Does this chart indicate that he maximum breaker allowed is a 30 amp?

wazzabie

Well-known member
Joined
May 9, 2010
Messages
424
Does this chart indicate that he maximum breaker allowed is a 30 amp?

1774196709069.png
 
To avoid these ads, REGISTER NOW!

Cruzan80

Well-known member
Joined
Jul 22, 2015
Messages
4,318
Location
Denver, CO
Isn't this the same panel that you want to run a new circuit for your compressor on? You said you already have a 50A circuit on there ...

I don't see any place on there listing a 30A limit.
 
OP
W

wazzabie

Well-known member
Joined
May 9, 2010
Messages
424
Just to the right of the main breaker on the diagramn, it says
"Do not install greater than a max of 200 amp connected load per tab"

:dunno:

.
I thought that could have meant the entire side could not have totaled 200amps if the breakers were added.
 

JohnX14

Well-known member
Joined
Jun 2, 2014
Messages
609
Location
Boston 'burbs
I thought that could have meant the entire side could not have totaled 200amps if the breakers were added.
It does mean that, sort of. It means the total of each bus, (every other breaker top to bottom) can't exceed 200 amp load. Which is different than adding up the breaker sizes.
 
OP
W

wazzabie

Well-known member
Joined
May 9, 2010
Messages
424
Yep, the combination of threads from OP is a clear indication he needs a pro
I found an error that both the electrician and inspector failed to catch over 10 years ago. The electrician installed a Siemens breaker into the Silvana panel. While the break did fit it is not correct. Eaton has the sole ownership of the breakers for this vintage panel.

So I need to pull the breaker the electrician and inspector failed to catch and replace. I also need to pull the three Siemens I installed and replace those breakers in more recent years. I'm hesitant to do this because the bus bar is scored anytime a breaker is removed and replaced.


1774199198547.png
 

whateg01

Well-known member
Joined
Mar 13, 2006
Messages
11,535
Location
doo dah, kansas, usa
"Do not install greater than a max of 200 amp connected load per tab"

I thought that could have meant the entire side could not have totaled 200amps if the breakers were added.
That "per tab" bit means that each tab cannot exceed 200A. If it meant that "the entire side" couldn't exceed 200A, it would say something like "per bus". But it doesn't.
 
OP
W

wazzabie

Well-known member
Joined
May 9, 2010
Messages
424
While the Siemens isn't listed for use in the Sylvania panel, I wouldn't lose sleep if it were in my house.
Using another manufacturers circuit breaker in the wrong panelboard violates NEC® 110.3(B) and violates the product listing. 1774201892814.png
 

mm08822

Well-known member
Joined
Jan 13, 2012
Messages
6,053
Location
NJ
Using another manufacturers circuit breaker in the wrong panelboard violates NEC® 110.3(B) and violates the product listing. 1774201892814.png
Unless the panel manufacturer has listed the panel to include other mfr's cbs. (highly unlikely)

However, a mfr different than the panel mfr can have their cb's classified to be used in another mfr's panel.
 
To avoid these ads, REGISTER NOW!
OP
W

wazzabie

Well-known member
Joined
May 9, 2010
Messages
424
Unless the panel manufacturer has listed the panel to include other mfr's cbs. (highly unlikely)

However, a mfr different than the panel mfr can have their cb's classified to be used in another mfr's panel.
Per Eaton 1774202747504.png
 
OP
W

wazzabie

Well-known member
Joined
May 9, 2010
Messages
424
Why? Do you think you've over loaded it?
I have no reason to believe I'm over load. I want to know what the calculations are for my own knowledge. I have some doubts about the work of the electrician and inspector performed since they both approved using a Siemens breaker rather then the Eaton. I would rather learn so that I personally know the work is correct.
 
OP
W

wazzabie

Well-known member
Joined
May 9, 2010
Messages
424
Scored?

Scorched?


Not exactly 100% sure what you're saying here but you need to call a pro and possibly have your panel replaced
The panel is not burned. Not sure why the panel would need to be replaced. It is not part of the Zinsco panel issue.
 

Cruzan80

Well-known member
Joined
Jul 22, 2015
Messages
4,318
Location
Denver, CO
The panel is not burned. Not sure why the panel would need to be replaced. It is not part of the Zinsco panel issue.
If you think the bus bars are "scored" aka. damaged, that would be an indication of a new panel being needed.

As others have said, this seems like a classic case of "book knowledge" exceeding your ability in the real world to accomplish things safely.
 

wyliesdiesels

Well-known member
Joined
Aug 14, 2012
Messages
20,074
Location
Modesto, CA
I'm hesitant to do this because the bus bar is scored anytime a breaker is removed and replaced.
what?

there shouldnt be any scoring when installing and removing a breaker. there is nothing inside the breaker clamp that could score the stab on the bus bar
 

JohnX14

Well-known member
Joined
Jun 2, 2014
Messages
609
Location
Boston 'burbs
nope it says STAB, meaning where the breakers connect, not the entire bus.
You're right.

But the rating of the panel is limited to 200 amps as well. (0r 225) This panel can't be fed with 400 amps and pull 200 on (2) stabs on the same leg. But I get it, that's not what I
Edit: deleted a statement that I realized wasn’t accurate
 
Last edited:

JohnX14

Well-known member
Joined
Jun 2, 2014
Messages
609
Location
Boston 'burbs
There are lug kits that I’ve used on Eaton BR load centers that allow me to pull 200 amps to a subpanel. So yes I agree it’s 200 per stab.
 