I got a deal on a cheap 4kw VFD. It's a Mollom G75-2T-4G-B, rated to 5hp.
I want to use it on a table saw that has a 3hp 3-phase motor.
This will be my first VFD conversion, so I'm learning a lot. I want to run through how I intend to wire this up and see if the collective Garage Journal brain-trust has any advice.
My VFD is over-sized for my motor. My understanding is that the VFD input wiring should be sized to the VFD, not to the motor being driven. My VFD says it has a maximum output of 17 amps. There isn't a listed maximum input current, but using math, I can estimate it would be around 29-30 amps (17 x 1.732).
I've read that it's common to upsize the breaker and the supply wire by 125% of the VFD max current, which puts me just under 37A. So, a 40A circuit would be required. I plan to run a 40A #8 240V circuit into a surface-mounted wall receptacle next to my panel, then use a power cable to send supply into a NEMA enclosure.
From there, I'll pass through a two-pole 40A breaker again (redundant, but I thought it would be nice to have a shut-off right in the box), then to a 40A-rated contactor (so I can remotely switch power to the VFD on/off).
Then each hot leg will pass through a 40A 10x38mm fast-acting fuse, like a KTK-40. Probably will use a DIN-rail mounted fuse holder for this.
Then I'll use a 40A-rated noise filter, and finally into the VFD itself.
The contactor I'm planning to use will likely have a 24VAC coil, so I'll need to add a transformer to get control power. The transformer will pull power to its primary winding off the noise filter lugs, and I'll add an in-line 1A fuse. I'll control the contactor windings with a simple switch somewhere under the table saw. This will let me shut off the entire enclosure when I'm not using it... which will be often.
Oh, and I want to add a fan. I've got a nice 12V DC fan handy, and I will add a 12v DC power supply easily enough.
Am I missing anything? Making any big mistakes? Wasting money?