Yep, the combination of threads from OP is a clear indication he needs a proWhen you're this unsure call an electrician.
I thought that could have meant the entire side could not have totaled 200amps if the breakers were added.Just to the right of the main breaker on the diagramn, it says
"Do not install greater than a max of 200 amp connected load per tab"
.
It does mean that, sort of. It means the total of each bus, (every other breaker top to bottom) can't exceed 200 amp load. Which is different than adding up the breaker sizes.I thought that could have meant the entire side could not have totaled 200amps if the breakers were added.
I found an error that both the electrician and inspector failed to catch over 10 years ago. The electrician installed a Siemens breaker into the Silvana panel. While the break did fit it is not correct. Eaton has the sole ownership of the breakers for this vintage panel.Yep, the combination of threads from OP is a clear indication he needs a pro

No.It does mean that, sort of. It means the total of each bus, (every other breaker top to bottom) can't exceed 200 amp load. Which is different than adding up the breaker sizes.
I'm hesitant to do this because the bus bar is scored anytime a breaker is removed and replaced.
"Do not install greater than a max of 200 amp connected load per tab"
That "per tab" bit means that each tab cannot exceed 200A. If it meant that "the entire side" couldn't exceed 200A, it would say something like "per bus". But it doesn't.I thought that could have meant the entire side could not have totaled 200amps if the breakers were added.
Says who?I'm hesitant to do this because the bus bar is scored anytime a breaker is removed and replaced.
Not even. A bus alternates between each horizontal row.If it meant that "the entire side" couldn't exceed 200A, it would say something like "per bus". But it doesn't.
Unless the panel manufacturer has listed the panel to include other mfr's cbs. (highly unlikely)
My assumption is that every time a breaker is removed that a groove in the metal will remain. This is a logical assumption as the electrical contactors are a metal to metal contact.Says who?
Good catch on me misstating that!Not even. A bus alternates between each horizontal row.
I'm considering calculating a load calculation for the panel. https://elecalculator.com/calculator/motor/load-calculator/Not even. A bus alternates between each horizontal row.
Keep going........time to shut this thread down.I'm considering calculating a load calculation for the panel. https://elecalculator.com/calculator/motor/load-calculator/
This is what I thought meant not to exceed 10-30 amp breakers.
This is what I thought meant not to exceed 10-30 amp breakers.
I'm considering calculating a load calculation for the panel. https://elecalculator.com/calculator/motor/load-calculator/
I have no reason to believe I'm over load. I want to know what the calculations are for my own knowledge. I have some doubts about the work of the electrician and inspector performed since they both approved using a Siemens breaker rather then the Eaton. I would rather learn so that I personally know the work is correct.Why? Do you think you've over loaded it?
The panel is not burned. Not sure why the panel would need to be replaced. It is not part of the Zinsco panel issue.Scored?
Scorched?
Not exactly 100% sure what you're saying here but you need to call a pro and possibly have your panel replaced
THIS ^ is why the OP should not be "playing" electrical contractor.This is what I thought meant not to exceed 10-30 amp breakers.
If you think the bus bars are "scored" aka. damaged, that would be an indication of a new panel being needed.The panel is not burned. Not sure why the panel would need to be replaced. It is not part of the Zinsco panel issue.
It does mean that, sort of. It means the total of each bus, (every other breaker top to bottom) can't exceed 200 amp load. Which is different than adding up the breaker sizes.
what?I'm hesitant to do this because the bus bar is scored anytime a breaker is removed and replaced.
so then you missed the Ø symbolThis is what I thought meant not to exceed 10-30 amp breakers.
You're right.nope it says STAB, meaning where the breakers connect, not the entire bus.
So yes I agree it’s 200 per stab.