U got a bunch of major violations on the electrical. U shouldve posted in the electrical section.

That wire u used for the branch feeder is NOT permitted to be used inside even in conduit. It is called URD....
And individual conductors like that should be in conduit...
What size is the wire?
Also the spool u posted a picture of is 4-wire but i only see 3-wires in the your disconnect can..Is the conduit metal or plastic? I see a bonding bushing so i assume metal...
I count 10 circuits in the panel unless 6 or less are in the panel, a main is required.