To avoid these ads, REGISTER NOW!

Light Fixture Layout Collections

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
Since I’ve spent a fair amount of time doing Light Fixture Layouts for GJ members, I figured I'd put them all in one thread as a general reference guide. I’ll start with the latest and add more as time permits.

All Isoplots in footcandles and done at 30" workplane height (30" from the floor).

To all of the posters I haven't been able to get to, please see post #931 in The Best Light Fixture Ever thread.
 
Last edited:
To avoid these ads, REGISTER NOW!
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
DSPark13 Fixture Layout Request 36’ x 27.5’ x 12’

Condensed:
3 car garage 36’ x 27.5’ x 12’
Class B Residential Ballast that doesn't interfere with the stereo or TV.
8' high 18" wide storage shelf
Two post lift in the single bay and hopefully a four post lift in the middle for work and or car storage.
The garage will be used mostly for working on cars as well as parking. On the 27.5' single bay side I will install a 2 post lift at 13' from the two window wall. The outside edge of the post baseplate will be 3' from the solid wall, an air compressor in the corner near the sub panel and the single garage door, a welder stored in the corner of the solid wall and window wall, tool chest and work benches all along the solid wall leaving room around the lift post.
The 4 post lift will be 9' 3" in width and 18' 8" total length with ramps, located in middle bay with the front of the lift 5' off the staircase wall. The 2 left side posts of the 4 post lift will be placed into the 2 foot space between the single and double garage doors.

 
Last edited:
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
DSPark13 Suggested Fixture Layout 36’ x 27.5’ x 12’

Qty. 29 COOPER LIGHTING - METALUX SSF-232 or similar 2.625" lamp spacing (lamp center to lamp center) with Residential Class B noise rated Ballast. (Here's a good article from GE on fluorescent ballast EMI)
8ft tandem 4 lamp F32T8 fixtures can be substituted for any two 4ft 2 lamp end-to-end mounted fixtures.

IES File Info used:
METALUX SSF-232
LAMP: TWO 32-WATT FO32T8 FLUORESCENTS, EACH RATED 2900 LUMENS.
BALLAST: MAGNETEK TRIAD B232I120RH
TOTAL INPUT WATTS = 57.6 AT 120.0 VOLTS

(Click Images for larger view)









 
Last edited:
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
DSPark13 Suggested Fixture Layout 36’ x 27.5’ x 12’ (cont'd)

Here's the Isoplot with some cars and a work bench in the garage.

 
Last edited:
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
DSPark13 Fixture and Bulb Suggestion 36’ x 27.5’ x 12’

Suggested Fixture: Lithonia C 2 32 120 RE available at Home Depot for $31.97

Recommended Lamps: Sylvania 22026 Flourescent T8 Fo32/850/Xp/Eco3 available at globalindustrial.com for $2.93 each. (must buy in cases of 30, thus you'll need 2 cases)
 
Last edited:
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
rown4au Fixture Layout Request 23'x 36' x 14' + 6'6" x 18' x 10'

Condensed:
The main garage space is 23' x 36' x 14' and the workshop is 6'6" x 18' x 10'.

Although it doesn't show it on these drawings I will have a row of cabinets and a workbench top in the workshop area next to the slop sink and fridge. There will also be a 4 post lift in the 3rd bay that shows the car.

I have already told the architects that I would prefer the jack shaft openers on the wall next to the door so they will not be located on the ceiling as the drawing shows. The tracks for all garage doors will go up to the full ceiling height to give max clearance so that would mean you have minimal overlap on the ceiling of the actual door to cause shadows.

That said my initial thoughts after reading some of the comments on this thread are to have 2 x fixtures located on either side of each vehicle like they show but I would add two more in between the workshop and the 3rd bay and 2 between the 1st bay and the house wall. I was also thinking that I should add one fixture per bay along the front wall centered in each bay. This would give plenty of light over the work bench area and around the front of the car and hopefully avoid shadows as discussed. However this would make a total of 13 fixtures for the space, so

I am not sure if that is overkill.

I am also thinking about adding a ceiling fan on either side of the center bay for air circulation but that is a different discussion.

Garage Layout.pdf
 
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
rown4au Suggested Fixture Layout 23'x 36' x 14' + 6'6" x 18' x 10'

Qty. 8 US Energy Sciences FSL-043208-EAN (with MIRO4 Mirror Aluminum 95% Reflector)
Qty. 10 US Energy Sciences FSL-023204-EAN (with MIRO4 Mirror Aluminum 95% Reflector)
Qty. 2 COOPER LIGHTING - METALUX 8TSSF-232-UNV-EB81 or similar 2.625" lamp spacing non-reflector strip light.

IES File Info used: (this is not a recommendation. just what's in the IES files)

FSL-023204-EAN
LAMP: TWO PHILIPS F32T8/TL841 RATED AT 2850 LUMENS EACH.
BALLAST: SYLVANIA QT2X32 IS-SC

METALUX SSF-232
LAMP: TWO 32-WATT FO32T8 FLUORESCENTS, EACH RATED 2900 LUMENS.
BALLAST: MAGNETEK TRIAD B232I120RH

(Click Images for larger view)









 
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
rown4au Suggested Fixture Layout 23'x 36' x 14' + 6'6" x 18' x 10'

Here's the Isoplot with some cars and a work bench in the garage.

 
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
rown4au Fixture and Bulb Suggestion 23'x 36' x 14' + 6'6" x 18' x 10'

Fixture “A” = US Energy Sciences FSL-043208-EAN (with MIRO4 Mirror Aluminum 95% Reflector) available at Shineretrofits.com for $70.14 each. (Be sure to click the 95% Reflector option.)

Qty. Required: 8

Fixture “B” = US Energy Sciences FSL-023204-EAN (with MIRO4 Mirror Aluminum 95% Reflector) available at Shineretrofits.com for $37.05 each. (Be sure to click the 95% Reflector option.)

Qty. Required: 10

Fixture “C” = Cooper Lighting 8TSSF-232-UNV-EB81 (no reflector) available at ronshomeandhardware.com for $42.99 each.

Qty. Required: 2

Recommended Lamps for all above = Sylvania 22026 Fluorescent T8 Fo32/850/Xp/Eco3 available at globalindustrial.com for $2.93 each. (Must buy in cases of 30, thus you’ll need 2 cases)

Qty. Required: 60 Lamps
 
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
dmcintosh Fixture Layout Request 24' x 30' x 10'

Condensed:
24' x 30' pole building with a 10' ceiling to replace a 12' x 18' shed. Planning to use this to work on/restore my 1966 Chevelle Wagon. The concrete will be 'painted' with Rust Bullet in the next day or so I can start my electric. Planning to install a 60 amp subpanel.

Been working on lighting ideas and would like some input. From what I've already learned, I am planning to use fluorescent strip lights (T8) probably Lithonia from HD since they are easy to get and the price is not bad. Any ideas on the layout? In addition to the main lighting I may also add lights directly over the work benches and equipment if it is too dark.

 
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
dmcintosh Suggested Fixture Layout 24' x 30' x 10'

Here's the most even illumination I can get to, providing workbench lighting and maintaining a less prominently lit mower/storage area:




Workplane Isoline Fc Plot:






All fixtures mounted directly to ceiling. IES info used = Metalux SSF-232
I assumed your 24x30 dims were exterior, so plot is based on 23x29 interior dim.
 
Last edited:

MushCreek

Well-known member
Joined
Jan 14, 2015
Messages
9,966
Location
Upstate South Carolina
Very cool- thanks! I have a 27 X31 X 12 (interior) space, so I should be able to work from one of those pretty well. I see I need to save up some more money, though. Anyone know what a kidney sells for these days?
 
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
gtae07 Suggested Fixture Layout 28' x 24' x 8'

Alternate Lighting Layout suggestion:
GJ-gtae07-1a.jpg

Fixture Recommendation:
31nSnyGYFjL.jpg
Lithonia SB232 $32.97 on Amazon.

Wraps (lensed fixtures) are recommended for 8ft ceiling height.
At that price the ballast is probably a budget model that will die within a few years, but by then you'll have a choice of upgrading to a higher quality fluorescent ballast or installing ballast bypass LED retrofits.

Light fixtures on low ceilings make longer shadows, thus placement becomes more critical.
Lumen output can be controlled via lamp selection:
The Sylvania OCTRON 800 XP XL ECOLOGIC3 Lamp spec sheet is a good example of the different lumen outputs available.
 
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
gtae07 Suggested Fixture Layout 28' x 24' x 8'

Since this is a good representation of a typical household garage, here are 4 layouts including my recommendation and gtae07's plan.

(Click Images for larger view)

gtae07-layout4-thumb.jpg

gtae07-iso4-thumb.jpg

gtae07-iso-cars4-thumb.jpg
 

tfalk

Well-known member
Joined
Mar 30, 2015
Messages
319
Location
Somerset NJ
Perfect timing... I'm in the process of laying out a (hopefully soon) build that is pretty much a 180 degree version of what you have posted for dmcintosh. Where that layout has the mower/storage, I will have an enclosed stairway leading down into the basement where I currently have bilco doors. Where you have 4 sets paralleling the car, I was thinking of using 3 sets of 4 tube fixtures evenly spaced. Now I'm rethinking that...
 

TTA89

Well-known member
Joined
Feb 23, 2014
Messages
230
Location
New Hampshire
Any chance I could get some help with a layout? I'm working on and restoring cars and would love some good light. I have 15 feet to the top of the ceilings. It will be finished drywall with the common white ceilings and walls down to about a 4 foot grey section at the bottom of the walls.

The 4 post lift in the front is mainly for storage and any work I do over there will be under the car. I'd say around the 2 post lift and the area in front of the workshop is where I'd mostly be working.




 
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
Any chance I could get some help with a layout? I'm working on and restoring cars and would love some good light. I have 15 feet to the top of the ceilings. It will be finished drywall with the common white ceilings and walls down to about a 4 foot grey section at the bottom of the walls.

The 4 post lift in the front is mainly for storage and any work I do over there will be under the car. I'd say around the 2 post lift and the area in front of the workshop is where I'd mostly be working.
Sure, please provide exterior workshop wall dimensions, garage door width and type. Lift location dimensions would be useful too.
 

dubojr10

Active member
Joined
May 4, 2015
Messages
31
Location
Jax, FL
I'd love some help as well. Lighting is an art and I am not qualified. LOL

My garage will be a 26X40 galavnized tubing structure with colored exterior skin. Walls will be 10' with an approx. 14' peak on the gable ends. Inside will remain all exposed. The truss's will be 2"X3" Galvanized tubing set on 5' centers. Unconfirmed but the inside of the exterior and roof tin panels should be an off white or at minimum light in color. Garage doors will be 10' wide and 8' tall Roll up style doors. Entry door will be a standard 3-0 door. There will be a 4 post lift most likely place in the center of the building so to have access all around any vehicle placed on it. There will be no drop ceilings and the fixtures will be suspended by jack chain at an elevation to be determined. Fixtures are 48" LED's rated at 4200 Lumens. LED color is 5,000k. 86 CRI. Fixture dimensions are 47.25" x 5.98" x 2.74". I have attached some pictures for reference. Is there anything else I can provide to assist you?

THANKS A TON IN ADVANCE! :bowdown:
 

Attachments

  • LED Shop Light.jpg
    LED Shop Light.jpg
    36.5 KB · Views: 725
  • Lift Overall Specs.jpg
    Lift Overall Specs.jpg
    153.7 KB · Views: 723
  • Vehicle Profile.jpg
    Vehicle Profile.jpg
    89.8 KB · Views: 675
  • Elevations.jpg
    Elevations.jpg
    107.3 KB · Views: 614
  • Floor.jpg
    Floor.jpg
    87.5 KB · Views: 718
Last edited:
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
... Fixtures are 48" LED's rated at 4200 Lumens. LED color is 5,000k. 86 CRI. Fixture dimensions are 47.25" x 5.98" x 2.74". I have attached some pictures for reference. Is there anything else I can provide to assist you?
Need IES file for selected fixture.
 
To avoid these ads, REGISTER NOW!
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
efinley 50x60x18

Cooper Metalux 8TSSF-254-UNV-EBT1 Qty. 18
Cooper Metalux SSF-254-UNV-EBT1 Qty. 18

Spec Sheet: http://www.cooperindustries.com/con...ts/metalux/spec_sheets/081872_SSF114_SSSx.pdf

Many manufacturers make similar style strip lights. I do not recommend any fixtures with lamps right next to each other. Assume that you'll probably have to special order these fixtures from a local distributor. I do not recommend the Metalux SNF series or the Lithonia Z series due to poor lamp spacing = reduced efficiency.

F54T5HO Lamp Qty: 108
Suggested lamp: Sylvania 20906 or 20949
$4.68 ea.(the 25,000 hr. Life on that site is wrong. Linked spec sheet 40-45,000 hrs.)

Ceiling height works with either F32T8 or F54T5. Went with F54T5 to reduce fixture quantity, thus reducing total lighting purchase and installation costs.



I don't have any boats to insert as objects in the building, so I modified 2 pickup trucks
(wider and longer than normal trucks)











SSF-254-UNV-EBT1 is 46" long and 8TSSF-254-UNV-EBT1 is 92" long.

 
Last edited:
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
C2tuck 30x30x14

30x30x14 Steel Pole Barn (12' Walls, 15'9" peak, 3/12 Pitch)

Original Request via PM from C2tuck:

I'm building a 30x30x12 3/12 pitch metal garage, 16x8 garage door, a 5x6 window centered on each side wall, and am thinking of putting 9 fluorescent lights in for the main lighting and maybe some bench lighting later on down the road.

I want to have plenty of light in there at night as I will be working on cars and other projects well into the wee hours of the morning.

I was thinking of going with a 4' T8 4 bulb fixture, but all of hem I have seen at homedepot and Lowes just look cheap to me.

I guess what I need to know is if this will be overkill and if so what you would recommend? Or if not what are the best options for me keeping in mind that I do t want to spend 2 grand on lights.

 
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
C2tuck 30x30x14

Fixture: Cooper Metalux 8TSSF-232-UNV-EB81 (no reflector) available at ronshomeandhardware.com for $42.99 each.
Qty.: 15

Lamps: Sylvania 22026 Fluorescent T8 Fo32/850/Xp/Eco3 available at globalindustrial.com for $2.93 each.
Qty.: 60 Lamps


Work Benches located along left and right walls will require supplemental task lighting.
 
Last edited:

CPyle

Member
Joined
May 20, 2015
Messages
9
Location
STL
Re: gtae07 Suggested Fixture Layout 28' x 24' x 8'

Since this is a good representation of a typical household garage, here are 4 layouts including my recommendation and gtae07's plan.

(Click Images for larger view)






Thanks for all of your work Platonic. Which was your recommendation out of the four? And is that recommendation based on the work being in the typical car bays? I'm looking at putting a woodworking/metalworking shop together where the majority of work will be on the periphery and down the middle so it helps to know what type of work your suggestion was directed at.

Thanks again!
 
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
Re: gtae07 Suggested Fixture Layout 28' x 24' x 8'

Thanks for all of your work Platonic. Which was your recommendation out of the four? And is that recommendation based on the work being in the typical car bays? I'm looking at putting a woodworking/metalworking shop together where the majority of work will be on the periphery and down the middle so it helps to know what type of work your suggestion was directed at.

Thanks again!
The top left layout in each collection is my recommendation. Though it was planned around automotive work, it is a very good layout for any application.
 
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
What software are you guys using?
There's only 1 guy doing this: I'm using Dialux for Isoplots, AutoCAD to simplify 3D layout generation and create final dimensioned layout drawings. Everything edited in Photoshop for forum posts.
 
Last edited:
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
jeopardy98 24x44x9

Suggested Fixture and Lamps:
Qty. 24 Lithonia C 2 32 120 RE = 2 lamp strip light with 2.625" lamp spacing and residential ballast (thus low RFI)
available at HD for $31.97 each.

Qty. 48 Lamps: Sylvania 22026 (5000K) or 21767 (4000K)
5000K Fluorescent T8 Fo32/850/Xp/Eco3 available at globalindustrial.com for $2.93 each.
or
4000K Fluorescent T8 Fo32/841/Xp/Eco3 available at globalindustrial.com for $3.37 each.



jeopardy98-24x44-layout.jpg


jeopardy98-24x44-isoplot.jpg


 
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
jeopardy98 23x40x9

Above layout modified to provided floor plan:

21 Fixtures, 42 Bulbs (same fixture and bulb recommendation as above)



jeopardy98-23x43x9-layout.jpg


jeopardy98-23x43x9-isoplot.jpg


 
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
sbosecker 45x59x16 Garage w/30x30x11+16 ceiling Wood Shop

Original Thread

TopView-Dimensioned%20-%20Updated%20Woodshop.jpg


Flat drywall ceilings. All Ceilings/Walls painted white.
2 Post lift in center bay. Fan locations TBD.
Workbench locations TBD.

North side of Wood Shop Dark Olive area = 11 feet tall ceiling.
South side of the Wood Shop Light Green area = 16 foot tall ceiling.
 
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
sbosecker 45x59x16 Garage w/30x30x11+16 ceiling Wood Shop

Cooper Metalux
8TSSF-232-UNV-EB81 Qty.: 11 (or equivalent)
plus
SSF-232-UNV-EB81 Qty. 7 (or equivalent)
or
SSF-232-UNV-EB81 Qty.29

Lamps: Sylvania 22026 or 21767 Fluorescent T8 Fo32/850/Xp/Eco3 or Fo32/841/Xp/Eco3 (5000K or 4100K respectively) Qty.: 58 Lamps


 

Lootenny

Well-known member
Joined
Jan 6, 2014
Messages
105
If I can impose on your goodwill, I haven't seen anything close to mine.

30' X 56', 14' inside height. Ceiling is flat to bottoms of trusses, white metal. There are 6 windows 2' X 4' set at 8' above the floor, 3 a side, another two on the front 30' side at 4' avove the floor, on either side of the one overhead door, 10' X 10'.

Thank you!
 
OP
P

Platonic Solid

Well-known member
Joined
Nov 29, 2014
Messages
3,587
Location
CT-USA
ihscomputers 40x60x14

Location: Georgia
  • New 40' x 60' x 12’ eave steel building with 2/12 pitch built for hobby automotive work.
  • NO skylights and NO windows.
  • Three steel roll up (barrel) doors and one walk-thru door on the front wall.
  • One walk-thru door on the back wall.
  • Two stick-built adjoining rooms in the southwest corner 6'x6' bathroom and 10' deep x 18' wide equipment room - both with 8' wooden ceilings.
  • There will be a 2' deep workbench running along the 18' exterior wall of the equipment room with flourescent lights mounted directly over the bench.
  • Two each 2Post car lifts in two of the three bays with the posts almost centered on the 60 foot center line.
  • The walls have 8' tall white steel panels all the way around.
  • The remaining wall surfaces and the entire ceiling is covered with the white plastic sheeted insulation.
  • The floor is concrete that will be coated with silver RustBullet.


vairshoplayout01242015_zpsaae45d23.jpg


DSC04092_zpsda0cb25d.jpg


DSC04095_zps1a20a2de.jpg
 
To avoid these ads, REGISTER NOW!