Does this chart indicate that he maximum breaker allowed is a 30 amp?
wazzabie
Cruzan80
Denver, CO
Isn't this the same panel that you want to run a new circuit for your compressor on? You said you already have a 50A circuit on there ...
I don't see any place on there listing a 30A limit.
W
wazzabie
Just to the right of the main breaker on the diagramn, it says
"Do not install greater than a max of 200 amp connected load per tab"
:dunno:
I thought that could have meant the entire side could not have totaled 200amps if the breakers were added.
JohnX14
Boston 'burbs
It does mean that, sort of. It means the total of each bus, (every other breaker top to bottom) can't exceed 200 amp load. Which is different than adding up the breaker sizes.
W
wazzabie
Yep, the combination of threads from OP is a clear indication he needs a pro
I found an error that both the electrician and inspector failed to catch over 10 years ago. The electrician installed a Siemens breaker into the Silvana panel. While the break did fit it is not correct. Eaton has the sole ownership of the breakers for this vintage panel.
So I need to pull the breaker the electrician and inspector failed to catch and replace. I also need to pull the three Siemens I installed and replace those breakers in more recent years. I'm hesitant to do this because the bus bar is scored anytime a breaker is removed and replaced.
whateg01
doo dah, kansas, usa
That "per tab" bit means that each tab cannot exceed 200A. If it meant that "the entire side" couldn't exceed 200A, it would say something like "per bus". But it doesn't.
W
wazzabie
While the Siemens isn't listed for use in the Sylvania panel, I wouldn't lose sleep if it were in my house.
Using another manufacturers circuit breaker in the wrong panelboard violates NEC® 110.3(B) and violates the product listing. 1774201892814.png
mm08822
Unless the panel manufacturer has listed the panel to include other mfr's cbs. (highly unlikely)
However, a mfr different than the panel mfr can have their cb's classified to be used in another mfr's panel.
W
wazzabie
W
wazzabie
Why? Do you think you've over loaded it?
I have no reason to believe I'm over load. I want to know what the calculations are for my own knowledge. I have some doubts about the work of the electrician and inspector performed since they both approved using a Siemens breaker rather then the Eaton. I would rather learn so that I personally know the work is correct.
W
wazzabie
Scored?
Scorched?
Not exactly 100% sure what you're saying here but you need to call a pro and possibly have your panel replaced
The panel is not burned. Not sure why the panel would need to be replaced. It is not part of the Zinsco panel issue.
Cruzan80
Denver, CO
If you think the bus bars are "scored" aka. damaged, that would be an indication of a new panel being needed.
As others have said, this seems like a classic case of "book knowledge" exceeding your ability in the real world to accomplish things safely.
wyliesdiesels
Modesto, CA
what?
there shouldnt be any scoring when installing and removing a breaker. there is nothing inside the breaker clamp that could score the stab on the bus bar
JohnX14
Boston 'burbs
nope it says STAB, meaning where the breakers connect, not the entire bus.
You're right.
But the rating of the panel is limited to 200 amps as well. (0r 225) This panel can't be fed with 400 amps and pull 200 on (2) stabs on the same leg. But I get it, that's not what I
Edit: deleted a statement that I realized wasn’t accurate
JohnX14
Boston 'burbs
There are lug kits that I’ve used on Eaton BR load centers that allow me to pull 200 amps to a subpanel. So yes I agree it’s 200 per stab.
