effect. Home inspectors really tick me off as they won't accept any negating commentary from the home seller who might just understand code better than they do.
 

dave*99

Well-known member
Joined
May 5, 2009
Messages
4,290
Location
Coastal NJ
And they do a terrible disservice to home sellers when they do that. An uneducated potential buyer will get nervous about the numerous "consult a licenced electrician" notes and potentially back out of the deal needlessly. Also in some states, those inspection notes have to be disclosed to the next potential buyers, causing a cascading effect. Home inspectors really tick me off as they won't accept any negating commentary from the home seller who might just understand code better than they do.
Certainly there can be code violations noted.
Locally, missing CO detectors and GFCIs' will also be picked up by the local town inspector. One realtor told me he personally installs battery CO detectors for his clients as part of his service.

But in my experience, most of the resulting discussion seems to be between the realtors and their respective clients. Stuff like "The HVAC system is currently working but at it's current age the industry says it is at end of life." Put a few of those in the report and the buyer wants a discount. The seller says its been working fine for me. So it's a negotiation that is solved with $$.
 

manwithtools

ALLIANCE MEMBER
Joined
Aug 24, 2015
Messages
14,195
Location
Lebanon, TN
Certainly there can be code violations noted.
I'm referring to incorrect violations of code noted.

For instance in my last house sale the inspector noted that the gas water heater needed to be 18" off the floor, not at floor level as it was.. He failed to understand that it was a Bradford White "Defender" series which is specifically rated for installation at floor level in a garage. This became a needless major issue for the buyers.

Even the "licensed" plumber they hired to inspect the installation said it had to raised. Two supposed experts who couldn't be bothered to look up the specs on the heater. The inspector would not remove it from his report even after I provided proof of it being an approved installation.

There were other instances on the same sale of the 4 year old house that had passed inspection fully at the time of construction. No new codes were in effect at the time of sale, no additions or modifications had been made to the structure. I have great distaste for Home Inspectors, they feel they have to provide a lengthy report to insure perceived value for their services. They can't just say "No major issues were found"
 
Last edited: