  1. M

    A/C thermostat wire ran inside power whip?

    not if the LV circuit is class 2 which the Tstat line is.
  2. M

    Changing non-grounding cord to grounding?

    thats a good idea and could help prevent your early demise.
  3. M

    2 sets of lights using 12/3 wire Controled seperatly?

    how many amps does one fixture draw? (not watts added up, but the amps on the ballast label)
  4. M

    Generac 20KW home generator install

    with regard to the frequency discussion, many UPSs will trip offline if the incoming frequency is off by a certain amount. I have come across some that are very sensitive.
  5. M

    Dug up phone line, what should I expect?

    usually they run a 3 pair to each house. Look at the wire where it comes into your house, i bet its 3pr
  6. M

    Dug up phone line, what should I expect?

    if this is just the line to your house, a call before you dig may not have even located it. No big deal theyll probably charge you a couple hundred to fix it. See if you can get their design specs and take care of the trench for them. if it had been a line serving customers other than you, or...
  7. M

    240v hour meter just popped and burnt out.

    did it come from china (not made in, but shipped from) ? Is it UL listed?
  8. M

    Rooftop cable for clipping-in safety harness

    you need it engineered. pulling sideways on a cable between two endpoints with a couple hundred pounds can put an exponentally larger amount of force on those endpoints.
  9. M

    Floresent fixture power leads

    no...dont do it.
  10. M

    I would like to see some pictures of 320-400 amp service

    interesting....i didnt know they use SWER in canada
  11. M

    Wiring a lighting contactor?

    the switches in the house should be one 3 way and one or more 4 way. the 2 travelers out of the 4 way and the common from the 3 way should go to the shed where the travelers would connect to a 3 way. Then switch the contactor coil with this. How many watts is the light?
  12. M

    What do you use to make mock-up parts?

    one day....a 3D printer
  13. M

    4 bulb T8 fixture with a cord & plug?

    for the cord, just get a 16ga cord. You dont need a 12 or 14ga plug in cord for a shop light unless the light's power consumption warrants it.
  14. M

    High quality Square D panel board ?

    and how do you use tandems in a panel supplying a house where almost everything has to be afci?
  15. M

    High quality Square D panel board ?

    16.6ka where? whats the interrupt rating of the breakers in that I-line?
  16. M

    High quality Square D panel board ?

    whats the available fault current where you are installing the subpanel? Can you use 10Ka breakers or do you need 22ka?
  17. M

    GFCI Circuit Breaker or GFCI Outlet in circuit?

    GFCI receptacles in most instances. You want the GFCI as close to the load, and you want as few individual loads on each gfci as possible. There is no such thing as 'nusiance tripping' -the gfci is doing its job. Everything has leakage, and the gfci trips at 4-6ma. Put 100ft of romex, 5 surge...
  18. M

    Panel Manufacturer Recommendations?

    doesnt really apply in 99% of residential installations, but the answer is: series ratings (this should make for a fun discussion)
  19. M

    are craftsman sockets still USA?

    are craftsman sockets still USA made?
  20. M

    how do I turn a CO2 bottle into an argon bottle?

    a gas place exchanged the CO2 tank for an argon tank and only charged the cost of the argon gas (although they gave nothing for the CO2 in the bottle which was full) all in all a very good deal.