Welp, had my rough in electrical inspection and was failed on two things. One is that I put a subpanel in a large closet and he told me it can't be in a closet. At this stage, that is a lot of work to change given I've got piping running all around it in the wall. Also, failed me because apparently we need to have three wired smoke detectors in the addition all joined together so if one goes off, all go off. Just venting. Frustrating because I had him out last week and he didn't make mention of either when I told him I'd schedule my rough in.
Can someone enlighten me on the wired in detectors. I've never had to wire them in. Just used the battery ones in my house. How do I wired them to all go off if one does? Is it as simple as running them in sequence back to the breaker?
BrandonV
Arizona
Most jurisdictions today require the smoke alarms are interconnected. When one goes off they all go off.
This is usually accomplished by using a 3rd wire for the interconnection signal (typically by running 14/3 NM) that is connected to all the smoke detectors so that when one goes off it sends a signal to the rest.
Not sure what code applies but they do have hard wired interconnected smoke alarms that accomplish the interconnection via a wireless signal. Not sure if that meets whatever code you have to adhere to.
If you can run a #14 THHN wire between the detectors I'd probably just do that.
Hohn
Diesel Central, Indiana
Just replaced all my detectors a couple days ago, and mine are 120V wired with battery backup. Had to rewire the little pigtails because the new ones had a different plug.
mm08822
Run 14-3 between each sd outlet box. Use the red to interconnect the alarms. Buy all the same brand so there aren't any compatability issues. (Not sure if they are all standardized alarm output signals.)
If an interior wall, can you turn the panel 180 degrees so it presents itself on the other side of the wall? This would be the least disruptive to the construction activities.
Higgins
Shepheardsville, KY
How large is the closet ???
Should have 3 ft on the left and right side, of the panel along with a work space in front of the panel!
BrandonV
Arizona
These days the interconnection signal is mostly the same 9V signal... but I found some of the older ones sent a 120V signal on the 3rd wire.
Important to make sure whatever is interconnecting is adequately rated for 120V if not 14/3. :).
wssix99
Chicago, IL
Battery smoke detectors are extremely unreliable. You should have a separate circuit dedicated to your 120V smoke detectors. As noted above, you just need a third wire between the boxes for communication and they will all have battery backups.
Another thing to consider is that you may also need CO detectors. In our house, we were required to have one CO detector per floor and then more smoke detectors at the entrance of each bedroom. One PITA we have is that our Smoke/CO units use AA batteries and our Smoke-only units use 9V batteries. When it comes time to replace the batteries, it's a bit of a pain. (I wish they were all the same design.)
sparky 1971
Central Iowa
There are two places panels can't be located regardless of clearances. Clothes closets and bathrooms. And it's 30" total width and 36" depth in those 30".
Smoke detectors are easy. Power to one and 14/3 between them all. You probably already know the locations. I was taught, and have always used a single gang box for them and I may or may not use drywall screws to attach them to said box.
W
wcp0611
Rockvale, TN
Its got way more than that. He said he could tell it was going to be a closet and said it can't be in a closet. I'm going to turn it around tonight but not happy with having to do it. I don't want to sass the inspector as I'm trying to get drywall in next week.
Bert_
NW Iowa
The code says clothes closet, not just closet. If it's in a bedroom or hallway you're going to have a hard time arguing that. But some closets could be acceptable.
I had a guy a couple years ago remodeling a house. The room in the basement where the panel was he was going to turn into a bathroom. I told him to build a little 3-ft closet around the panel and leave it unfinished inside. Now it's not in the bathroom, and nobody is going to argue that an unfinished closet will be used to keep clothing.
W
wcp0611
Rockvale, TN
So do you run that circuit off its own 15amp breaker? My house doesn't have any hardwired ones in it so this is new to me.
mm08822
That's why I say make them all the same. When I am replacing them, it's all or none.
mm08822
I have seen a seperate circuit more often then not.
One thing I don't do is mix other cables within the smoke detector outlet box. Each outlet only contains cables that interconnect the sd's.
A dedicated circuit would require an afci since the outlets are in bedrooms, hallways, etc.
Junkdrawer Dog
LV NV
Had to do same here. They make little pigtail adapters just for that if you can find them.
sparky 1971
Central Iowa
If it's not going to, nor could it ever be, a clothes closet you could argue it. But, other than a pantry it's hard to find a closet that's not going to store some type of clothing in a house. There are utility and mechanical closets, and if it's big enough, mop closets.
Panels have not been allowed in clothes closets for a long time now... thats on you for not knowing the code not the inspector, who im sure often misses things.
you will need to move it and for good reason. I bet it doesnt even have the required working clearances...
this has also been a requirement in most jurisdictions for at least a decade.
you need to run 3 wire NM-b between all of them. first detector gets 2 wire NM-b for power feed from breaker. then with the 3-wire NM-b between them, power is provided on 2 conductors and the third conductor is the signaling wire that is interconnected between all 3.
that would require conduit. cant run loose conductors in the wall
W
wcp0611
Rockvale, TN
Panels have not been allowed in closets for a long time now... thats on you for not knowing the code not the inspector, who im sure often misses things.
Thanks. The closet is large enough to check all the boxes on clearance but again, I'm not going against what he told me to do as I don't need him failing me a second time to stay on track. My house was built in 95 and has no wired detectors so that was all new to me. I've got some 14/3 left over from the three way switches controlling the hall way light going to it the addition.
when it comes to clothes closets, it doesnt matter what the clearances are. clothes closets arent allowed.
mm08822
Too bad the panel location wasn't caught in plan review.
Even the smokes could have been caught - whether missing all together or just lack of interconnection.
Either way, it's on the owner to have the build made correctly. Otherwise, no CO!
sparky 1971
Central Iowa
I know they can't be and haven't been allowed in closets for quite some time now. Any idea when it changed? In 1997 I wired two big houses side by side in a Dallas suburb, (Highland Park?) both with 400 amp services, both had one of the panels in the master closet on the second floor. I'll never forget what a pain those were because getting the feeders up there were a beotch, everything in there had to be EMT. I was the only person in the shop with any experience running EMT and at that point in my career, it wasn't much experience at all and had been limited to 1/2 and 3/4. I'm sure they list money on those.
PelicanPines
Well... I will mention it... In addition to wired smoke detectors... they require at least ONE carbon monoxide detector "Combo" as well. One smoke detector in EACH bedroom, one near the kitchen and the Carbon Monoxide detector combo on the ceiling in a main hallway. Usually at the top of the stairs if you have stairs... if not... somewhere in the central hallway.
sparky 1971
Central Iowa
Good point on the carbon, but the only locations that should be required should be likited to the addition. I don't know what the addition consists of, but if they want three, I'd guess it's two bedrooms and a hallway. If so, the carbon would go in the hall.
TRWham
East Cobb County, Georgia
We just did this on a renovation where the panel was in the old laundry room that is now the new laundry room but also now a bathroom with no separation. Our electrical closet is not 36" deep, but the pocket door we installed allows the required working space when open and we passed rough with no issue.
As for wired smokes and COs, IRC 314 and 315 cover this in detail. Each bedroom needs a smoke detector, and each level needs a smoke and CO within 10' of every bedroom door (the code just says "in the vicinity" but 10' has become the rule of thumb) in the hallway outside (but at least 3' from any bathroom), so that may drive the need for additional units. And they must be powered from "the building wiring," so they cannot be part of the security system (I had one client try that one). In our area, the first thing they check on rough inspection is the smokes. If they are not roughed in, the inspector will not look at anything else.
sparky 1971
Central Iowa
You would have to convince him that there won't be any clothes in there. Good luck with that. You're better off with plan B, turning it around.
Jim greengo
Behind my house
Atleast since the early90s around omaha anyway.
LopezBart
Lopez Island, WA
There are also low voltage inter-connected alarms that hook up to a panel w/ batteries and a charger. These typically make it through a couple of days w/o power... Some can be configured to call fire, etc.
75gmck25
Alexandria, VA
I initially thought I should have all the wired smoke detectors on a dedicated circuit, but as I was starting to run out of breakers I found other guidance that suggested putting the detectors on a very visible lighting circuit. The logic was that if a frequently used bedroom or hallway lighting circuit went out, that would prompt you to check the breaker box and find out your smoke alarms were also off. YMMV
I have one of those combo fire/CO detectors in my basement office because its close to the room with my heating system. Every once and a while my wife sets off the wired smoke alarms by firing up the kitchen burners on high without first turning on the exhaust fan. The wired combo detector in my office then starts alarming with "BEEP-BEEP, Fire!". I guess that's how it makes it clear it is not a CO alarm.
LOW1
ontario
Might be worth considering hardwiring new smoke detectors into the old portion of your house if you can get access to run the needed wires.
Smoke and CO detectors are a wise investment.
TRWham
That is required in many states if you pull a permit for any work in the conditioned space.
TRWham
That will not comply according to the AHJs where we work. Must be powered by the building wiring.